M525 stopped working
I am running latest available Mervis version (2.2.0.30). After 10 days of operation, the modbus communication over serial port RS485-1.1 failed. I am reading some values from 3 Inepro power meters.
Hi @Martin-Kudláček,
I found article: https://kb.unipi.technology/en:sw:04-unipi-firmware?s[]=firmware
I had firmware v5.40 and just updated now to v5.50.
Hello @pascal37,
all of that is ok. You can check what is going on on the serial port in Mervis IDE directly. Switch to debugging mode and in the bottom panel look for "port monitor". Start the monitoring of the affected port. You should see more information.Also, try disconnecting the meters to see if the problem is caused by one of them. And also make sure, that you use shielded twist pair cables, with the shielding connected to earth ground on one end and use proper termination of the bus.
Hi @martin-kudláček,
The problem recurred, again after 10 days of smooth operation.
Here is the output of the serial port:
Since the solution works fine during multiple days without any error on the serial interface, I do not think there is an issue on the RS485 bus. Yes, I am using am appropriate shielded cable with terminations on both ends.
I recently replaced the M505 with an M525 because of relay issues but I never had this RS485 serial bus issue with the M505 !?
There are 3 Inepro PRO380 devices on the bus, I tried to disconnect each Meter, one after the other, but the issue seems not caused by one of them. I have also connected each meter individually direcly to the M525 with another cable but no success either.
Anything else we can do on the M525 to further troublehoot before I try restart/redeploy the solution ?
Many thanks in advance and kind regards,
Pascal
A simple "sudo reboot" of the PLC has solved the issue and communication works again error free:
Current serial port is RS485-1.1, I will try if same issue occurs after 10 days if using port RS485-1.3 ...
No issue after 15 days of uptime using port RS485-1.3 :
I switch now back to port RS485-1.1 to check if issue occurs again after 10 days...
@pascal37 if it occurs again, please send the captured data on the port monitor in txt file from a longer period so we could get better overview
Hi @tomas_hora,
The issue occured again with port RS485-1.1 just after 5 days of uptime, but sorry, I was not capturing serial data before the "crash". This is quite difficult to do: it means leave IDE open in debugging mode during up to 10 days and be able to select all the output (> 50 millions packets) !? Is there any better why to archieve that ?
Workaround is to redeploy the solution from IDE (cold restart), and serial communication works again immedately.
The issue is definitvely not on the RS485 bus or Inepro devices.I had this issue now 3 times with the port 1.1 on the Axon M525, but not with port 1.3, nor with an Axon M505.
Since a solution deploy does not reboot the Debian OS of the PLC, the issue should be somewhere in the Mervis runtime !?The first time the issue occured, I did a complete reboot of the PLC, but this is not a workaround... as if a counter in the Mervis runtime is not reseted properly like a solution deploy with cold restart.
Many thanks in advance for your help and kind regards.
Hello @pascal37, I did not men to capture the data at the time it stops responding, but jus to get a longer period of the caputed data after it stops communicatig to find out if it's all timeout or what is going on the line.
What should be the configuration of the RS485 (baudrate, parity, ...)
Could you execute this command in linux while the communication stops?
cat /run/unipi/io_group1/uart_config -
Hi @tomas_hora,
Issue occurred again with port RS485-1.1
This time, a simple reboot (from Debian OS) was enough to regain data acquisition from the 3 Inepro PRO380 meters.
Port configuration:
cat /run/unipi/io_group1/uart_config 9bdData captured after communication stops working:
09:02:36.2939 => Sending: 02 03 50 12 00 02 75 3D 09:02:36.3139 <= Receiving: CB EC EB 09:02:36.3139 Timeout 09:02:36.3239 => Sending: 02 03 50 12 00 02 75 3D 09:02:36.3439 <= Receiving: CB EC EB 09:02:36.3439 Timeout 09:02:36.3639 => Sending: 02 03 60 00 00 02 DA 38 09:02:36.3839 <= Receiving: EC EB 09:02:36.3839 Timeout 09:02:36.3939 => Sending: 02 03 60 00 00 02 DA 38 09:02:36.4139 <= Receiving: 6D D5 09:02:36.4139 Timeout 09:02:36.4239 => Sending: 02 03 60 00 00 02 DA 38 09:02:36.4539 <= Receiving: 6D D5 09:02:36.4539 Timeout 09:02:36.4739 => Sending: 03 03 50 12 00 02 74 EC 09:02:36.4939 <= Receiving: 6D D5 09:02:36.4939 Timeout 09:02:36.5039 => Sending: 03 03 50 12 00 02 74 EC 09:02:36.5359 <= Receiving: 68 5B 09:02:36.5359 Timeout 09:02:36.5459 => Sending: 03 03 50 12 00 02 74 EC 09:02:36.5659 <= Receiving: 6F 68 5B 09:02:36.5659 Timeout 09:02:36.5859 => Sending: 03 03 60 00 00 02 DB E9 09:02:36.6059 <= Receiving: 68 5B 09:02:36.6059 Timeout 09:02:36.6159 => Sending: 03 03 60 00 00 02 DB E9 09:02:36.6459 <= Receiving: 3D F3 8F 09:02:36.6459 Timeout 09:02:36.6559 => Sending: 03 03 60 00 00 02 DB E9 09:02:36.6759 <= Receiving: F3 8F 09:02:36.6759 Timeout 09:02:36.7009 => Sending: 01 03 50 02 00 06 75 08 09:02:36.7209 <= Receiving: F3 8F 09:02:36.7209 Timeout 09:02:36.7309 => Sending: 01 03 50 02 00 06 75 08 09:02:36.7599 <= Receiving: 43 09:02:36.7599 Timeout 09:02:36.7699 => Sending: 01 03 50 02 00 06 75 08 09:02:36.8399 Timeout 09:02:36.8599 => Sending: 01 03 50 12 00 02 75 0E 09:02:36.8599 <= Receiving: 43 73 00 00 43 09:02:36.8599 <= Receiving: 72 99 9A A3 09:02:36.8599 Wrong telegram: ??? 09:02:36.8699 => Sending: 01 03 50 12 00 02 75 0E 09:02:36.9399 Timeout 09:02:36.9499 => Sending: 01 03 50 12 00 02 75 0E 09:02:36.9699 <= Receiving: 62 23 09:02:36.9699 Timeout 09:02:36.9899 => Sending: 01 03 60 0C 00 02 1A 08 09:02:37.0099 <= Receiving: 62 23 09:02:37.0099 Timeout 09:02:37.0199 => Sending: 01 03 60 0C 00 02 1A 08 09:02:37.0519 <= Receiving: 9F 09:02:37.0519 Timeout 09:02:37.0619 => Sending: 01 03 60 0C 00 02 1A 08 09:02:37.1319 Timeout 09:02:37.1519 => Sending: 01 03 60 18 00 02 5A 0C 09:02:37.1719 <= Receiving: 00 5C 09:02:37.1719 Timeout 09:02:37.1819 => Sending: 01 03 60 18 00 02 5A 0C 09:02:37.2129 <= Receiving: 69 26 09:02:37.2129 Timeout 09:02:37.2229 => Sending: 01 03 60 18 00 02 5A 0C 09:02:37.2429 <= Receiving: 69 26 09:02:37.2429 Timeout 09:02:37.2629 => Sending: 02 03 50 12 00 02 75 3D 09:02:37.2829 <= Receiving: 52 69 26 09:02:37.2829 Timeout 09:02:37.2929 => Sending: 02 03 50 12 00 02 75 3D 09:02:37.3129 <= Receiving: EA 1D 09:02:37.3129 Timeout 09:02:37.3229 => Sending: 02 03 50 12 00 02 75 3D 09:02:37.3429 <= Receiving: EA 1D 09:02:37.3429 Timeout 09:02:37.3629 => Sending: 02 03 60 00 00 02 DA 38 09:02:37.3839 <= Receiving: EA 1D 09:02:37.3839 Timeout 09:02:37.3939 => Sending: 02 03 60 00 00 02 DA 38 09:02:37.4139 <= Receiving: 6D D5 09:02:37.4139 Timeout 09:02:37.4239 => Sending: 02 03 60 00 00 02 DA 38 09:02:37.4439 <= Receiving: 6D D5 09:02:37.4439 Timeout 09:02:37.4639 => Sending: 03 03 50 12 00 02 74 EC 09:02:37.4849 <= Receiving: 6D D5 09:02:37.4849 Timeout 09:02:37.4949 => Sending: 03 03 50 12 00 02 74 EC 09:02:37.5159 <= Receiving: 68 5B 09:02:37.5159 Timeout 09:02:37.5259 => Sending: 03 03 50 12 00 02 74 EC 09:02:37.5459 <= Receiving: 68 5B 09:02:37.5459 Timeout 09:02:37.5659 => Sending: 03 03 60 00 00 02 DB E9 09:02:37.5859 <= Receiving: 68 5B 09:02:37.5859 Timeout 09:02:37.5959 => Sending: 03 03 60 00 00 02 DB E9 09:02:37.6279 <= Receiving: F3 8F 09:02:37.6279 Timeout 09:02:37.6628 => Sending: 03 03 60 00 00 02 DB E9 09:02:37.6828 <= Receiving: F3 8F 09:02:37.6828 Timeout 09:02:37.7088 => Sending: 01 03 50 02 00 06 75 08 09:02:37.7288 <= Receiving: F3 8F 09:02:37.7288 Timeout 09:02:37.7388 => Sending: 01 03 50 02 00 06 75 08 09:02:37.7708 <= Receiving: 43 73 09:02:37.7708 Timeout 09:02:37.7808 => Sending: 01 03 50 02 00 06 75 08 09:02:37.8508 Timeout 09:02:37.8708 => Sending: 01 03 50 12 00 02 75 0E 09:02:37.8708 <= Receiving: CD 43 73 00 00 09:02:37.8708 <= Receiving: 43 72 99 9A 09:02:37.8708 Wrong telegram: ??? 09:02:37.8808 => Sending: 01 03 50 12 00 02 75 0E 09:02:37.9508 Timeout 09:02:37.9608 => Sending: 01 03 50 12 00 02 75 0E 09:02:37.9808 <= Receiving: 62 23 09:02:37.9808 Timeout 09:02:38.0008 => Sending: 01 03 60 0C 00 02 1A 08 09:02:38.0218 <= Receiving: 62 23 09:02:38.0218 Timeout 09:02:38.0318 => Sending: 01 03 60 0C 00 02 1A 08 09:02:38.0628 <= Receiving: 00 5C 09:02:38.0628 Timeout 09:02:38.0728 => Sending: 01 03 60 0C 00 02 1A 08 09:02:38.0928 <= Receiving: 00 5C 09:02:38.0928 Timeout 09:02:38.1128 => Sending: 01 03 60 18 00 02 5A 0C 09:02:38.1338 <= Receiving: 00 5C 09:02:38.1338 Timeout 09:02:38.1438 => Sending: 01 03 60 18 00 02 5A 0C 09:02:38.1638 <= Receiving: 69 26 09:02:38.1638 Timeout 09:02:38.1738 => Sending: 01 03 60 18 00 02 5A 0C 09:02:38.1938 <= Receiving: 69 26 09:02:38.1938 Timeout 09:02:38.2138 => Sending: 02 03 50 12 00 02 75 3D 09:02:38.2338 <= Receiving: 69 26 09:02:38.2338 Timeout 09:02:38.2438 => Sending: 02 03 50 12 00 02 75 3D 09:02:38.2638 <= Receiving: EA 1D 09:02:38.2638 Timeout 09:02:38.2738 => Sending: 02 03 50 12 00 02 75 3D 09:02:38.2938 <= Receiving: EA 1D 09:02:38.2938 Timeout 09:02:38.3138 => Sending: 02 03 60 00 00 02 DA 38 09:02:38.3338 <= Receiving: EA 1D 09:02:38.3338 Timeout 09:02:38.3438 => Sending: 02 03 60 00 00 02 DA 38 09:02:38.3638 <= Receiving: 6D D5 09:02:38.3638 Timeout 09:02:38.3738 => Sending: 02 03 60 00 00 02 DA 38 09:02:38.4048 <= Receiving: 6D D5 09:02:38.4048 Timeout 09:02:38.4248 => Sending: 03 03 50 12 00 02 74 EC 09:02:38.4448 <= Receiving: 6D D5 09:02:38.4448 Timeout 09:02:38.4548 => Sending: 03 03 50 12 00 02 74 EC 09:02:38.4748 <= Receiving: 68 5B 09:02:38.4748 Timeout 09:02:38.4848 => Sending: 03 03 50 12 00 02 74 EC 09:02:38.5158 <= Receiving: 68 5B 09:02:38.5158 Timeout 09:02:38.5358 => Sending: 03 03 60 00 00 02 DB E9 09:02:38.5558 <= Receiving: 68 5B 09:02:38.5558 Timeout 09:02:38.5658 => Sending: 03 03 60 00 00 02 DB E9 09:02:38.5858 <= Receiving: F3 8F 09:02:38.5858 Timeout 09:02:38.5958 => Sending: 03 03 60 00 00 02 DB E9 09:02:38.6158 <= Receiving: F3 8F 09:02:38.6158 Timeout 09:02:38.6408 => Sending: 01 03 50 02 00 06 75 08 09:02:38.6608 <= Receiving: F3 8F 09:02:38.6608 Timeout 09:02:38.6708 => Sending: 01 03 50 02 00 06 75 08 09:02:38.7028 <= Receiving: CD 09:02:38.7028 Timeout 09:02:38.7128 => Sending: 01 03 50 02 00 06 75 08 09:02:38.7828 Timeout 09:02:38.8028 => Sending: 01 03 50 12 00 02 75 0E 09:02:38.8028 <= Receiving: 43 73 19 9A 43 09:02:38.8028 <= Receiving: 72 B3 33 26 09:02:38.8028 Wrong telegram: ??? 09:02:38.8128 => Sending: 01 03 50 12 00 02 75 0E 09:02:38.8828 Timeout 09:02:38.8928 => Sending: 01 03 50 12 00 02 75 0E Free space in internal port monitor buffer: 59.7 kB 09:02:38.9628 Timeout 09:02:38.9828 => Sending: 01 03 60 0C 00 02 1A 08 09:02:39.0028 <= Receiving: 1B EE 09:02:39.0028 Timeout 09:02:39.0128 => Sending: 01 03 60 0C 00 02 1A 08 09:02:39.0448 <= Receiving: 00 5C 09:02:39.0448 Timeout 09:02:39.0548 => Sending: 01 03 60 0C 00 02 1A 08 09:02:39.0748 <= Receiving: 00 5C 09:02:39.0748 Timeout 09:02:39.0948 => Sending: 01 03 60 18 00 02 5A 0C 09:02:39.1148 <= Receiving: 00 5C 09:02:39.1148 Timeout 09:02:39.1512 => Sending: 01 03 60 18 00 02 5A 0C 09:02:39.1712 <= Receiving: 69 26 09:02:39.1712 Timeout 09:02:39.1812 => Sending: 01 03 60 18 00 02 5A 0C 09:02:39.2012 <= Receiving: 69 26 09:02:39.2012 Timeout 09:02:39.2212 => Sending: 02 03 50 12 00 02 75 3D 09:02:39.2412 <= Receiving: 69 26 09:02:39.2412 Timeout 09:02:39.2512 => Sending: 02 03 50 12 00 02 75 3D 09:02:39.2712 <= Receiving: EA 1D 09:02:39.2712 Timeout 09:02:39.2812 => Sending: 02 03 50 12 00 02 75 3D 09:02:39.3012 <= Receiving: EA 1D 09:02:39.3012 Timeout 09:02:39.3212 => Sending: 02 03 60 00 00 02 DA 38 09:02:39.3422 <= Receiving: EA 1D 09:02:39.3422 Timeout 09:02:39.3522 => Sending: 02 03 60 00 00 02 DA 38 09:02:39.3722 <= Receiving: 9A 6D D5 09:02:39.3722 Timeout 09:02:39.3822 => Sending: 02 03 60 00 00 02 DA 38 09:02:39.4022 <= Receiving: 6D D5 09:02:39.4022 Timeout 09:02:39.4222 => Sending: 03 03 50 12 00 02 74 EC 09:02:39.4422 <= Receiving: 6D D5 09:02:39.4422 Timeout 09:02:39.4522 => Sending: 03 03 50 12 00 02 74 EC 09:02:39.4722 <= Receiving: 68 5B 09:02:39.4722 Timeout 09:02:39.4822 => Sending: 03 03 50 12 00 02 74 EC 09:02:39.5022 <= Receiving: 68 5B 09:02:39.5022 Timeout 09:02:39.5222 => Sending: 03 03 60 00 00 02 DB E9 09:02:39.5422 <= Receiving: 68 5B 09:02:39.5422 Timeout 09:02:39.5522 => Sending: 03 03 60 00 00 02 DB E9 09:02:39.5722 <= Receiving: F3 8F 09:02:39.5722 Timeout 09:02:39.5822 => Sending: 03 03 60 00 00 02 DB E9 09:02:39.6032 <= Receiving: F3 8F 09:02:39.6032 Timeout 09:02:39.6282 => Sending: 01 03 50 02 00 06 75 08 09:02:39.6482 <= Receiving: F3 8F 09:02:39.6482 Timeout 09:02:39.6582 => Sending: 01 03 50 02 00 06 75 08 09:02:39.6892 <= Receiving: CD 09:02:39.6892 Timeout 09:02:39.6992 => Sending: 01 03 50 02 00 06 75 08 09:02:39.7692 Timeout 09:02:39.7892 => Sending: 01 03 50 12 00 02 75 0E 09:02:39.7892 <= Receiving: 43 73 00 00 43 09:02:39.7892 <= Receiving: 72 99 9A A3 09:02:39.7892 Wrong telegram: ??? 09:02:39.7992 => Sending: 01 03 50 12 00 02 75 0E 09:02:39.8692 Timeout 09:02:39.8792 => Sending: 01 03 50 12 00 02 75 0E 09:02:39.9492 Timeout 09:02:39.9692 => Sending: 01 03 60 0C 00 02 1A 08 09:02:39.9892 <= Receiving: 5C 1B EE 09:02:39.9892 Timeout 09:02:39.9992 => Sending: 01 03 60 0C 00 02 1A 08 09:02:40.0292 <= Receiving: 3D 09:02:40.0292 Timeout 09:02:40.0392 => Sending: 01 03 60 0C 00 02 1A 08 09:02:40.1092 Timeout 09:02:40.1292 => Sending: 01 03 60 18 00 02 5A 0C 09:02:40.1492 <= Receiving: 00 5C 09:02:40.1492 Timeout 09:02:40.1592 => Sending: 01 03 60 18 00 02 5A 0C 09:02:40.1792 <= Receiving: 69 26 09:02:40.1792 Timeout 09:02:40.1892 => Sending: 01 03 60 18 00 02 5A 0C 09:02:40.2212 <= Receiving: 69 26 09:02:40.2212 Timeout 09:02:40.2412 => Sending: 02 03 50 12 00 02 75 3D 09:02:40.2612 <= Receiving: 52 69 26 09:02:40.2612 Timeout 09:02:40.2712 => Sending: 02 03 50 12 00 02 75 3D 09:02:40.2912 <= Receiving: DD 3E 09:02:40.2912 Timeout 09:02:40.3012 => Sending: 02 03 50 12 00 02 75 3D 09:02:40.3212 <= Receiving: DD 3E 09:02:40.3212 Timeout 09:02:40.3412 => Sending: 02 03 60 00 00 02 DA 38 09:02:40.3612 <= Receiving: DD 3E 09:02:40.3612 Timeout 09:02:40.3712 => Sending: 02 03 60 00 00 02 DA 38 09:02:40.4032 <= Receiving: 6D D5 09:02:40.4032 Timeout 09:02:40.4132 => Sending: 02 03 60 00 00 02 DA 38 09:02:40.4332 <= Receiving: 6D D5 09:02:40.4332 Timeout 09:02:40.4532 => Sending: 03 03 50 12 00 02 74 EC 09:02:40.4732 <= Receiving: 6D D5 09:02:40.4732 Timeout 09:02:40.4832 => Sending: 03 03 50 12 00 02 74 EC 09:02:40.5032 <= Receiving: 68 5B 09:02:40.5032 Timeout 09:02:40.5132 => Sending: 03 03 50 12 00 02 74 EC 09:02:40.5332 <= Receiving: 68 5B 09:02:40.5332 TimeoutMany thanks in advance for your help and kind regards
@pascal37 said in M525 stopped working:
Did you run this command when you received the Timeout or afer you restarted it?
The command was run while serial communication timeouts, but output is the same after a PLC restart.
This post is deleted! -
@pascal37 Can you try increasing the Max telegram duration a bit higher? For example 300ms? If that won't help. You can also try to increase the pause between telegrams to 5ms.
Hi @tomas_hora,
I have increased Max telegram duration to 300ms + added a 5ms pause between telegrams.
I have also update my M525 to latest Axon runtime (2.3.0.8) with latest firmwares/drivers.
I will let you know if issue occurs again.
Many thanks and kind regards. -
Hi @tomas_hora, issue occured again again with port 1.1 and new settings (Max telegram duration to 300ms + added a 5ms pause between telegrams.)
A simple PLC reboot (from Debian OS) was enough to regain data acquisition from the 3 Inepro PRO380 meters.I do not understand why problem never occured when using port 1.3 of same PLC, nor with my previous M505.
What is the difference between ports 1.1 and 1.3 ?
If same hardware, could it be a hardware issue with port 1.1 on my M525?22:13:08.5230 => Send: 03 03 60 00 00 02 DB E9 22:13:08.5530 <= Recv: CA CB 22:13:08.5530 Timeout 22:13:08.5630 => Send: 03 03 60 00 00 02 DB E9 22:13:08.5930 <= Recv: CA CB 22:13:08.5930 Timeout 22:13:08.6230 => Send: 01 03 50 02 00 06 75 08 22:13:08.6530 <= Recv: CA CB 22:13:08.6530 Timeout 22:13:08.6630 => Send: 01 03 50 02 00 06 75 08 22:13:08.6630 <= Recv: 43 71 CC CD 43 22:13:08.7040 <= Recv: 72 E6 66 22:13:08.7040 Wrong telegram: ??? 22:13:08.7140 => Send: 01 03 50 02 00 06 75 08 22:13:09.0140 Timeout 22:13:09.0390 => Send: 01 03 50 12 00 02 75 0E 22:13:09.0390 <= Recv: 43 71 CC CD 43 22:13:09.0390 <= Recv: 72 E6 66 52 22:13:09.0390 Wrong telegram: ??? 22:13:09.0490 => Send: 01 03 50 12 00 02 75 0E 22:13:09.3490 Timeout 22:13:09.3590 => Send: 01 03 50 12 00 02 75 0E 22:13:09.3890 <= Recv: 4B E3 22:13:09.3890 Timeout 22:13:09.4140 => Send: 01 03 60 0C 00 02 1A 08 22:13:09.4440 <= Recv: EC 4B E3 22:13:09.4440 Timeout 22:13:09.4540 => Send: 01 03 60 0C 00 02 1A 08 22:13:09.4840 <= Recv: CC D8 22:13:09.4840 Timeout 22:13:09.4940 => Send: 01 03 60 0C 00 02 1A 08 22:13:09.5240 <= Recv: CC D8 22:13:09.5240 Timeout 22:13:09.5490 => Send: 01 03 60 18 00 02 5A 0C 22:13:09.5790 <= Recv: CC D8 22:13:09.5790 Timeout 22:13:09.5890 => Send: 01 03 60 18 00 02 5A 0C 22:13:09.6190 <= Recv: 72 00 22:13:09.6190 Timeout 22:13:09.6290 => Send: 01 03 60 18 00 02 5A 0C 22:13:09.6590 <= Recv: 72 00 22:13:09.6590 Timeout 22:13:09.6840 => Send: 02 03 50 12 00 02 75 3D 22:13:09.7140 <= Recv: 72 00 22:13:09.7140 Timeout 22:13:09.7240 => Send: 02 03 50 12 00 02 75 3D 22:13:09.7540 <= Recv: 46 88 22:13:09.7540 Timeout 22:13:09.7640 => Send: 02 03 50 12 00 02 75 3D 22:13:09.7940 <= Recv: 46 88 22:13:09.7940 Timeout 22:13:09.8190 => Send: 02 03 60 00 00 02 DA 38 22:13:09.8490 <= Recv: 46 88 22:13:09.8490 Timeout 22:13:09.8590 => Send: 02 03 60 00 00 02 DA 38 22:13:09.8890 <= Recv: 85 9B 22:13:09.8890 Timeout 22:13:09.8990 => Send: 02 03 60 00 00 02 DA 38 22:13:09.9290 <= Recv: 85 9B 22:13:09.9290 Timeout 22:13:09.9540 => Send: 03 03 50 12 00 02 74 EC 22:13:09.9840 <= Recv: 85 9B 22:13:09.9840 Timeout 22:13:09.9940 => Send: 03 03 50 12 00 02 74 EC 22:13:10.0240 <= Recv: 68 5B 22:13:10.0240 Timeout 22:13:10.0340 => Send: 03 03 50 12 00 02 74 EC 22:13:10.0640 <= Recv: 68 5B 22:13:10.0640 Timeout 22:13:10.0890 => Send: 03 03 60 00 00 02 DB E9 22:13:10.1190 <= Recv: 68 5B 22:13:10.1190 Timeout 22:13:10.1290 => Send: 03 03 60 00 00 02 DB E9 22:13:10.1700 <= Recv: 04 22:13:10.1700 Timeout 22:13:10.1800 => Send: 03 03 60 00 00 02 DB E9 22:13:10.4800 Timeout 22:13:10.5100 => Send: 01 03 50 02 00 06 75 08 22:13:10.5623 <= Recv: CA CB 22:13:10.5623 Timeout 22:13:10.5723 => Send: 01 03 50 02 00 06 75 08 22:13:10.5723 <= Recv: 43 71 CC CD 43 22:13:10.6133 <= Recv: 72 E6 66 52 22:13:10.6133 Wrong telegram: ??? 22:13:10.6233 => Send: 01 03 50 02 00 06 75 08 22:13:10.9233 Timeout 22:13:10.9483 => Send: 01 03 50 12 00 02 75 0E 22:13:10.9483 <= Recv: 43 71 CC CD 43 22:13:10.9483 <= Recv: 72 E6 66 52 22:13:10.9483 Wrong telegram: ??? 22:13:10.9583 => Send: 01 03 50 12 00 02 75 0E 22:13:11.2583 Timeout 22:13:11.2683 => Send: 01 03 50 12 00 02 75 0E 22:13:11.2993 <= Recv: 4B E3 22:13:11.2993 Timeout 22:13:11.3243 => Send: 01 03 60 0C 00 02 1A 08 22:13:11.3543 <= Recv: 4B E3 22:13:11.3543 Timeout 22:13:11.3643 => Send: 01 03 60 0C 00 02 1A 08 22:13:11.3943 <= Recv: CC D8 22:13:11.3943 Timeout 22:13:11.4043 => Send: 01 03 60 0C 00 02 1A 08 22:13:11.4343 <= Recv: CC D8 22:13:11.4343 Timeout 22:13:11.4593 => Send: 01 03 60 18 00 02 5A 0C 22:13:11.4893 <= Recv: CC D8 22:13:11.4893 Timeout 22:13:11.4993 => Send: 01 03 60 18 00 02 5A 0C 22:13:11.5293 <= Recv: 72 00 22:13:11.5293 Timeout 22:13:11.5393 => Send: 01 03 60 18 00 02 5A 0C 22:13:11.5693 <= Recv: E1 72 00 22:13:11.5693 Timeout 22:13:11.5943 => Send: 02 03 50 12 00 02 75 3D 22:13:11.6243 <= Recv: 72 00 22:13:11.6243 Timeout 22:13:11.6343 => Send: 02 03 50 12 00 02 75 3D 22:13:11.6643 <= Recv: 46 88 22:13:11.6643 Timeout 22:13:11.6743 => Send: 02 03 50 12 00 02 75 3D 22:13:11.7043 <= Recv: 46 88 22:13:11.7043 Timeout 22:13:11.7293 => Send: 02 03 60 00 00 02 DA 38 22:13:11.7593 <= Recv: 46 88 22:13:11.7593 Timeout 22:13:11.7693 => Send: 02 03 60 00 00 02 DA 38 22:13:11.7993 <= Recv: 85 9B 22:13:11.7993 Timeout 22:13:11.8093 => Send: 02 03 60 00 00 02 DA 38 22:13:11.8393 <= Recv: 85 9B 22:13:11.8393 Timeout 22:13:11.8643 => Send: 03 03 50 12 00 02 74 EC 22:13:11.8943 <= Recv: 85 9B 22:13:11.8943 Timeout 22:13:11.9043 => Send: 03 03 50 12 00 02 74 EC 22:13:11.9343 <= Recv: 68 5B 22:13:11.9343 Timeout 22:13:11.9443 => Send: 03 03 50 12 00 02 74 EC 22:13:11.9743 <= Recv: 68 5B 22:13:11.9743 Timeout 22:13:11.9993 => Send: 03 03 60 00 00 02 DB E9 22:13:12.0293 <= Recv: 68 5B 22:13:12.0293 Timeout 22:13:12.0393 => Send: 03 03 60 00 00 02 DB E9 22:13:12.0693 <= Recv: CA CB 22:13:12.0693 Timeout 22:13:12.0793 => Send: 03 03 60 00 00 02 DB E9 22:13:12.1093 <= Recv: CA CB 22:13:12.1093 Timeout 22:13:12.1393 => Send: 01 03 50 02 00 06 75 08 22:13:12.1693 <= Recv: CA CB 22:13:12.1693 Timeout 22:13:12.1793 => Send: 01 03 50 02 00 06 75 08 22:13:12.1793 <= Recv: 43 71 B3 33 43 22:13:12.2193 <= Recv: 72 E6 66 70 22:13:12.2193 Wrong telegram: ??? 22:13:12.2293 => Send: 01 03 50 02 00 06 75 08 22:13:12.5293 Timeout 22:13:12.5543 => Send: 01 03 50 12 00 02 75 0E 22:13:12.5543 <= Recv: 43 71 B3 33 43 22:13:12.5543 <= Recv: 72 E6 66 70 22:13:12.5543 Wrong telegram: ??? 22:13:12.5643 => Send: 01 03 50 12 00 02 75 0E 22:13:12.8643 Timeout 22:13:12.8743 => Send: 01 03 50 12 00 02 75 0E 22:13:12.9043 <= Recv: 4B E3 22:13:12.9043 Timeout 22:13:12.9293 => Send: 01 03 60 0C 00 02 1A 08 22:13:12.9593 <= Recv: 4B E3 22:13:12.9593 Timeout 22:13:12.9693 => Send: 01 03 60 0C 00 02 1A 08 22:13:12.9993 <= Recv: CC D8 22:13:12.9993 Timeout 22:13:13.0093 => Send: 01 03 60 0C 00 02 1A 08 22:13:13.0393 <= Recv: CC D8 22:13:13.0393 Timeout 22:13:13.0643 => Send: 01 03 60 18 00 02 5A 0C 22:13:13.0943 <= Recv: CC D8 22:13:13.0943 Timeout 22:13:13.1043 => Send: 01 03 60 18 00 02 5A 0C 22:13:13.1557 <= Recv: 72 00 22:13:13.1557 Timeout 22:13:13.1657 => Send: 01 03 60 18 00 02 5A 0C 22:13:13.1957 <= Recv: 72 00 22:13:13.1957 Timeout 22:13:13.2207 => Send: 02 03 50 12 00 02 75 3D 22:13:13.2507 <= Recv: 72 00 22:13:13.2507 Timeout 22:13:13.2607 => Send: 02 03 50 12 00 02 75 3D 22:13:13.2907 <= Recv: 46 88 22:13:13.2907 Timeout 22:13:13.3007 => Send: 02 03 50 12 00 02 75 3D 22:13:13.3307 <= Recv: 46 88 22:13:13.3307 Timeout 22:13:13.3557 => Send: 02 03 60 00 00 02 DA 38 22:13:13.3857 <= Recv: 46 88 22:13:13.3857 Timeout 22:13:13.3957 => Send: 02 03 60 00 00 02 DA 38 22:13:13.4257 <= Recv: 85 9B 22:13:13.4257 Timeout 22:13:13.4357 => Send: 02 03 60 00 00 02 DA 38 22:13:13.4657 <= Recv: 85 9B 22:13:13.4657 Timeout 22:13:13.4907 => Send: 03 03 50 12 00 02 74 EC 22:13:13.5207 <= Recv: 85 9B 22:13:13.5207 Timeout 22:13:13.5307 => Send: 03 03 50 12 00 02 74 EC 22:13:13.5607 <= Recv: 68 5B 22:13:13.5607 Timeout 22:13:13.5707 => Send: 03 03 50 12 00 02 74 EC 22:13:13.6007 <= Recv: 68 5B 22:13:13.6007 Timeout 22:13:13.6257 => Send: 03 03 60 00 00 02 DB E9 22:13:13.6557 <= Recv: 68 5B 22:13:13.6557 Timeout 22:13:13.6657 => Send: 03 03 60 00 00 02 DB E9 22:13:13.6957 <= Recv: CA CB 22:13:13.6957 Timeout 22:13:13.7057 => Send: 03 03 60 00 00 02 DB E9 22:13:13.7357 <= Recv: 0A CA CB 22:13:13.7357 Timeout 22:13:13.7657 => Send: 01 03 50 02 00 06 75 08 22:13:13.7957 <= Recv: CA CB 22:13:13.7957 Timeout 22:13:13.8057 => Send: 01 03 50 02 00 06 75 08 22:13:13.8057 <= Recv: 43 71 CC CD 43 22:13:13.8447 <= Recv: 72 CC CD BF 07 22:13:13.8447 Wrong telegram: ??? 22:13:13.8547 => Send: 01 03 50 02 00 06 75 08 22:13:13.8547 <= Recv: 43 71 CC CD 43 22:13:13.8847 <= Recv: 72 CC CD BF 07 22:13:13.8847 Wrong telegram: ??? 22:13:13.9097 => Send: 01 03 50 12 00 02 75 0E 22:13:13.9097 <= Recv: 43 71 CC CD 43 22:13:13.9097 <= Recv: 72 CC CD BF 22:13:13.9097 Wrong telegram: ??? 22:13:13.9197 => Send: 01 03 50 12 00 02 75 0E 22:13:14.2197 Timeout 22:13:14.2297 => Send: 01 03 50 12 00 02 75 0E 22:13:14.2597 <= Recv: 4B E3 22:13:14.2597 Timeout 22:13:14.2847 => Send: 01 03 60 0C 00 02 1A 08 22:13:14.3147 <= Recv: 4B E3 22:13:14.3147 Timeout 22:13:14.3247 => Send: 01 03 60 0C 00 02 1A 08 22:13:14.3547 <= Recv: CC D8 22:13:14.3547 Timeout 22:13:14.3647 => Send: 01 03 60 0C 00 02 1A 08 22:13:14.3947 <= Recv: CC D8 22:13:14.3947 Timeout 22:13:14.4197 => Send: 01 03 60 18 00 02 5A 0C 22:13:14.4497 <= Recv: CC D8 22:13:14.4497 Timeout 22:13:14.4597 => Send: 01 03 60 18 00 02 5A 0C 22:13:14.4897 <= Recv: 72 00 22:13:14.4897 Timeout 22:13:14.4997 => Send: 01 03 60 18 00 02 5A 0C 22:13:14.5297 <= Recv: 72 00 22:13:14.5297 Timeout 22:13:14.5547 => Send: 02 03 50 12 00 02 75 3D 22:13:14.5847 <= Recv: 72 00 22:13:14.5847 Timeout 22:13:14.5947 => Send: 02 03 50 12 00 02 75 3D 22:13:14.6247 <= Recv: 46 88 22:13:14.6247 Timeout 22:13:14.6347 => Send: 02 03 50 12 00 02 75 3D 22:13:14.6647 <= Recv: 46 88 22:13:14.6647 Timeout 22:13:14.6897 => Send: 02 03 60 00 00 02 DA 38 22:13:14.7197 <= Recv: 46 88 22:13:14.7197 Timeout 22:13:14.7297 => Send: 02 03 60 00 00 02 DA 38 22:13:14.7597 <= Recv: 85 9B 22:13:14.7597 Timeout 22:13:14.7697 => Send: 02 03 60 00 00 02 DA 38 22:13:14.7997 <= Recv: 85 9B 22:13:14.7997 Timeout 22:13:14.8247 => Send: 03 03 50 12 00 02 74 EC 22:13:14.8547 <= Recv: 85 9B 22:13:14.8547 Timeout 22:13:14.8647 => Send: 03 03 50 12 00 02 74 EC 22:13:14.8947 <= Recv: 68 5B 22:13:14.9166 Timeout 22:13:14.9266 => Send: 03 03 50 12 00 02 74 EC 22:13:14.9566 <= Recv: 68 5B 22:13:14.9566 Timeout 22:13:14.9816 => Send: 03 03 60 00 00 02 DB E9 22:13:15.0116 <= Recv: 68 5B 22:13:15.0116 Timeout 22:13:15.0216 => Send: 03 03 60 00 00 02 DB E9 22:13:15.0516 <= Recv: CA CB 22:13:15.0516 Timeout 22:13:15.0616 => Send: 03 03 60 00 00 02 DB E9 22:13:15.0916 <= Recv: CA CB 22:13:15.0916 Timeout 22:13:15.1216 => Send: 01 03 50 02 00 06 75 08 22:13:15.1516 <= Recv: CA CB 22:13:15.1516 Timeout 22:13:15.1616 => Send: 01 03 50 02 00 06 75 08 22:13:15.1616 <= Recv: 43 71 B3 33 43 22:13:15.2016 <= Recv: 72 E6 66 C3 C3 22:13:15.2016 Wrong telegram: ??? 22:13:15.2116 => Send: 01 03 50 02 00 06 75 08 22:13:15.2116 <= Recv: 43 71 B3 33 43 22:13:15.2416 <= Recv: 72 E6 66 C3 C3 22:13:15.2416 Wrong telegram: ??? 22:13:15.2666 => Send: 01 03 50 12 00 02 75 0E 22:13:15.2666 <= Recv: 43 71 B3 33 43 22:13:15.2666 <= Recv: 72 E6 66 C3 22:13:15.2666 Wrong telegram: ??? 22:13:15.2766 => Send: 01 03 50 12 00 02 75 0E 22:13:15.5766 Timeout 22:13:15.5866 => Send: 01 03 50 12 00 02 75 0E 22:13:15.6166 <= Recv: 4B E3 22:13:15.6166 Timeout 22:13:15.6416 => Send: 01 03 60 0C 00 02 1A 08 22:13:15.6716 <= Recv: 4B E3 22:13:15.6716 Timeout 22:13:15.6816 => Send: 01 03 60 0C 00 02 1A 08 22:13:15.7116 <= Recv: CC D8 22:13:15.7116 Timeout 22:13:15.7216 => Send: 01 03 60 0C 00 02 1A 08 22:13:15.7516 <= Recv: CC D8 22:13:15.7516 Timeout 22:13:15.7766 => Send: 01 03 60 18 00 02 5A 0C 22:13:15.8066 <= Recv: CC D8 22:13:15.8066 Timeout 22:13:15.8166 => Send: 01 03 60 18 00 02 5A 0C 22:13:15.8466 <= Recv: 72 00 22:13:15.8466 Timeout 22:13:15.8566 => Send: 01 03 60 18 00 02 5A 0C 22:13:15.8866 <= Recv: 72 00 22:13:15.8866 Timeout 22:13:15.9116 => Send: 02 03 50 12 00 02 75 3D 22:13:15.9416 <= Recv: 72 00 22:13:15.9416 Timeout 22:13:15.9516 => Send: 02 03 50 12 00 02 75 3D 22:13:15.9926 <= Recv: 04 22:13:15.9926 Timeout 22:13:16.0026 => Send: 02 03 50 12 00 02 75 3D 22:13:16.3026 Timeout 22:13:16.3276 => Send: 02 03 60 00 00 02 DA 38 22:13:16.3576 <= Recv: 46 88 22:13:16.3576 Timeout 22:13:16.3676 => Send: 02 03 60 00 00 02 DA 38 22:13:16.3976 <= Recv: 85 9B 22:13:16.3976 Timeout 22:13:16.4076 => Send: 02 03 60 00 00 02 DA 38 22:13:16.4376 <= Recv: 85 9B 22:13:16.4376 Timeout 22:13:16.4626 => Send: 03 03 50 12 00 02 74 EC 22:13:16.4926 <= Recv: 85 9B 22:13:16.4926 Timeout 22:13:16.5026 => Send: 03 03 50 12 00 02 74 EC 22:13:16.5326 <= Recv: 68 5B 22:13:16.5326 Timeout 22:13:16.5426 => Send: 03 03 50 12 00 02 74 EC 22:13:16.5726 <= Recv: 68 5B 22:13:16.5726 Timeout 22:13:16.5976 => Send: 03 03 60 00 00 02 DB E9 22:13:16.6276 <= Recv: 68 5B 22:13:16.6276 Timeout 22:13:16.6376 => Send: 03 03 60 00 00 02 DB E9 22:13:16.6676 <= Recv: CA CB 22:13:16.6676 Timeout 22:13:16.6776 => Send: 03 03 60 00 00 02 DB E9 22:13:16.7076 <= Recv: CA CB 22:13:16.7076 Timeout 22:13:16.7376 => Send: 01 03 50 02 00 06 75 08 22:13:16.7686 <= Recv: CA CB 22:13:16.7686 Timeout -
Hello @pascal37,
thank you for the information sent. Unfortunately, based on it, we are not able to determine the exact source of the issue.
Can you please check the following:- Again, make sure you have the latest firmware in the I/O board flashed. Type:
/opt/unipi/tools/fwspi -i 0-
Can you confirm that the i2c-0 error in the dmesg log appears always in the moment of communication goes wrong? It seems there is a correlation (863475 seconds is almost exactly 10 days).
Are you sure that no other running processes access the interface (/dev/ttyNS0)? Please check also your time-scheduled tasks (e.g. executed from cron).
Are you sure that no noise or interference from the environment or power supply can infiltrate the unit?
As the last resort, we are able to simulate your application with the same HW, but it will be pretty time-consuming. In the meantime, please use another RS485 interface.
Hi @martin_triska,
- I did a reflash (USB method) of my M525 with latest Mervis OS image (2.3.0.10), firmwares are already up-to-date:
unipi@M525-sn8:~$ sudo /opt/unipi/tools/fwspi -i 0 Boardset: 0 B-1000 (v1.0) Baseboard: 0 B-1000 (v2.0) Firmware: v5.50 unipi@M525-sn8:~$ sudo /opt/unipi/tools/fwspi -i 1 Boardset: 19 E-4Ai4Ao_U-R485Di4Ro5 (v1.0) Baseboard: 11 E-4Ai4Ao (v1.0) Firmware: v5.50-
From what I've seen after serial communications "crashes", I did not see anymore an i2c-0 error in demsg, so I am not sure this is correlated.
Yes: it is a standard Mervis OS image + 2 pythons scripts running as daemons with pymodbus client over ModbusTCP, so no serial communications there.
Yes: I am using shielded cable specific for RS485, the bus is properly terminated at each end. Cable shield is properly grounded at PLC side and also to PLC itself. Environment is stable and, so long the issue is not occurring, communication is working perfectly.
With the increase of Max telegram duration to 300ms, there is absolutely no error during multiple days:
It seems most likely a driver or Mervis runtime issue related to M525 model and port 1.1 !?
As I said, I never had the issue when using port 1.3 instead of port 1.1
I have also another RS485 bus on port 2.1 and no issue either.
This issue also never occurred with port 1.1 on my previous M505 PLCIf you want to try reproduce the issue, you need 3 Inepro PRO380 meters and read constantly multiple values from them like power, energy, voltage.
In my case, the maximum uptime before a crash is about 10 days.I can use port 1.3 in the meantime, but I will need the 3rd RS485 port later for my project...
But let's check again if it is really stable with port 1.3 over >10 days !Many thanks in advance and kind regards
Hi @martin_triska,
I confirm the solution is stable over >50 days when using port 1.3 :
... but not with port 1.1, where serial communications crashes < 10 days !
If you did not find a software issue related to port RS485-1.1 on Axon M525, there should be a hardware issue with my PLC !I have bought this PLC because I need 3 RS485 ports, so using port 1.3 over 1.1 is not a solution...
Can you please replace this unit ?
Many thanks in advance and kind regards,Pascal
Hello @pascal37,
thank you for the feedback. So, let us sum it up:
- On ports other than 1.1, you've never seen the issue yet (tested over 50 days without reboot).
- On port 1.1, the issue appears always in a few (approx. 10) days.
- There is no correlation with any item in the system log (dmesg) recorded in the moment of failure.
- Flash to the latest version 5.50 has not solved it.
- An older PLC M505 does not have this problem (is the FW and image versions in it also the latest?)
If so, you are right - it seems to the issue is hardware-based and the unit has to be replaced.