Neurons Analog Input (AI) measurement accuracy problem

  • 0_1502707122643_upload-2af07c63-c828-41af-ab98-d9a821eea0ac

    After installation brand new Neuron in group 1 on Analog input 1_01 shows the value 0.017V (when it is connected to the GND)
    According to data sheet point 4.3 measurement accuracy should be +/-0.5% it means maximum deviation for 1V on AI should be 0.005V.

    How can I tune Neurons analog input to get 0V?


  • administrators

    @wizro_pl That is a common behaviour of most analogue inputs... If you want to have 0 than set a limit eg 0.03V that everything below is 0V