Let's investigate:
- Did you restart the Neuron after changing the settings (or at least the evok service)?
- what Raspbian image do you use ? Please, paste the output of the
uname -a.
We are probably (not confirmed, working on it) experiencing an issue with running the EVOK on the up-to-date Raspbian
M.
- Yes; I'm very neurotic on that, I rebooted the L513, and made the extensions powerless also.
- As for the version, I'm using the latest Debian, (downloaded it from the website last week?):
Linux raspberrypi 4.14.50-v7+ #1122 SMP Tue Jun 19 12:26:26 BST 2018 armv7l GNU/Linux -
That seems to be OK. I will have to reproduce your setup, but I'm not sure, if I will be able to make it today. Tommorow morning for sure.
M.
OK, I partially reproduced your setup. I have:
- Neuron L503 with latest, up-to-date Raspbian (
Linux raspberrypi 4.14.52-v7+ #1123 SMP Wed Jun 27 17:35:49 BST 2018 armv7l GNU/Linux), and EVOK 2.0.7. Serial line 1.1 configured with 19200bps, 8N1:
- One extension xS40 with address 3 (DIPs 3 and 4 are down):
- Another extension xS50 with address 2 (DIP 2 is up):
- Extensions and Neuron are connected with all RS485 "As" connected together and RS485 "Bs" connected together:
- The configuration in the evok.conf is this one:
#!!! Do not use '#' for comments !!! [MAIN] config_version = 2.5 ; Configuration file version, DO NOT CHANGE! use_schema_verification = False ; Enabling this will deny any requests that do not match the JSON Schema; NOTE THAT THIS RESULTS IN A SIGNIFICANT INCREASE IN LATENCY AND SHOULD NOT BE USED EXCEPT FOR TESTING log_level = ERROR ; Minimum severity of messages to be logged; one of INFO, DEBUG, WARNING, ERROR, CRITICAL log_file = /var/log/evok.log ; Log file to use; will be cleared on boot port = 8080 ; !!! Internal API port - only change if you are certain you know what you are doing; FOR OUR WEB INTERFACE THE PORT SHOULD BE CHANGED IN "/etc/evok-nginx.conf" INSTEAD !!! webhook_enabled = False ; Enables webhook notification - see e.g. https://sendgrid.com/blog/whats-webhook/ webhook_address = http://127.0.0.1:80 ; Put your server endpoint address here (e.g. http://123.123.123.123:/wh ) webhook_device_mask = ["input","wd"] ; List of device types to notify on (written as a JSON list) - adding AI will generate a large amount of messages! webhook_complex_events = False ; EVOK will send POST requests with the same data as WebSocket, rather than an empty GET request wifi_control_enabled = False ; !!! REQUIRES THE UNIPIAP WIFI CONTROLLER TO BE INSTALLED !!! Will allow evok to control the internal Neuron wifi soap_server_enabled = False ; Enables the simple SOAP server; use only if you need the functionality soap_server_port = 8081 ; !!! IF SOAP SERVER IS ENABLED, THIS PORT NEEDS TO BE UNIQUE (i.e. different from the port setting above) !!! [NEURON_1] global_id = 1 ; Mandatory, REQUIRED TO BE UNIQUE allow_register_access = False ; Optional, False default scan_frequency = 10 ; Optional, 10 default scan_enabled = True ; Optional, True default ; Below you can find examples for connecting devices over UART; first example is a Neuron extension while the second is a custom third-party device ; Devices sharing a port use the port settings of the first device on that port (baud rate, parity, stopbits) ; !!!Note that device_name has to match a filename in the /etc/hw_definitions directory!!! See /etc/hw_definitions/DOMAT MMIO.yaml for an example [EXTENSION_1] global_id = 2 ; Mandatory, REQUIRED TO BE UNIQUE device_name = xS40 ; Mandatory modbus_uart_port = /dev/extcomm/0/0 ; Mandatory ;neuron_uart_circuit = 1_01 ; Optional, allows associating extensions with specific Neuron UART-over-Modbus ports (not possible for non-Modbus UART ports, e.g. /dev/ttyUSB0 or /dev/ttyS0) ;allow_register_access = True ; Optional, False default, is mandatory with third-party devices address = 3 ; Optional, 1 default ;scan_frequency = 10 ; Optional, 10 default ;scan_enabled = True ; Optional, True default ; Note that the following settings will be inherited by other devices sharing the same port, i.e. /dev/extcomm/0/0 ;baud_rate = 19200 ; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN ;parity = N ; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN ;stop_bits = 1 ; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN [EXTENSION_2] global_id = 3 ; Mandatory, REQUIRED TO BE UNIQUE device_name = xS50 ; Mandatory modbus_uart_port = /dev/extcomm/0/0 ; Mandatory ;neuron_uart_circuit = 1_01 ; Optional, allows associating extensions with specific Neuron UART-over-Modbus ports (not possible for non-Modbus UART ports, e.g. /dev/ttyUSB0 or /dev/ttyS0) ;allow_register_access = True ; Optional, False default, is mandatory with third-party devices address = 2 ; Optional, 1 default ;scan_frequency = 10 ; Optional, 10 default ;scan_enabled = True ; Optional, True default ; Note that the following settings will be inherited by other devices sharing the same port, i.e. /dev/extcomm/0/0 ;baud_rate = 19200 ; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN ;parity = N ; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN ;stop_bits = 1 ; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN ;[EXTENSION_2] ;global_id = 3 ; Mandatory, REQUIRED TO BE UNIQUE ;device_name = CUSTOM MODBUS DEVICE ; Mandatory ;modbus_uart_port = /dev/extcomm/0/0 ; Mandatory ;neuron_uart_circuit = 1_01 ; Optional, allows associating extensions with specific Neuron UART-over-Modbus ports (not possible for non-Modbus UART ports, e.g. /dev/ttyUSB0 or /dev/ttyS0) ;allow_register_access = True ; Mandatory with third-party devices ;address = 1 ; Optional, 15 default ;scan_frequency = 2 ; Optional, 1 default ;scan_enabled = True ; Optional, True default [OWBUS_1] owbus = /dev/i2c-1 --i2c=/dev/i2c-1:ALL ; Scanned bus (--i2c=/dev/i2c-1:ALL or localhost:2122 or 'u' for USB dongle) interval = 3 ; [s] Default sensor reading scan_interval = 300 ; [s] How often is scanning done ;Example of 1W-4R/4DI extension module, 1W-8R is almost the same, only with inputs instead of relays ; ; - Map a new 1Wire sensor with the appropriate address, type and interval ; - The syntax can be either SENSOR or 1WDEVICE ; - Setting the correct reading interval is crucial to achieve ideal performance; the default interval is 15s ; ;[1WDEVICE_2] ;bus = 1 ;address = 29F39A17000000BC ;type = DS2408 ;interval = 1 ; ;[1WRELAY_10] ;sensor = 2 ;pin = 0 ; ;[1WRELAY_11] ;sensor = 2 ;pin = 1 ; ;[1WRELAY_12] ;sensor = 2 ;pin = 2 ; ;[1WRELAY_13] ;sensor = 2 ;pin = 3 ; ;[1WINPUT_20] ;sensor = 2 ;pin = 4 ; ;[1WINPUT_21] ;sensor = 2 ;pin = 5 ; ;[1WINPUT_22] ;sensor = 2 ;pin = 6 ; ;[1WINPUT_23] ;sensor = 2 ;pin = 7- After restarting the evok (
service restart evok), the devices and their inputs/outputs were immediatelly available in the Web UI:
Can you check your setup against mine above? Try simplifying the extension's configuration as I did.
M.
I wil have to check in a minute.
As far as I can remember from testing yesterday; even if I connect just 1 module, which I give a fixed address with the dipswitch (say; dip 1 = up, makes address = 1 (right?)), and configure the evok.conf accordingly, it won't work.So in my opinion, setting an address manually by dip-switch, causes something to go wrong. Either I don't understand how the dip's represent an address, or something else goes haywire...
however; I didn't check with the
;neuron_uart_circuit = 1_01commented like in your example, wil check that in a minute.What does this option do anyway ?
So; another quick test:
If I connect just 1 xS50, which I give a fixed address with the dipswitch (dip 1 = up, makes address = 1 (right?)), and configure the evok.conf accordingly, and configure the serial speed, it won't work.
All dip's down, on evok address 15, it works.
this really seems to be an issue on our part, probably related to the firmware of the extensions. You are not the only one having the exactly same problem (see https://forum.unipi.technology/topic/652/how-to-add-xs40-to-neuron-l203-using-custom-software/42). We will investigate it a bit more and let you know as soon as possible.Thank you for your patience,
Ah.. okay. Well, at least I'm not crazy.
Please let me know, I need to get this setup running asap.Thanks!
ok, to get your setup running ASAP - would it be possible to use Teamviewer or direct SSH to the controller so we can check what's happening? We will check the extension's firmware version and do the FW update if neccessary.The best time would be between 12:00 and 20:00 CEST.
Boris -
- SSH into your controller, the user "pi", the password (if not changed) is "raspberry". If your image is Raspbian, you need to install additional packages:
pi@raspberrypi:~ $ sudo bash root@raspberrypi:/home/pi# echo "deb https://files.unipi.technology/debian stretch main" > /etc/apt/sources.list.d/unipi.list root@raspberrypi:/home/pi# wget -O - https://files.unipi.technology/debian/unipi_pub.gpg | apt-key add root@raspberrypi:/home/pi# apt update root@raspberrypi:/home/pi# apt install -y neuron-firmware neuron-modbus-tools-
Connect the extension to the controller over RS485. If you have multiple extensions, connect only one at a time. Right now, all of them thinks they have address 15, so you need to avoid collisions.
Confirm, you have a connection to extension
root@L503-sn101:/home/pi# /opt/neuron-bin/fwserial -p /dev/extcomm/0/0 Boardset: 5 E-14Ro_P-11DiR485 (v1.0) Baseboard: 2 E-14Ro (v1.0) Firmware: v5.6 Modbus timeout set- Flash the firmware
root@L503-sn101:/opt/fw# /opt/neuron-bin/fwserial -p /dev/extcomm/0/0 -PR Boardset: 5 E-14Ro_P-11DiR485 (v1.0) Baseboard: 2 E-14Ro (v1.0) Firmware: v5.6 Modbus timeout set Programming page 00 ...Finished programming chunk 0, ret: 64 err: 0 Finished programming chunk 1, ret: 64 err: 0 Finished programming chunk 2, ret: 64 err: 0 Finished programming chunk 3, ret: 64 err: 0 Finished programming chunk 4, ret: 64 err: 0 Finished programming chunk 5, ret: 64 err: 0 Finished programming chunk 6, ret: 64 err: 0 Finished programming chunk 7, ret: 64 err: 0 Page written OK. Programming page 01 ...Finished programming chunk 0, ret: 64 err: 0 ..........- Verify the firmware. Since the flashed firmware now accepts address set by DIP switches, you need to specify the address in the parameter -u. My extension has address 3
root@L503-sn101:/opt/fw# /opt/neuron-bin/fwserial -p /dev/extcomm/0/0 -u 3 Boardset: 5 E-14Ro_P-11DiR485 (v1.0) Baseboard: 2 E-14Ro (v1.0) Firmware: v5.18 Modbus timeout set- Repeat the process for all of the extensions
Firmware is now 5.9 (it was 5.6 as you said), is there any need to upgrade to 5.18? -
This post is deleted! -
@martin-kudláček My fault, did not do step 1 in your decsription above since fwserial and firmware files were already present. It's 5.18 now, thank you!
Ok, took a while before I had time to do this, but now the downloads don't seem to work anymore, check below (btw, I'm using an own build image, not the Neuron image):
root@L203-sn81:/home/pi# wget -O - https://files.unipi.technology/debian/unipi_pub.gpg | apt-key add\ > ^C root@L203-sn81:/home/pi# wget -O - https://files.unipi.technology/debian/unipi_pub.gpg | apt-key add --2019-09-12 08:05:48-- https://files.unipi.technology/debian/unipi_pub.gpg Resolving files.unipi.technology (files.unipi.technology)... 86.49.170.141 Connecting to files.unipi.technology (files.unipi.technology)|86.49.170.141|:443... connected. HTTP request sent, awaiting response... 302 Found Location: https://kb.unipi.technology/debian/unipi_pub.gpg [following] --2019-09-12 08:05:49-- https://kb.unipi.technology/debian/unipi_pub.gpg Resolving kb.unipi.technology (kb.unipi.technology)... 86.49.170.141 Connecting to kb.unipi.technology (kb.unipi.technology)|86.49.170.141|:443... connected. HTTP request sent, awaiting response... 200 OK Length: unspecified [text/html] Saving to: 'STDOUT' - [ <=> ] 13.43K --.-KB/s in 0.03s 2019-09-12 08:05:49 (385 KB/s) - written to stdout [13757] gpg: no valid OpenPGP data found. root@L203-sn81:/home/pi# apt update Get:1 http://archive.raspberrypi.org/debian stretch InRelease [25.4 kB] Get:2 http://raspbian.raspberrypi.org/raspbian stretch InRelease [15.0 kB] Get:3 http://raspbian.raspberrypi.org/raspbian stretch/contrib Sources [75.2 kB] Get:5 http://raspbian.raspberrypi.org/raspbian stretch/non-free Sources [125 kB] Get:6 http://archive.raspberrypi.org/debian stretch/main armhf Packages [221 kB] Get:7 http://raspbian.raspberrypi.org/raspbian stretch/main Sources [9721 kB] Get:8 http://archive.raspberrypi.org/debian stretch/ui armhf Packages [45.0 kB] Err:4 https://kb.unipi.technology/debian stretch InRelease Clearsigned file isn't valid, got 'NOSPLIT' (does the network require authentication?) Get:9 http://raspbian.raspberrypi.org/raspbian stretch/main armhf Packages [11.7 MB] Get:10 http://raspbian.raspberrypi.org/raspbian stretch/contrib armhf Packages [56.9 kB] Get:11 http://raspbian.raspberrypi.org/raspbian stretch/non-free armhf Packages [95.5 kB] Fetched 22.1 MB in 18s (1192 kB/s) Reading package lists... Done E: Failed to fetch https://files.unipi.technology/debian/dists/stretch/InRelease Clearsigned file isn't valid, got 'NOSPLIT' (does the network require authentication?) E: Some index files failed to download. They have been ignored, or old ones used instead. root@L203-sn81:/home/pi# apt install -y neuron-firmware neuron-modbus-tools Reading package lists... Done Building dependency tree Reading state information... Done Note, selecting 'unipi-modbus-tools' instead of 'neuron-modbus-tools' E: Unable to locate package neuron-firmware root@L203-sn81:/home/pi# /opt/neuron-bin/fwserial -p /dev/extcomm/0/0 bash: /opt/neuron-bin/fwserial: No such file or directory