    Anlogue Output Voltage
    • K
      knebb last edited by
      finally I was able to set (and read) the analogue output (AO1) on my Neuron M103 device through C with modbus_read_registers().
      So I am using as documented regsiter 3000-3001 as floating point variable.
      Works fine so far- I can set and verify the value by reading.
      Now when attaching a voltmeter to measure the real physical AO voltage I am getting some strange numbers.
      Here is a little table from what I observed:
      Setting the register to value (upper line) yields in measuring a voltage of the lower line on the AO1:
      Set to: 0 1.3 3.5 5.0 5.7 7.9 10.
      Result: 0 1.1 2.9 4.0 4.8 6.5 8.2
      Somehow I doubt it is mismeasured. The device usually is accurate.
      So how does it come to these differences?
      Thanks!
      /KNEBB
        Martin Kudláček @knebb last edited by
        Hi @knebb,
        can you please post the C code?
        • K
          knebb @Martin Kudláček last edited by
          @Martin-Kudláček :
          Of course. Here you are. I set the registers and am measuring the AO port during the sleep() cycle.
          #include "header.h"
          #include "vars.h"
          void main(int argc, char* argv[])
          modbus_t *modbusglob;
          union {
                 uint16_t word[2];
                 uint32_t dword;
                 float fl;
          } counter,direct;
          int n[9],mode;
          /********************************* Function **********************************/
          void fieldbus_free(modbus_t *modbus)
                  if (modbus != NULL) {
                  modbus_close(modbus);
                  modbus_free(modbus);
          modbus_t * fieldbus_new(void)
          int err;
          modbus_t *modbus;
          char host[15];
          int port;
              strcpy(host,"127.0.0.1");
              port   = 502;
              modbus = modbus_new_tcp(host, port);
              if (modbus == NULL )
                 fieldbus_free(modbus);
                 exit (55);
              err = modbus_connect(modbus);
              if (err  == -1)
                  modbus = NULL;
                  exit (55);
              err=modbus_set_slave(modbus, 0);
              if(  err == -1)
                  modbus = NULL;
                  exit (60);
              } else {
                  return modbus;
          int setvoltage(float wish)
          int errlvl;
          union {
                 uint16_t word[2];
                 uint32_t dword;
                 float fl;
          } wert;
          uint16_t ao;
                  wert.fl=wish;
                  errlvl=modbus_write_registers(modbusglob, 3000, 2, (&wert.word[0]));
                  if (errlvl == -1) {printf("ERR1 modbus_write_register, %s\n",modbus_strerror(errno));}
                  else { printf("Register set to %f\n",wert.fl);}
                  return errlvl;
          modbusglob=fieldbus_new();
          mode=1;
          setvoltage(1.3);
          sleep(60);
          setvoltage(3.5);
          sleep(60);
          setvoltage(5.7);
          sleep(60);
          setvoltage(7.9);
          sleep(60);
          setvoltage(10.0);
          sleep(60);
          setvoltage(0);
          sleep(60);
          setvoltage(5.0);
          fieldbus_free(modbusglob);
          exit (0);