measuring Temperature with AI
-
Dear Community,
I'm new to unipi and mervis and put up and since I could solve my first problem that my second one ^^.
History: After reading the documentation more carefully I recognized the need of "configuring the module", to change the I/O settings of my module. Until then I got the value -246.861. This is solved. :-)
Now a new issue appeared. I set up three Pt100 measurements with the same configuration. Two giving a reasonable value. Around 25 °C, but the first one shows -220 °C. Any ideas why? The same values appear when interchanging the sensors.
I'm using a brand new L523 module.
I enclosed some pictures for trouble shooting.Thanks in advance for your help.
/Matthias

-
Solved by: The pre K value was set to 0.1 as described in the documentation. I set it back to 1. With one every measurement is working properly.
Question: Could you explain in more detail how the pre and post K and Q values are working. I'm a bit confused. Obviously its just a matter of scaling since for Pt1000 the pre K factor need to be set to 0.1. So for Pt500 the pre K factor should be set to 0.5? Am I correct?
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.