    Configuration Neuron M203 failed

    Scheduled Pinned Locked Moved Mervis
    9 Posts 3 Posters 2.3k Views 1 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • L
      LubomirMaron
      last edited by

      Hello everybody

      I have problem to get new configuration to M203. During uploading configuration by Mervis I am getting this error :

      a302b953-52eb-4d2f-b246-dcfbe3a98923-image.png

      It's very odd because IP setting is correctly set. I can ping PLC and PLC see WAN.

      What i've done :

      1. I install OS (Raspberrian) and EVOK
      2. Set DirectSwitch's on some DI (through web) and all went well
      3. Erase OS by cleaning SD card
      4. I install new OS - MervisOS
      5. If i get configuration on Mervis, i see all DI with DirectSwitch=Disabled. But DS is still on ! I am not able to change it through Mervis.

      I am pretty new at Mervis, so any help is appriciated :)

      Thanks in advance

      Lubos

      T 1 Reply Last reply
      Reply Quote 0
      • T
        tomas_hora administrators @LubomirMaron
        last edited by

        Hello @LubomirMaron,

        If you decide to go with Meris, do not mix other solution - the direct switch functionality can be configured in Mervis as well. You see it's disabled because Mervis does not read the actual configuration from the device. It expects that the IDE is the only tool to configure the HW so the latest configuration should be there.

        However, the previous configuration of DirectSwitch should not have any affect to Mervis. Are you able to deploy the solution to the PLC? Could you share yoru solution with us?

        1 Reply Last reply
        Reply Quote 0
        • L
          LubomirMaron
          last edited by

          Hello Tomas

          Thanks for response. As a first think, I instal EVOK, set the DirectSwitch on DI and used it for half a year. After that i wanted to switch to Mervis, so i reinstal OS on card. I use empty (default) project, in simple mode of IDE. I just want to change DirectSwitch configuration. And deploing Solution seems ok, Mervis said : Solution upload was succesfull.

          1 Reply Last reply
          Reply Quote 0
          • Martin KudláčekM
            Martin Kudláček
            last edited by

            Hello @LubomirMaron,
            deploying of the solution doesn't affect the configuration of the IOs. You need to "Configure the Unipi Module": https://kb.unipi.technology/en:sw:01-mervis:unipi-configure-module-hidden

            Best regards,
            Martin

            1 Reply Last reply
            Reply Quote 0
            • L
              LubomirMaron
              last edited by

              Hello @Martin-Kudláček

              I know, when I hit "Configure the Unipi module" error I mentioned up appears.
              (Failed to connect to PLC, or confired device not available. Probably incorrect IP settings).

              By the way.
              TCP Parameters in properties panel is set to loopback and device port is 502 by default.
              And mode switch to Commision mode seems working.

              Lubos

              Martin KudláčekM 1 Reply Last reply
              Reply Quote 0
              • Martin KudláčekM
                Martin Kudláček @LubomirMaron
                last edited by

                Hello @LubomirMaron,
                if "Configure the Unipi Module" fails to connect to the PLC, that means the PLC is not reachable over ethernet. Try reattaching to the PLC.

                Tip: this can happen when you switch Profiles. Reattaching usually helps.

                Best regards,
                Martin

                1 Reply Last reply
                Reply Quote 0
                • L
                  LubomirMaron
                  last edited by

                  @Martin-Kudláček thanks for reply, but didn't help :(.

                  I think that you are right that PLC is unreachable for MERVIS. But I can attach PLC normally, like it is in manual.

                  Is there som way to restart PLC to deafult/factory settings, or something like that ?

                  Martin KudláčekM 1 Reply Last reply
                  Reply Quote 0
                  • Martin KudláčekM
                    Martin Kudláček @LubomirMaron
                    last edited by

                    Hello @LubomirMaron, you can always flash the SD card with the clean image. Then do the licensing and then upload the solution.

                    1 Reply Last reply
                    Reply Quote 0
                    • L
                      LubomirMaron
                      last edited by

                      Hello @Martin-Kudláček

                      Thanks for everything, reflashing SD with new MervisOS helped.

                      1 Reply Last reply
                      Reply Quote 0

                      Hello! It looks like you're interested in this conversation, but you don't have an account yet.

                      Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.