How to passing real type value through ModbusTCP ?
-
I am not sure that here is the right place to ask.
I want read real value on Mervis from Touch Screen MT8071ip,
I bought shop here. I could read and write on type of int value,
but I don't know how to configure for real.thank you.
-
Hello @ayone0518,
you need to pull 32bit data, so you have to define element which spans over 2 registers. This is done via the Multibyte Length property, which you have to set to 4 (4 bytes = 32 bits)If it is possible, I would suggest to turn the communication around. Make the Mervis a Modbus Slave (server) and the Weintek Modbus Master. Configuration in the Mervis will be much easier. Try following this tutorial: https://kb.unipi.technology/en:sw:01-mervis:setting-modbus-server-hidden and here you can see how to set it against Weintek: https://kb.unipi.technology/en:sw:01-mervis:weintek-ip-series-hidden#setting_up_the_unipi_for_sharing_temperature_and_relay_output
Best regards,
Martin
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.