    BACnet "Commandable with priority array"
    Scheduled Pinned Locked Moved Mervis
    2 Posts 2 Posters 926 Views
    • L
      lyngaas
      Our Belimo Energy Valve requires a special mode for updating the setpoint. Regular writes fail. I tried selecting a Priority (instead of "Not Specified"), but that was not sufficient.
      Belimo BACnet interface description
      Belimo EDE file
      Any tips for how to configure AO[1] correctly in Mervis?
      (Updating setpoint with the valve in Modbus mode works as expected, but they have not exposed some readonly-values that we need through Modbus.)
      Thanks,
      Ståle
      1 Reply Last reply
      Reply Quote 0
        AVsetula
        Hi @lyngaas,
        This bug where it is not possible to write a value from the PLC to the connected device appeared in some versions of the Mervis IDE, but we have always fixed it with the release of a newer version of the IDE.
        It is currently functional in all Mervis IDE versions supporting BACnet:
        • Mervis IDE 2.3.0 (106337)
        • Mervis IDE 2.4.0 (117845)
        • Mervis IDE 2.4.1 (125493)
        Antonin
        1 Reply Last reply
        Reply Quote 0
        Hello! It looks like you're interested in this conversation, but you don't have an account yet.
        Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.