      Hi ,

      I need help with EMO-AO4/12 Setup ,

      in Mervis what would be the device address of EMO-AO4/12 (hex or dec)

      how can i check if it's connected to the unipi or not

      how can i pass value to the EMO-AO4/12 analog channel buy using HMI

      Many thanks

      T 1 Reply Last reply Reply Quote 0
      • T
        todward last edited by

        Hi,

        the device address in Mervis is decimal (eg. "71" with all DIP switches on EMO set to "On"). The connection via I2C-Bus to UniPi is indicated by a LED below the address DIP switch. This is the hardware side. In Mervis you can check in debugging mode if your solution with EMO-AO5/12 works.
        I cannot answer your question regarding HMI, because I only use the PWM channels 4-12 with PI/PID-controller.

        Best regards

        1 Reply Last reply Reply Quote 1
        • B
          Bassam Alsibai last edited by

          @todward many thanks for your kind support

          1 Reply Last reply Reply Quote 0
          • T
            tomas_hora administrators @Bassam Alsibai last edited by

            @Bassam-Alsibai Just like any other variable. Make sure that the the output can be set while in debug mode from the variable manager and then just follow the youtube mervis hmi tutorial