    • Martin KudláčekM
      Martin Kudláček @Vesa Kauppinen
      last edited by Martin Kudláček

      Oh, sorry for the misunderstanding @vesa-kauppinen.

      We have a functionality called Master Watch Dog (MWD). When enabled, the underlying HW will watch when the last communication happend. If it will be longer than the preset time, it will reboot itself. Now, this can be set per group in the PLC, and it will watch if the ModbusTCP server communicates with the given group. If not, the board will reboot. Similarly, this can be set on the extensions as well. If nothing communicates with the extension over ModbusRTU, the extension reboots itself.

      This can be set via modbus. Look for the "Enable MWD" coil and "MWD timeout" register. The timeout is in miliseconds.

      Best regards,
      Martin

      Vesa KauppinenV 1 Reply Last reply
      Reply Quote 0
      • Vesa KauppinenV
        Vesa Kauppinen @Martin Kudláček
        last edited by

        @martin-kudláček

        Thank you!

        Can you give a noob example of how to set 'MWD Enable' to 1 with pollmb.py?

        Br,
        Vesa

        Martin KudláčekM 1 Reply Last reply
        Reply Quote 0
        • Martin KudláčekM
          Martin Kudláček @Vesa Kauppinen
          last edited by

          @vesa-kauppinen

          Sorry, I've never used the pollmb.py. Would be the mbpoll example sufficient? You can install the mbpoll from our repository: apt update && apt install mbpoll

          Martin

          Vesa KauppinenV 1 Reply Last reply
          Reply Quote 0
          • Vesa KauppinenV
            Vesa Kauppinen @Martin Kudláček
            last edited by

            @martin-kudláček

            Yes. If you can give mbpoll example that would be great!

            :)

            Br,
            Vesa

            Martin KudláčekM 1 Reply Last reply
            Reply Quote 0
            • Martin KudláčekM
              Martin Kudláček @Vesa Kauppinen
              last edited by

              @vesa-kauppinen

              For Group 1 on M503

              Verify the status of the MWD (if 0 - MWD disable, if 1 - MWD enabled but never rebooted, if 2 - MWD enabled and already rebooted):
              mbpoll -m tcp -a 0 127.0.0.1 -0 -1 -r 6

              Set the MWD timeout to 5000ms:
              mbpoll -m tcp -a 0 127.0.0.1 -0 -r 1008 5000

              Enable the MWD:
              mbpoll -m tcp -a 0 127.0.0.1 -0 -r 6 1

              Write the settings to the NVRAM:
              mbpoll -m tcp -a 0 127.0.0.1 -0 -t 0 -r 1003 1

              Verify the MWD by stopping the UniPi Modbus TCP server:
              sudo systemctl stop unipitcp

              The both lines of LEDs should blink for 1sec after the MWD timeout

              Disable the MWD:
              mbpoll -m tcp -a 0 127.0.0.1 -0 -r 6 0

              Write the settings to the NVRAM:
              mbpoll -m tcp -a 0 127.0.0.1 -0 -t 0 -r 1003 1

              For Group 2 on M503
              Use the MWD control register 114 instead of 6
              Use the MWD timeout register 1108 instead of 1008
              Use the Save configuration coil 1103 instead of 1003

              Vesa KauppinenV 1 Reply Last reply
              Reply Quote 0
              • Vesa KauppinenV
                Vesa Kauppinen @Martin Kudláček
                last edited by

                @martin-kudláček

                Thanks for the good instructions! After enabling MWD, setting timeout and writing the settings:

                mbpoll -m tcp -a 0 127.0.0.1 -0 -1 -r 6
                mbpoll 1.2-6 - FieldTalk(tm) Modbus(R) Master Simulator
                Copyright (c) 2015 epsilonRT, All rights reserved.
                This software is governed by the CeCILL license <http://www.cecill.info>
                
                Protocol configuration: Modbus TCP
                Slave configuration...: address = [0]
                                        start reference = 6, count = 1
                Communication.........: 127.0.0.1, port 502, t/o 1.00 s, poll rate 1000 ms
                Data type.............: 16-bit register, output (holding) register table
                
                -- Polling slave 0...
                [6]:    3
                

                ...or...

                mbpoll -m tcp -a 0 127.0.0.1 -0 -1 -r 114
                mbpoll 1.2-6 - FieldTalk(tm) Modbus(R) Master Simulator
                Copyright (c) 2015 epsilonRT, All rights reserved.
                This software is governed by the CeCILL license <http://www.cecill.info>
                
                Protocol configuration: Modbus TCP
                Slave configuration...: address = [0]
                                        start reference = 114, count = 1
                Communication.........: 127.0.0.1, port 502, t/o 1.00 s, poll rate 1000 ms
                Data type.............: 16-bit register, output (holding) register table
                
                -- Polling slave 0...
                [114]:  3
                

                What does that result (3) mean? Its not 0, 1 or 2.

                Btw

                sudo systemctl stop unipitcp
                

                should be

                sudo systemctl stop neurontcp
                

                in Neuron M503...right??

                Br,
                Vesa

                Martin KudláčekM 1 Reply Last reply
                Reply Quote 0
                • Martin KudláčekM
                  Martin Kudláček @Vesa Kauppinen
                  last edited by Martin Kudláček

                  Hi @vesa-kauppinen,
                  sorry the value 3 is 1 + 2, which means board has MWD enabled and the MWD already rebooted the board.

                  The service is called unipitcp, but in older packages it was called neurontcp. The service is the same for Neurons and Axons, so we renamed it to unipitcp to make it more clear.

                  Best regards,
                  Martin

                  Vesa KauppinenV 1 Reply Last reply
                  Reply Quote 0
                  • Vesa KauppinenV
                    Vesa Kauppinen @Martin Kudláček
                    last edited by Vesa Kauppinen

                    @martin-kudláček

                    Aaaaa...of course :D

                    But what about this: either 11 or 3

                    root@residevice:~# mbpoll -m tcp -a 0 127.0.0.1 -0 -1 -r 6
                    mbpoll 1.2-6 - FieldTalk(tm) Modbus(R) Master Simulator
                    Copyright (c) 2015 epsilonRT, All rights reserved.
                    This software is governed by the CeCILL license <http://www.cecill.info>
                    
                    Protocol configuration: Modbus TCP
                    Slave configuration...: address = [0]
                                            start reference = 6, count = 1
                    Communication.........: 127.0.0.1, port 502, t/o 1.00 s, poll rate 1000 ms
                    Data type.............: 16-bit register, output (holding) register table
                    
                    -- Polling slave 0...
                    [6]:    11
                    
                    root@residevice:~# mbpoll -m tcp -a 0 127.0.0.1 -0 -1 -r 6
                    mbpoll 1.2-6 - FieldTalk(tm) Modbus(R) Master Simulator
                    Copyright (c) 2015 epsilonRT, All rights reserved.
                    This software is governed by the CeCILL license <http://www.cecill.info>
                    
                    Protocol configuration: Modbus TCP
                    Slave configuration...: address = [0]
                                            start reference = 6, count = 1
                    Communication.........: 127.0.0.1, port 502, t/o 1.00 s, poll rate 1000 ms
                    Data type.............: 16-bit register, output (holding) register table
                    
                    -- Polling slave 0...
                    [6]:    3
                    
                    root@residevice:~# mbpoll -m tcp -a 0 127.0.0.1 -0 -1 -r 6
                    mbpoll 1.2-6 - FieldTalk(tm) Modbus(R) Master Simulator
                    Copyright (c) 2015 epsilonRT, All rights reserved.
                    This software is governed by the CeCILL license <http://www.cecill.info>
                    
                    Protocol configuration: Modbus TCP
                    Slave configuration...: address = [0]
                                            start reference = 6, count = 1
                    Communication.........: 127.0.0.1, port 502, t/o 1.00 s, poll rate 1000 ms
                    Data type.............: 16-bit register, output (holding) register table
                    
                    -- Polling slave 0...
                    [6]:    11
                    

                    Br,
                    Vesa

                    Martin KudláčekM 1 Reply Last reply
                    Reply Quote 0
                    • Martin KudláčekM
                      Martin Kudláček @Vesa Kauppinen
                      last edited by

                      @vesa-kauppinen

                      Ok, this is a little bit tricky. The register has 16bits, and some of the bits represent some state or function.

                      Bit 0: Set or read the status of the MWD
                      Bit 1: The MWD rebooted the boarde
                      other bits contain some debug information, which we haven't documented yet

                      So value 11 in decimal is 0000 0000 0000 1011 in binary. The bit no. 0 (first from the right) is 1, which means MWD is enabled. The bit no. 1 (second from the right) is 1, which means MWD already rebooted the board. Other bits don't apply to you.

                      You can "mask" the lowest 2 bits with boolean operation AND, typically with bit mask in hexadecimal representation:

                      register_6 && 0x0003

                      Or with binary mask:

                      register_6 && 0b11

                      I hope this helps you.
                      Martin

                      Vesa KauppinenV 2 Replies Last reply
                      Reply Quote 0
                      • Vesa KauppinenV
                        Vesa Kauppinen @Martin Kudláček
                        last edited by

                        @martin-kudláček

                        Okay. This clarified the case :)

                        Thank you!

                        Br,
                        Vesa

                        1 Reply Last reply
                        Reply Quote 0
                        • Vesa KauppinenV
                          Vesa Kauppinen @Martin Kudláček
                          last edited by Vesa Kauppinen

                          @martin-kudláček

                          Hi...again

                          One more stupid question: How do I reset 1-wire bus with mbpoll?

                          I mean, how can i "convert" those commands:

                          ./pollmb.py -p 502 -u 1 -f 5 -a 1001 -q 1 -d 1
                          ./pollmb.py -p 502 -u 1 -f 5 -a 1001 -q 1 -d 0
                          

                          to mbpoll "format". I just don't understand how to read/write coils with mbpoll.

                          Thank you!
                          Vesa

                          Martin KudláčekM 1 Reply Last reply
                          Reply Quote 0
                          • Martin KudláčekM
                            Martin Kudláček @Vesa Kauppinen
                            last edited by

                            Hi @vesa-kauppinen,
                            writing 1 to coil 1001:

                            mbpoll -m tcp -a 0 127.0.0.1 -t 0 -0 -r 1001 1

                            Writing 0:

                            mbpoll -m tcp -a 0 127.0.0.1 -t 0 -0 -r 1001 0

                            You can learn more from the quite detailed help of the mbpoll:

                            mbpoll -h

                            Regards,
                            Martin

                            1 Reply Last reply
                            Reply Quote 0

                            Hello! It looks like you're interested in this conversation, but you don't have an account yet.

                            Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.