    How to disable and enable the 1Wire bus (M503)
    23 Posts 4 Posters 15.2k Views 1 Watching
      Martin Kudláček @Vesa Kauppinen
      Hello @vesa-kauppinen,
      yes, check our Modbus Registers Maps: https://kb.unipi.technology/files:products:02-neuron
      For M503 it is coil 1001 - Enable/Disable 1Wire Bus
      Vesa KauppinenV 1 Reply Last reply
      • Vesa KauppinenV
        Vesa Kauppinen @Martin Kudláček
        @martin-kudláček
        That's what we've done with 1-Wire and it works.
        I mean, is it possible to do this same 'reset' for Modbus (RTU) itself? We sometimes lose a modbus device.
        Br,
        Vesa
          Oh, sorry for the misunderstanding @vesa-kauppinen.
          We have a functionality called Master Watch Dog (MWD). When enabled, the underlying HW will watch when the last communication happend. If it will be longer than the preset time, it will reboot itself. Now, this can be set per group in the PLC, and it will watch if the ModbusTCP server communicates with the given group. If not, the board will reboot. Similarly, this can be set on the extensions as well. If nothing communicates with the extension over ModbusRTU, the extension reboots itself.
          This can be set via modbus. Look for the "Enable MWD" coil and "MWD timeout" register. The timeout is in miliseconds.
          • Vesa KauppinenV
            @martin-kudláček
            Thank you!
            Can you give a noob example of how to set 'MWD Enable' to 1 with pollmb.py?
            Br,
            Vesa
              @vesa-kauppinen
              Sorry, I've never used the pollmb.py. Would be the mbpoll example sufficient? You can install the mbpoll from our repository: apt update && apt install mbpoll
              • Vesa KauppinenV
                @martin-kudláček
                Yes. If you can give mbpoll example that would be great!
                Br,
                Vesa
                  @vesa-kauppinen
                  For Group 1 on M503
                  Verify the status of the MWD (if 0 - MWD disable, if 1 - MWD enabled but never rebooted, if 2 - MWD enabled and already rebooted):
                  mbpoll -m tcp -a 0 127.0.0.1 -0 -1 -r 6
                  Set the MWD timeout to 5000ms:
                  mbpoll -m tcp -a 0 127.0.0.1 -0 -r 1008 5000
                  Enable the MWD:
                  mbpoll -m tcp -a 0 127.0.0.1 -0 -r 6 1
                  Write the settings to the NVRAM:
                  mbpoll -m tcp -a 0 127.0.0.1 -0 -t 0 -r 1003 1
                  Verify the MWD by stopping the UniPi Modbus TCP server:
                  sudo systemctl stop unipitcp
                  The both lines of LEDs should blink for 1sec after the MWD timeout
                  Disable the MWD:
                  mbpoll -m tcp -a 0 127.0.0.1 -0 -r 6 0
                  For Group 2 on M503
                  Use the MWD control register 114 instead of 6
                  Use the MWD timeout register 1108 instead of 1008
                  Use the Save configuration coil 1103 instead of 1003
                  • Vesa KauppinenV
                    @martin-kudláček
                    Thanks for the good instructions! After enabling MWD, setting timeout and writing the settings:
                    mbpoll 1.2-6 - FieldTalk(tm) Modbus(R) Master Simulator
                    Copyright (c) 2015 epsilonRT, All rights reserved.
                    This software is governed by the CeCILL license <http://www.cecill.info>
                    Protocol configuration: Modbus TCP
                    Slave configuration...: address = [0]
                                            start reference = 6, count = 1
                    Communication.........: 127.0.0.1, port 502, t/o 1.00 s, poll rate 1000 ms
                    Data type.............: 16-bit register, output (holding) register table
                    -- Polling slave 0...
                    [6]:    3
                    ...or...
                    mbpoll -m tcp -a 0 127.0.0.1 -0 -1 -r 114
                                            start reference = 114, count = 1
                    [114]:  3
                    What does that result (3) mean? Its not 0, 1 or 2.
                    Btw
                    should be
                    sudo systemctl stop neurontcp
                    in Neuron M503...right??
                    Br,
                    Vesa
                      Hi @vesa-kauppinen,
                      sorry the value 3 is 1 + 2, which means board has MWD enabled and the MWD already rebooted the board.
                      The service is called unipitcp, but in older packages it was called neurontcp. The service is the same for Neurons and Axons, so we renamed it to unipitcp to make it more clear.
                      • Vesa KauppinenV
                        @martin-kudláček
                        Aaaaa...of course :D
                        But what about this: either 11 or 3
                        root@residevice:~# mbpoll -m tcp -a 0 127.0.0.1 -0 -1 -r 6
                        [6]:    11
                        [6]:    3
                        [6]:    11
                        Br,
                        Vesa
                          @vesa-kauppinen
                          Ok, this is a little bit tricky. The register has 16bits, and some of the bits represent some state or function.
                          Bit 0: Set or read the status of the MWD
                          Bit 1: The MWD rebooted the boarde
                          other bits contain some debug information, which we haven't documented yet
                          So value 11 in decimal is 0000 0000 0000 1011 in binary. The bit no. 0 (first from the right) is 1, which means MWD is enabled. The bit no. 1 (second from the right) is 1, which means MWD already rebooted the board. Other bits don't apply to you.
                          You can "mask" the lowest 2 bits with boolean operation AND, typically with bit mask in hexadecimal representation:
                          register_6 && 0x0003
                          Or with binary mask:
                          register_6 && 0b11
                          I hope this helps you.
                          Vesa KauppinenV 2 Replies Last reply
                          • Vesa KauppinenV
                            @martin-kudláček
                            Okay. This clarified the case :)
                            Thank you!
                            Br,
                            Vesa
                            • Vesa KauppinenV
                              @martin-kudláček
                              Hi...again
                              One more stupid question: How do I reset 1-wire bus with mbpoll?
                              I mean, how can i "convert" those commands:
                              ./pollmb.py -p 502 -u 1 -f 5 -a 1001 -q 1 -d 1
                              ./pollmb.py -p 502 -u 1 -f 5 -a 1001 -q 1 -d 0
                              to mbpoll "format". I just don't understand how to read/write coils with mbpoll.
                              Thank you!
                              Vesa
                                Hi @vesa-kauppinen,
                                writing 1 to coil 1001:
                                mbpoll -m tcp -a 0 127.0.0.1 -t 0 -0 -r 1001 1
                                Writing 0:
                                mbpoll -m tcp -a 0 127.0.0.1 -t 0 -0 -r 1001 0
                                You can learn more from the quite detailed help of the mbpoll:
                                mbpoll -h