1 wire net dies "Problem solved"
-
Now it has happened again
did not help with shielded cable
I'll test to update to the latest UniPi-Mervis-OS 2016-12-06
-
@zorro_66 Please test and report, any possibility to use shielded cable between the sensors?
-
@zorro_66 did you connect shield to the ground ? it is necessary.
-
Yes as in the picture
-
Now it has worked in two days
My second Unipi do not have these problems
where I have 20 pieces of sensors connected in a star network with no shielded cable.
Does it help to update the software in Rpi.
There seems to be some software errors.
Just got home 2 1-Wire hub from Unipi.
Can i connect with a standard RJ45 patch cable -
Now, I have rebuilt my entire 1-wire network and used Unipi hub instead
so now we will see if the network stops die
-
My 1-wire is incredibly unstable
network dies at irregular intervals, showing unreasonable temperatures.
I have rebuilt my net for spec from Unipi wiki shielded cat5 cable and hubs.
But no difference 1-wire network die anyways.
So it can not be anything wrong with the network itself, but the fault must be in Unipi alt. software.
Grateful for help . -
@zorro_66 Can you try enabling the CRC check at the sensors? Just check the box in the sesors in the Scratchpad group. You might need to make the sensor as a custom and backup your project before playing with it
-
I do not understand what you mean now
-
-
aha tanks:thumbsup_tone3:
-
Problem solved, I finally found a bad solder
at the VCC pin caused power loss in my 1-wire network
-
We are sorry for that @zorro_66!
But it is really hard to find out this kind of issue during our test but we will update our testing procedures... Thanks for the info.