    Loss of connection with PLC

    Scheduled Pinned Locked Moved Mervis
    5 Posts 2 Posters 1.4k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • M
      msoenen
      last edited by

      Hello
      I need your help, I no longer have communication with the PLC. I wanted to go from IDE 2.2 to 2.3 (with os 2.2) to do a scada project. When I uploaded, I lost communication. I already had several problems going from 2.0 to 2.2 because I had all the variables have been duplicated. I have attached a screenshot with the faults
      https://1drv.ms/u/s!Aq__SFpXusxkgbsM6_HIUKDZaBI6aQ?e=S2MA0F

      Thank you in advance for your assistance```
      Insert Code Here

      1 Reply Last reply
      Reply Quote 0
      • T
        tomas_hora administrators
        last edited by

        Do you see the PLC when you try to Attach it againg? (Right click on PLC->Attach PLC -> UDP Broadcast)

        1 Reply Last reply
        Reply Quote 0
        • M
          msoenen
          last edited by

          Hello

          Yes, I can see the PLC
          in the appendix, the screenshots that I see
          I checked the IP address on my router and it is 192.168.1.40
          I already had problems when switching to 2.2, because by 2 times, the variables were duplicated, and the plc no longer worked, and I had to delete all the duplicate variables, and it's a big job[texte du lien]
          (https://1drv.ms/u/s!Aq__SFpXusxkgbsO0aXb02aOyHXhSw?e=aNadYM)
          https://1drv.ms/u/s!Aq__SFpXusxkyDClTBLXk0QoVXnV?e=0JOTym
          https://1drv.ms/u/s!Aq__SFpXusxkgbsQjvU4ZrB13xv5kQ?e=YiRcp7
          https://1drv.ms/u/s!Aq__SFpXusxkgbsN7vJdQ1gMJYMJqg?e=TwS47K

          Thanks on adavance for you help

          1 Reply Last reply
          Reply Quote 0
          • T
            tomas_hora administrators
            last edited by

            This "Limited functionality" message means that the IDE cannot connect to the PLC using TCP using the IP address it found in the previous "Attachment" step using UDP broadcast.

            Can you access the website of the plc? http://192.168.1.40 ?

            1 Reply Last reply
            Reply Quote 0
            • M
              msoenen
              last edited by

              Problem solved, I did a complete reinstallation in version 2.2, because version 2.3 does not work for me

              thanks

              1 Reply Last reply
              Reply Quote 0

              Hello! It looks like you're interested in this conversation, but you don't have an account yet.

              Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.