Hello @ayone0518,
you need to pull 32bit data, so you have to define element which spans over 2 registers. This is done via the Multibyte Length property, which you have to set to 4 (4 bytes = 32 bits)
If it is possible, I would suggest to turn the communication around. Make the Mervis a Modbus Slave (server) and the Weintek Modbus Master. Configuration in the Mervis will be much easier. Try following this tutorial: https://kb.unipi.technology/en:sw:01-mervis:setting-modbus-server-hidden and here you can see how to set it against Weintek: https://kb.unipi.technology/en:sw:01-mervis:weintek-ip-series-hidden#setting_up_the_unipi_for_sharing_temperature_and_relay_output
Best regards,
Martin