    Neurons Analog Input (AI) measurement accuracy problem

    Scheduled Pinned Locked Moved Neuron Series
    2 Posts 2 Posters 2.1k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • W
      wizro_pl
      last edited by

      0_1502707122643_upload-2af07c63-c828-41af-ab98-d9a821eea0ac

      After installation brand new Neuron in group 1 on Analog input 1_01 shows the value 0.017V (when it is connected to the GND)
      According to data sheet point 4.3 measurement accuracy should be +/-0.5% it means maximum deviation for 1V on AI should be 0.005V.

      How can I tune Neurons analog input to get 0V?

      BR,
      D.

      T 1 Reply Last reply
      Reply Quote 0
      • T
        tomas_hora administrators @wizro_pl
        last edited by

        @wizro_pl That is a common behaviour of most analogue inputs... If you want to have 0 than set a limit eg 0.03V that everything below is 0V

        1 Reply Last reply
        Reply Quote 0

        Hello! It looks like you're interested in this conversation, but you don't have an account yet.

        Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.