    Evok problem getting I/O boards data
    3524
      tempurpri last edited by
      I've had some problems with evok in the past, which I was finally able to solve with a fresh OS installation and by adapting ports before installing Codesys (which I need on the Neuron S103 that I have).
      See the linked discussion for further information:
      https://forum.unipi.technology/topic/516/evok-high-cpu-usage/10
      Recently however another problem appeared.
      Evok (service) is running Nginx (service) is running, however I'm unable to access the I/Os through the web page neither throught the modbus server. Both were working for me.
      As far as I can remember the only thing that was done during this time was the usual apd-get update / apt-get upgrade.
      Unfortunately I cannot pinpoint exactly when the problem appeared because I don't need this functionality all the time.
      To make thinfs clear, here is how the web page appears:
      No inputs or outputs are accessible.
      I'm supplying the information that might help shed some light on the situation if anyone can help
      lsmod
      Module                  Size  Used by
      can_raw                 7426  0
      can                    31515  1 can_raw
      w1_therm                6401  0
      w1_gpio                 4818  0
      ds2482                  4427  0
      wire                   32619  3 ds2482,w1_gpio,w1_therm
      cn                      5889  1 wire
      at24                    7587  0
      spidev                  7373  0
      nvmem_core             13774  1 at24
      rtc_ds1307             13908  0
      hwmon                  10552  1 rtc_ds1307
      brcmfmac              292632  0
      brcmutil                9863  1 brcmfmac
      cfg80211              544545  1 brcmfmac
      rfkill                 20851  2 cfg80211
      i2c_bcm2835             7167  0
      spi_bcm2835             7596  0
      bcm2835_gpiomem         3940  0
      uio_pdrv_genirq         3923  0
      fixed                   3285  0
      uio                    10204  1 uio_pdrv_genirq
      i2c_bcm2708             5994  0
      i2c_dev                 6913  0
      ip_tables              13161  0
      x_tables               20578  1 ip_tables
      ipv6                  408900  27
      i2cdetect 1
      WARNING! This program can confuse your I2C bus, cause data loss and worse!
      I will probe file /dev/i2c-1.
      I will probe address range 0x03-0x77.
      Continue? [Y/n] y
      10: -- -- -- -- -- -- -- -- UU -- -- -- -- -- -- --
      50: -- -- -- -- -- -- -- UU -- -- -- -- -- -- -- --
      60: -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- UU
      70: -- -- -- -- -- -- -- --
      ps -fax
        PID TTY      STAT   TIME COMMAND
          2 ?        S      0:00 [kthreadd]
          3 ?        S      0:00  \_ [ksoftirqd/0]
          5 ?        S<     0:00  \_ [kworker/0:0H]
          6 ?        S      0:00  \_ [kworker/u8:0]
          7 ?        S      0:00  \_ [rcu_sched]
          8 ?        S      0:00  \_ [rcu_bh]
          9 ?        S      0:00  \_ [migration/0]
         10 ?        S<     0:00  \_ [lru-add-drain]
         11 ?        S      0:00  \_ [cpuhp/0]
         12 ?        S      0:00  \_ [cpuhp/1]
         13 ?        S      0:00  \_ [migration/1]
         14 ?        S      0:00  \_ [ksoftirqd/1]
         16 ?        S<     0:00  \_ [kworker/1:0H]
         17 ?        S      0:00  \_ [cpuhp/2]
         18 ?        S      0:00  \_ [migration/2]
         19 ?        S      0:00  \_ [ksoftirqd/2]
         21 ?        S<     0:00  \_ [kworker/2:0H]
         22 ?        S      0:00  \_ [cpuhp/3]
         23 ?        S      0:00  \_ [migration/3]
         24 ?        S      0:00  \_ [ksoftirqd/3]
         26 ?        S<     0:00  \_ [kworker/3:0H]
         27 ?        S      0:00  \_ [kdevtmpfs]
         28 ?        S<     0:00  \_ [netns]
         29 ?        S      0:00  \_ [khungtaskd]
         30 ?        S      0:00  \_ [oom_reaper]
         31 ?        S<     0:00  \_ [writeback]
         32 ?        S      0:00  \_ [kcompactd0]
         33 ?        S<     0:00  \_ [crypto]
         34 ?        S<     0:00  \_ [bioset]
         35 ?        S<     0:00  \_ [kblockd]
         36 ?        S<     0:00  \_ [watchdogd]
         38 ?        S<     0:00  \_ [rpciod]
         39 ?        S<     0:00  \_ [xprtiod]
         40 ?        S      0:00  \_ [kswapd0]
         41 ?        S<     0:00  \_ [vmstat]
         42 ?        S<     0:00  \_ [nfsiod]
         52 ?        S<     0:00  \_ [kthrotld]
         53 ?        S<     0:00  \_ [bioset]
         54 ?        S<     0:00  \_ [bioset]
         55 ?        S<     0:00  \_ [bioset]
         56 ?        S<     0:00  \_ [bioset]
         57 ?        S<     0:00  \_ [bioset]
         58 ?        S<     0:00  \_ [bioset]
         59 ?        S<     0:00  \_ [bioset]
         60 ?        S<     0:00  \_ [bioset]
         61 ?        S<     0:00  \_ [bioset]
         62 ?        S<     0:00  \_ [bioset]
         63 ?        S<     0:00  \_ [bioset]
         64 ?        S<     0:00  \_ [bioset]
         65 ?        S<     0:00  \_ [bioset]
         66 ?        S<     0:00  \_ [bioset]
         67 ?        S<     0:00  \_ [bioset]
         68 ?        S<     0:00  \_ [bioset]
         69 ?        S<     0:00  \_ [bioset]
         70 ?        S<     0:00  \_ [bioset]
         71 ?        S<     0:00  \_ [bioset]
         72 ?        S<     0:00  \_ [bioset]
         73 ?        S<     0:00  \_ [bioset]
         74 ?        S<     0:00  \_ [bioset]
         75 ?        S<     0:00  \_ [bioset]
         76 ?        S<     0:00  \_ [bioset]
         77 ?        S<     0:00  \_ [iscsi_eh]
         78 ?        S<     0:00  \_ [dwc_otg]
         80 ?        S<     0:00  \_ [DWC Notificatio]
         81 ?        S<     0:00  \_ [VCHIQ-0]
         82 ?        S<     0:00  \_ [VCHIQr-0]
         83 ?        S<     0:00  \_ [VCHIQs-0]
         84 ?        S      0:00  \_ [VCHIQka-0]
         85 ?        S<     0:00  \_ [SMIO]
         87 ?        S      0:00  \_ [irq/92-mmc1]
         90 ?        S<     0:00  \_ [bioset]
         91 ?        S      0:01  \_ [mmcqd/0]
         93 ?        S      0:00  \_ [jbd2/mmcblk0p2-]
         94 ?        S<     0:00  \_ [ext4-rsv-conver]
         96 ?        S<     0:00  \_ [ipv6_addrconf]
        147 ?        S      0:00  \_ [kworker/3:2]
        212 ?        S      0:00  \_ [spi0]
        247 ?        S<     0:00  \_ [cfg80211]
        249 ?        S<     0:00  \_ [brcmf_wq/mmc1:0]
        250 ?        S      0:00  \_ [brcmf_wdog/mmc1]
        285 ?        S      0:00  \_ [w1_bus_master1]
        479 ?        S<     0:00  \_ [kworker/3:1H]
        616 ?        S<     0:00  \_ [kworker/1:1H]
        721 ?        S      0:00  \_ [kworker/1:0]
        722 ?        S<     0:00  \_ [kworker/0:1H]
        893 ?        S      0:00  \_ [kworker/1:1]
        904 ?        S      0:00  \_ [kworker/3:0]
        909 ?        S<     0:00  \_ [kworker/2:1H]
        926 ?        S      0:00  \_ [kworker/0:0]
        991 ?        S      0:00  \_ [kworker/0:1]
       1092 ?        S      0:00  \_ [kworker/u8:1]
       1100 ?        S      0:00  \_ [kworker/2:0]
       1112 ?        S      0:00  \_ [kworker/2:2]
       1118 ?        S      0:00  \_ [kworker/2:1]
          1 ?        Ss     0:02 /sbin/init
        119 ?        Ss     0:00 /lib/systemd/systemd-journald
        152 ?        Ss     0:00 /lib/systemd/systemd-udevd
        317 ?        Ssl    0:00 /lib/systemd/systemd-timesyncd
        359 ?        Ss     0:00 /usr/sbin/cron -f
        360 ?        Ss     0:00 avahi-daemon: running [S103-sn344.local]
        390 ?        S      0:00  \_ avahi-daemon: chroot helper
        362 ?        Ss     0:00 /lib/systemd/systemd-logind
        368 ?        Ss     0:01 /opt/neuron-bin/neuron_tcp_server -p 502 --check-firmware
        369 ?        Ss     0:00 /usr/sbin/thd --triggers /etc/triggerhappy/triggers.d/ --socket /run/thd.socket --user nobody --deviceglob /dev/input/event*
        375 ?        Ss     0:00 /usr/bin/dbus-daemon --system --address=systemd: --nofork --nopidfile --systemd-activation
        393 ?        Ssl    0:00 /usr/sbin/rsyslogd -n
        395 ?        SNsl   1:04 node-red
        413 ?        Ssl    0:01 /sbin/apcupsd
        469 tty1     Ss+    0:00 /sbin/agetty --noclear tty1 linux
        486 ?        Ss     0:00 /sbin/netplugd -p /var/run/netplugd.pid
        492 ?        S      0:01 /opt/codesys/bin/codesyscontrol.bin /etc/CODESYSControl.cfg
        505 ?        Sl     8:07  \_ /opt/codesys/bin/codesyscontrol.bin /etc/CODESYSControl.cfg
        497 ?        Ss     0:00 /usr/sbin/sshd -D
        741 ?        Ss     0:00  \_ sshd: pi [priv]
        756 ?        S      0:01  |   \_ sshd: pi@pts/0
        759 pts/0    Ss     0:00  |       \_ -bash
        775 pts/0    S+     1:33  |           \_ htop
        782 ?        Ss     0:00  \_ sshd: pi [priv]
        792 ?        S      0:00      \_ sshd: pi@pts/1
        795 pts/1    Ss     0:01          \_ -bash
       1119 pts/1    R+     0:00              \_ ps -fax
        598 ?        Ss     0:00 /sbin/dhclient -4 -v -pf /run/dhclient.eth0.pid -lf /var/lib/dhcp/dhclient.eth0.leases -I -df /var/lib/dhcp/dhclient6.eth0.leases eth0
        746 ?        Ss     0:00 /lib/systemd/systemd --user
        749 ?        S      0:00  \_ (sd-pam)
        977 ?        Ssl    0:22 /usr/bin/python /opt/evok/evok.py
        979 ?        Z      0:00  \_ [python] <defunct>
        986 ?        Ss     0:00 nginx: master process /usr/sbin/nginx -g daemon on; master_process on;
        987 ?        S      0:00  \_ nginx: worker process
        988 ?        S      0:00  \_ nginx: worker process
        989 ?        S      0:00  \_ nginx: worker process
        990 ?        S      0:00  \_ nginx: worker process
      /boot/config.txt (having the dtoverlay=neuron-spu-new was not problematic during this time .. I could comment it out though if that would welp for some test ?)
      gpu_mem=32
      dtparam=i2c_arm=on,watchdog=on
      dtoverlay=i2c-rtc,mcp7941x
      # disable it on Unipi 1.x (gpio24, 25!)
      dtoverlay=neuron-spi-new
      dtoverlay=neuronee
      #dtoverlay=unipiee
      #Enable kernel driver for I2c OneWire Master
      dtoverlay=ds2482
      #remove dependency of spi-clock on system freq
      core_freq=250
      #BT enabled on RPi3 swaps UART (ttyAMA) and miniUART ttyS0.
      dtoverlay=pi3-disable-bt
      #WIFI disabled
      #dtoverlay=pi3-disable-wifi
      # For more options and information see
      # http://rpf.io/configtxt
      # Some settings may impact device functionality. See link above for details
      # uncomment if you get no picture on HDMI for a default "safe" mode
      #hdmi_safe=1
      # uncomment this if your display has a black border of unused pixels visible
      # and your display can output without overscan
      #disable_overscan=1
      # uncomment the following to adjust overscan. Use positive numbers if console
      # goes off screen, and negative if there is too much border
      #overscan_left=16
      #overscan_right=16
      #overscan_top=16
      #overscan_bottom=16
      # uncomment to force a console size. By default it will be display's size minus
      # overscan.
      #framebuffer_width=1280
      #framebuffer_height=720
      # uncomment if hdmi display is not detected and composite is being output
      #hdmi_force_hotplug=1
      # uncomment to force a specific HDMI mode (this will force VGA)
      #hdmi_group=1
      #hdmi_mode=1
      # uncomment to force a HDMI mode rather than DVI. This can make audio work in
      # DMT (computer monitor) modes
      #hdmi_drive=2
      # uncomment to increase signal to HDMI, if you have interference, blanking, or
      # no display
      #config_hdmi_boost=4
      # uncomment for composite PAL
      #sdtv_mode=2
      #uncomment to overclock the arm. 700 MHz is the default.
      #arm_freq=800
      # Uncomment some or all of these to enable the optional hardware interfaces
      #dtparam=i2c_arm=on
      #dtparam=i2s=on
      #dtparam=spi=on
      # Uncomment this to enable the lirc-rpi module
      #dtoverlay=lirc-rpi
      # Additional overlays and parameters are documented /boot/overlays/README
      # Enable audio (loads snd_bcm2835)
      #dtparam=audio=off
      eeprom verification
      ~ $ sudo grep S103 /sys/bus/i2c/devices/1-0057/eeprom
      Binary file /sys/bus/i2c/devices/1-0057/eeprom matches
      This time however I have a lot of errors in /var/log/evok.log (all the same thought)
      2018-01-21 22:09:32,851 - evok - ERROR - 'NoneType' object has no attribute 'do_scan'
        File "/opt/evok/neuron.py", line 217, in scan_boards
          yield self.modbus_cache_map.do_scan()
      AttributeError: 'NoneType' object has no attribute 'do_scan'
      2018-01-21 22:09:33,354 - evok - ERROR - 'NoneType' object has no attribute 'do_scan'
      2018-01-21 22:09:33,857 - evok - ERROR - 'NoneType' object has no attribute 'do_scan'
      2018-01-21 22:09:34,360 - evok - ERROR - 'NoneType' object has no attribute 'do_scan'
      2018-01-21 22:09:34,862 - evok - ERROR - 'NoneType' object has no attribute 'do_scan'
      It seems that the python script fails in finding the "boards" for the i/o, but I'm not able to find out why.
      Please help, I have a running application on this board and have to connect the I/O signals to it, but I came to a stop with this problem.
        Do you have the Neuron tcp server installed and running? (you can check with "systemctl status neurontcp", or using some utility such as e.g. qModMaster to connect to the Neuron ip address, port 502). It might also help us to know what your Evok config looks like. The message simply means that Evok can't find any recognisable Neuron subdevices on the SPI bus, which requires the Modbus daemon to be running.
        I should mention that it might be easier to use Codesys with TCP/Modbus rather than Evok, but I don't know enough about your intended use to say it for certain. We are also in the finishing stages of implementing native drivers for the digital and analog inputs/outputs as Linux GPIOs and IIOs respectively.
        The other thing is that we should be releasing an actual Codesys Neuron package with 3S (developers of Codesys) support and approval within two or three weeks.
          Yes, Neuron tcp is installed and running (as it was from the original open-source OS).
          ~$systemctl status neurontcp
          ● neurontcp.service - Unipi Neuron Modbus/Tcp Server
             Loaded: loaded (/opt/neuron-bin/neurontcp.service; enabled; vendor preset: en
             Active: active (running) since Mon 2018-01-22 21:58:30 UTC; 1 day 2h ago
           Main PID: 362 (neuron_tcp_serv)
             CGroup: /system.slice/neurontcp.service
                     └─362 /opt/neuron-bin/neuron_tcp_server -p 502 --check-firmware
          Jan 22 21:58:30 S103-sn344 systemd[1]: Started Unipi Neuron Modbus/Tcp Server.
          evok.conf
          [MAIN]
          config_version = 2.4					; Configuration file version, DO NOT CHANGE!
          use_schema_verification = False			; Enabling this will deny any requests that do not match the JSON Schema; NOTE THAT THIS RESULTS IN A SIGNIFICANT INCREASE IN LATENCY AND SHOULD NOT BE USED EXCEPT FOR TESTING
          log_level = ERROR   					; Minimum severity of messages to be logged; one of INFO, DEBUG, WARNING, ERROR, CRITICAL
          log_file = /var/log/evok.log			; Log file to use; will be cleared on boot
          port = 8085								; !!! Internal API port - only change if you are certain you know what you are doing; FOR OUR WEB INTERFACE THE PORT SHOULD BE CHANGED IN "/etc/evok-nginx.conf" INSTEAD !!!
          webhook_enabled = False					; Enables webhook notification - see e.g. https://sendgrid.com/blog/whats-webhook/
          webhook_address = http://127.0.0.1:85   ; Put your server endpoint address here (e.g. http://123.123.123.123:/wh )
          webhook_device_mask = ["input","wd"]	; List of device types to notify on (written as a JSON list) - adding AI will generate a large amount of messages!
          webhook_complex_events = False			; EVOK will send POST requests with the same data as WebSocket, rather than an empty GET request
          wifi_control_enabled = False			; !!! REQUIRES THE UNIPIAP WIFI CONTROLLER TO BE INSTALLED !!! Will allow evok to control the internal Neuron wifi
          soap_server_enabled = False				; Enables the simple SOAP server; use only if you need the functionality
          soap_server_port = 8081					; !!! IF SOAP SERVER IS ENABLED, THIS PORT NEEDS TO BE UNIQUE (i.e. different from the port setting above) !!!
          [NEURON_1]
          global_id = 1							; Mandatory, REQUIRED TO BE UNIQUE
          allow_register_access = True 			; Optional, False default
          scan_frequency = 2 						; Optional, 1 default
          scan_enabled = True 					; Optional, True default
          ; Below you can find examples for connecting devices over UART; first example is a Neuron extension while the second is a custom third-party device
          ; Devices sharing a port use the port settings of the first device on that port (baud rate, parity, stopbits)
          ; !!!Note that device_name has to match a filename in the /etc/hw_definitions directory!!! See /etc/hw_definitions/DOMAT MMIO.yaml for an example
          ;[EXTENSION_1]
          ;global_id = 2							; Mandatory, REQUIRED TO BE UNIQUE
          ;device_name = xS10						; Mandatory
          ;modbus_uart_port = /dev/extcomm/0/0 	; Mandatory
          ;neuron_uart_circuit = 1_01				; Optional, allows associating extensions with specific Neuron UART-over-Modbus ports (not possible for non-Modbus UART ports, e.g. /dev/ttyUSB0 or /dev/ttyS0)
          ;allow_register_access = True 			; Optional, False default, is mandatory with third-party devices
          ;address = 15 							; Optional, 15 default
          ;scan_frequency = 2 					; Optional, 1 default
          ;scan_enabled = True 					; Optional, True default
          ;baud_rate = 19200						; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN
          ;parity = N								; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN
          ;stop_bits = 1							; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN
          ;[EXTENSION_2]
          ;global_id = 3							; Mandatory, REQUIRED TO BE UNIQUE
          ;device_name = CUSTOM MODBUS DEVICE		; Mandatory
          ;allow_register_access = True 			; Mandatory with third-party devices
          ;address = 1 							; Optional, 15 default
          [OWBUS_1]
          owbus = /dev/i2c-1 --i2c=/dev/i2c-1:ALL     		; Scanned bus (--i2c=/dev/i2c-1:ALL or localhost:2122 or 'u' for USB dongle)
          interval = 3          					; [s] Default sensor reading
          scan_interval = 300    					; [s] How often is scanning done
          ;Example of 1W-4R/4DI extension module, 1W-8R is almost the same, only with inputs instead of relays
          ; - Map a new 1Wire sensor with the appropriate address, type and interval
          ; - The syntax can be either SENSOR or 1WDEVICE
          ; - Setting the correct reading interval is crucial to achieve ideal performance; the default interval is 15s
          ;[1WDEVICE_2]
          ;bus = 1
          ;address = 29F39A17000000BC
          ;type = DS2408
          ;interval = 1
          ;[1WRELAY_10]
          ;sensor = 2
          ;pin = 0
          ;[1WRELAY_11]
          ;sensor = 2
          ;pin = 1
          ;[1WRELAY_12]
          ;sensor = 2
          ;pin = 2
          ;[1WRELAY_13]
          ;sensor = 2
          ;pin = 3
          ;[1WINPUT_20]
          ;sensor = 2
          ;pin = 4
          ;[1WINPUT_21]
          ;sensor = 2
          ;pin = 5
          ;[1WINPUT_22]
          ;sensor = 2
          ;pin = 6
          ;[1WINPUT_23]
          ;sensor = 2
          ;pin = 7
          evok-nginx.conf
          server {
          	listen 85 default_server;
          	server_name  _;
          	#ssl on;
          	#ssl_certificate      /etc/nginx/democert.pem;
          	#ssl_certificate_key  /etc/nginx/democert.key;
          	access_log  /var/log/evok.access.log;
          	root /var/www/evok;
          	location / {
          	    index index.html;
          	location /ws {
          		proxy_pass http://localhost:8085;
          		proxy_set_header Host $host:$server_port;
          		proxy_http_version 1.1;
          		proxy_set_header Upgrade $http_upgrade;
          		proxy_set_header Connection "upgrade";
          		proxy_buffering off;
          		proxy_cache off;
          		#send_timeout 120;
          		proxy_read_timeout 180;
          		#proxy_set_header X-Real-IP $remote_addr;
          	location /rest {
          	location /json {
          I can see the tcp port 502 opened at 127.0.0.1
          I also know that Modbus is the better way to go .. in fact that was the way I also had it working (as you can probably see from the setting in evok.conf), but modbus access went down too - it's not working either. Connecting to the modbus server, trying to read one register at address 0 I only get a modbus exception error code 2.
          I noticed one additional error as shown below, specifically if it means anything new...doubt it though.
          ~ $ systemctl status evok
          ● evok.service - Evok Modbus/Websocket/Rpc Server
             Loaded: loaded (/etc/systemd/system/evok.service; enabled; vendor preset: enabled)
             Active: active (running) since Wed 2018-01-24 00:42:03 UTC; 3s ago
           Main PID: 1807 (python)
             CGroup: /system.slice/evok.service
                     └─1807 /usr/bin/python /opt/evok/evok.py
          Jan 24 00:42:03 S103-sn344 systemd[1]: Started Evok Modbus/Websocket/Rpc Server.
          Jan 24 00:42:07 S103-sn344 OWFS[1812]: DEFAULT: owlib.c:(52) No valid 1-wire buses found
          I guess that if the modbus deamon isn't working properly the problem is somewhere deeper.
          (Modbus TCP access to I/Os was fine and fast whle it was forking. Now it's not. But I really look forward to accessing the I/Os directly from Codesys. Alas deadlines are deadlines and I have to get this working at least as it was about a month ago.)
          Do you think it's possible a system update (as I mentioned i DID perform a apt-get update / upgrade during this time) might have introduced some sort of an incompatibility ? Do you have any other suggestion ?
          FYI last time (if you check my other post) reinstalling evok / neurontcp didn't help at all....but then there were what seemed other issues.
          Thanks for your help
            Oh right, I know what the issue is - we've encountered the same thing when trying to get Codesys working - Codesys has its own 1Wire driver which is not compatible with other ones out of the box - meaning that only Codesys can communicate with 1Wire devices when it is installed, including the I/O board.
            This is a known issue with Codesys not supporting OWFS. At least not fully and officially, there are hacks to get it working somewhat (by having the Codesys driver emulate a virtual 1Wire bus master, which then OWFS connects to - this causes various issues however), but they are unsupported.
            Our solution for Codesys was to disable EVOK 1Wire (and Mervis, which is not compatible 1Wire-wise as well) when Codesys installation is detected.
            You might wish try to get the board working through Codesys 1Wire instead.
              tomas_hora administrators @tempurpri last edited by
              @tempurpri Codesys for Neurons will be soon released (also discussed here https://forum.unipi.technology/topic/549/codesys-on-unipi-neuron-installing-issues-help-please )
                Andrew Watson last edited by
                Sorry to hijack this thread a little, but it seems that I have a very similar problem, so maybe this can help both of us?
                I get the same empty web interface, but I'm not using Codesys as far as I know.
                I started with a bare install of Raspbian stretch lite, installed a few basic things
                apt-get install git vim supervisor python-gpiozero
                Then followed the installation instructions from the evok git repository.
                I get the same error:
                $ tail /var/log/evok.log
                2018-01-24 11:03:13,781 - evok - ERROR - 'NoneType' object has no attribute 'do_scan'
                  File "/opt/evok/neuron.py", line 225, in scan_boards
                2018-01-24 11:03:14,283 - evok - ERROR - 'NoneType' object has no attribute 'do_scan'
                status looks ok to me :
                   Active: active (running) since Wed 2018-01-24 11:03:18 UTC; 3min 50s ago
                 Main PID: 340 (python)
                           ├─340 /usr/bin/python /opt/evok/evok.py
                           └─464 /usr/bin/python /opt/evok/evok.py
                Jan 24 11:03:44 unipi01 OWFS[464]: DEFAULT: ow_reconnect.c:(72) DS2482-100 bus master reconnected
                Jan 24 11:04:11 unipi01 OWFS[464]: DEFAULT: ow_reconnect.c:(72) DS2482-100 bus master reconnected
                Here are the open ports:
                $ netstat -le
                Active Internet connections (only servers)
                Proto Recv-Q Send-Q Local Address           Foreign Address         State       User       Inode
                tcp        0      0 0.0.0.0:ssh             0.0.0.0:*               LISTEN      root       12789
                tcp        0      0 0.0.0.0:502             0.0.0.0:*               LISTEN      root       9194
                tcp        0      0 0.0.0.0:http            0.0.0.0:*               LISTEN      root       12806
                tcp        0      0 0.0.0.0:http-alt        0.0.0.0:*               LISTEN      root       10395
                tcp6       0      0 [::]:ssh                [::]:*                  LISTEN      root       12791
                tcp6       0      0 [::]:http-alt           [::]:*                  LISTEN      root       10396
                udp        0      0 0.0.0.0:mdns            0.0.0.0:*                           avahi      10357
                udp        0      0 0.0.0.0:51138           0.0.0.0:*                           avahi      10359
                udp        0      0 0.0.0.0:bootpc          0.0.0.0:*                           root       9499
                udp6       0      0 [::]:mdns               [::]:*                              avahi      10358
                udp6       0      0 [::]:56078              [::]:*                              avahi      10360
                raw6       0      0 [::]:ipv6-icmp          [::]:*                  7           root       9502
                Active UNIX domain sockets (only servers)
                Proto RefCnt Flags       Type       State         I-Node   Path
                unix  2      [ ACC ]     STREAM     LISTENING     11523    /run/user/1000/systemd/private
                unix  2      [ ACC ]     STREAM     LISTENING     12867    /tmp/tmux-1000/default
                unix  2      [ ACC ]     STREAM     LISTENING     11528    /run/user/1000/gnupg/S.gpg-agent
                unix  2      [ ACC ]     STREAM     LISTENING     11531    /run/user/1000/gnupg/S.gpg-agent.ssh
                unix  2      [ ACC ]     STREAM     LISTENING     11533    /run/user/1000/gnupg/S.gpg-agent.extra
                unix  2      [ ACC ]     STREAM     LISTENING     11535    /run/user/1000/gnupg/S.gpg-agent.browser
                unix  2      [ ACC ]     STREAM     LISTENING     10769    /var/run/supervisor.sock.530
                unix  2      [ ACC ]     STREAM     LISTENING     9275     /var/run/avahi-daemon/socket
                unix  2      [ ACC ]     STREAM     LISTENING     9278     /var/run/dbus/system_bus_socket
                unix  2      [ ACC ]     STREAM     LISTENING     9281     /run/thd.socket
                unix  2      [ ACC ]     STREAM     LISTENING     9399     /var/run/dhcpcd.sock
                unix  2      [ ACC ]     STREAM     LISTENING     9401     /var/run/dhcpcd.unpriv.sock
                unix  2      [ ACC ]     STREAM     LISTENING     6355     /run/systemd/private
                unix  2      [ ACC ]     SEQPACKET  LISTENING     6369     /run/udev/control
                unix  2      [ ACC ]     STREAM     LISTENING     6372     /run/systemd/fsck.progress
                unix  2      [ ACC ]     STREAM     LISTENING     6375     /run/systemd/journal/stdout
                Rebooting and restarting evok (via sudo service evok restart) doesn't help.
                  Some additional information, since I had time. I flashed a new sd card with a brand new raspbian stretch lite image (latest version, 2017-11-29)
                  installed git and updated the system
                  sudo -s
                  apt-get install git
                  apt-get update && apt-get upgrade -y && apt-get dist-upgrade -y
                  raspi-config and changed the hostname
                  Then installed the latest evok version (from commit 8a14c95 it seems).
                  • Selected website port 80
                  • Internal API port 8080
                  • Install for Unipi Neuron (I have the S103)
                  • No WiFi
                  • Reboot
                  And this time it works... I don't know if this is due to something that was changed in the last commit (between 11am and 1.30pm today) or simply not installing the gpiozero library.
                    tempurpri @TomasKnot last edited by
                    @tomas_knot The incompatibility with Codesys (the one you mention and the port incompatibility) would be an understandeable reason for the problems I have....had I not managed to have a working setup of Codesys for raspberry and evok running in the last month.
                    Unless the 1-wire incompatibility between the two only becomes problematic with time (I'm not sure how that could be), then that was not the case for me. Just to make it clear Codesys and digital signal readout worked for me ... Modbus acces and the web interface. I needed that functionality only occasionally, so I'm not sure when it stopped working, but it was during the last month. Neither Codesys nor evok were re-installed nor was there any change in their configuration.
                    I'm trying to find out what happened and especially try to make it work again.
                    @tomas_knot @tomas_hora I understand that proper codesys integration is coming, but unless it's coming during this week it won't help my application. Unfortunately that's the timeframe I'm looking at, nothing to do with with Unipi itself.
                    OK, so if codesys 1 wire driver is the suspect, is there a way to check that and maybe disable it within the Codesys editor ?
                      TomasKnot @Andrew Watson last edited by TomasKnot
                      @Andrew-Watson said in Evok problem getting I/O boards data:
                      sudo -s
                      apt-get install git
                      • No WiFi
                      • Reboot
                      It's quite likely it may be the GPIOZero library. Generally speaking software connected to hardware in a direct manner (with its own drivers etc.) is considerably less compatible among itself than other software. We test EVOK internally on clean Raspbian, as well as with our own image, which is based on the Raspbian Zero; for these combinations, along with some simple software (in fact EVOK installs vim itself), the software does pass testing (with occasional edge issues e.g. the light sensor issue recently).
                      As to a guess why the GPIOZero library could be causing issues - we use 4 of the GPIO lines on the RPi to expand the primary SPI bus with interrupts and an extra device select slot. This (among other things) is done through the device overlay installed by EVOK, but it's possible that other software (at least one which is set up under root privileges) might change it, particularly if it deals with GPIO functionality.
                      The latest commits only changed functionality related to the Sedtronic WTS DS2438 1Wire sensor, so it's very unlikely to have caused the problem. The issue you (and @tempurpri) are seeing is due to the expected boards not being found on the SPI bus - this can be because the SPI bus does not function correctly for some reason, or because the I2C EEPROM which stores data about which boards are expected does not function correctly.
                      @tempurpri said in Evok problem getting I/O boards data:
                      I was assuming you have a 1Wire UniPi expansion board, which would not work correctly with Codesys. If you do not, it may still be possible to get it running. But first - does the device function correctly with a clean non-Codesys image? If yes then we can confidently say the issue lies with Codesys, and proceed from there.