      Iogo
      last edited by

      I have been trying to connect PT1000 to Neuron S103 AO or AI without success.

      Resistance to temperature conversion has been chosen, also PT1000 is selected.

      Neuron S10x_AO_1 resulting in PLC value of -246.8609 etc..

      Tried following youtube tutorial with no success. Should I connect the PT1000 to AI or AO? I bet if I connect resistor to ao or ai, it still shows the same.

      Any ideas?

      T 1 Reply Last reply
      Reply Quote 0
      • T
        tomas_hora administrators @Iogo
        last edited by

        @Iogo Resistance measurement on S103 is available only on Analog Output (even though it sounds a bit wierd). You have to connect the sensor between AO and AGND. Did you follow the chapetr 2.8.2.1Analog Outputof group 1 (Alternatively Resistance Analog Input–Pt1000)?

        1 Reply Last reply
        Reply Quote 0
        • I
          Iogo
          last edited by

          Well, at first, i thought it would do these all connections internally after selection has been done with the AO/AI channel to measure resistance and just put it directly to a variable, which would have been easy.. Then I tried the function block, but as you can see..nothing

          0_1509017111485_aoi module.jpg

          T 1 Reply Last reply
          Reply Quote 0
          • T
            tomas_hora administrators @Iogo
            last edited by

            @Iogo It seems that the measured resistance is really too small = 9Ω. Is it really Pt1000? And do you really have it connected?

            1 Reply Last reply
            Reply Quote 0
            • T
              tomas_hora administrators
              last edited by

              Btw what are the AO_moed and AO_1 variables? Are they mapped to the HW? It should be like like this. (We might need to update the documentation)
              0_1509024911409_neuron_resistance.png

              1 Reply Last reply
              Reply Quote 0
              • I
                Iogo
                last edited by

                They are mapped to hw, although the name does not imply that. Exactly as in your example. Did not get it to work, so I decided to add a modbus device, 4 channel analog output module and take the pt1000 temperatures through another modbus device...seemed easier way to go =)

                1 Reply Last reply
                Reply Quote 0

                Hello! It looks like you're interested in this conversation, but you don't have an account yet.

                Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.