    After installation of a xG18 extention I get a Server Error 500 for the Rest Json
    22 Posts 4 Posters 9.7k Views
      Stoeffel
      I was able to narrow down the problem further and I think the following error messages in the nginx.log are triggered when the server error 500 occurs:
      xy@sps:/var/log/nginx $ cat error.log
      2021/07/01 23:05:44 [alert] 1321#1321: *1 open socket #12 left in connection 2
      2021/07/01 23:05:44 [alert] 1321#1321: *2 open socket #13 left in connection 3
      2021/07/01 23:05:44 [alert] 1321#1321: *3 open socket #14 left in connection 4
      2021/07/01 23:05:44 [alert] 1321#1321: *4 open socket #15 left in connection 5
      2021/07/01 23:05:44 [alert] 1321#1321: aborting
      As soon as I comment out the xG18 in the evok.conf, the error messages are gone and the server runs perfectly.
        Martin Kudláček
        Hi @Stoeffel ,
        I tried to reproduce the error, but without any luck. I used:
        Neuron S103
        This OS image: https://kb.unipi.technology/_media/files:software:os-images:neuron-opensource-os_image-20210426.0.zip
        Then I installed evok (apt update && apt install evok -y)
        Replaced the /etc/evok.conf with the one you provided
        Rebooted the PLC
        The Evok starts without any problem and I can see the temperature:
        Can you please try the procedure from above?
        Thank you and have a nice day,
          Stoeffel
          Hello Martin
          Thanks for your reply.
          And <IP_Neuron>/josn/all shows correct values? Or Server Error 500?
          In the Webfrontend of evok I have also correct values.
          Stefan
            Stoeffel
            Hello Martin
            Here's what I did:
            • Downloaded your image and copied it to a new SD card.
            • Set network parameters.
            • Logged in via ssh and executed the following:
              sudo apt-get update && sudo apt-get upgrade
              sudo apt-get install evok
            check if evok frontend is running --> okay
            check if <IP>/json/all is running --> okay
            • Configure xG18 in evok.conf (version above)
            • restart evok
            check if <IP>/json/all is running --> Server Error 500
            If its easier I can open a Open VPN vor you to the Neuron for debugging.
            I have been trying to solve the problem for more than a year now, and I bought the 4 xG18s specifically to avoid the problems with the owfs. I would be happy if we could solve the problem. By the way, I've informed and work together with klaus from fhem forum that the xG18 extensions are correctly recognised in FHEM. That's done now.
            Thanks Stefan
              Stoeffel
              Hello Martin
              I have some more information for you.
              I have now connected another xG18 to my M203. I can reproduce the problem there exactly the same as with the L503 in the post above. Possibly the problem is with all Neurons versions the same.
              My xG18 are V1.0
              I also have the feeling that the Evok frontend is updated much more slowly with connected xG18 and sometimes hangs. However, the inputs and outputs work perfectly.
              I have also updated the NGINX server from the bulleye repository to version 1.18 because I had read a report in the forum with similar log entries as errors, which are patched from V.1.17 onwards. Unfortunately, this was not the solution.
              Kind regards
              Stefan
                Martin Kudláček @Stoeffel
                Hello @Stoeffel,
                thank you for the information. I am able to replicate the problem now. I have forwared the issue to my colleague who takes care the Evok and I'll get back to you as soon as I will now more, probably next week.
                  martin_triska
                  Hello @Stoeffel,
                  the issue should be fixed in the current release. Please upgrade to version 2.4.8.
                    Stoeffel
                    Hello Martin
                    I updated to 2.4.8. I can't see any difference. The problem is the same.
                    <IP>/json/all:
                    Also Modbus stops working after 1-5min. (Rx Tx stop blinking)
                    <IP>/rest/all works properly.
                    Greetings Stefan
                      Hello @Stoeffel,
                      with the 2.4.8 it looks ok from my side.
                      This is /json/all:
                      {"status": "success", "data": [{"counter_modes": ["Enabled", "Disabled"], "glob_dev_id": 1, "modes": ["Simple", "DirectSwitch"], "value": 0, "circuit": "1_01", "debounce": 50, "counter": 0, "counter_mode": "Enabled", "dev": "input", "mode": "Simple"}, {"counter_modes": ["Enabled", "Disabled"], "glob_dev_id": 1, "modes": ["Simple", "DirectSwitch"], "value": 0, "circuit": "1_02", "debounce": 50, "counter": 0, "counter_mode": "Enabled", "dev": "input", "mode": "Simple"}, {"counter_modes": ["Enabled", "Disabled"], "glob_dev_id": 1, "modes": ["Simple", "DirectSwitch"], "value": 0, "circuit": "1_03", "debounce": 50, "counter": 0, "counter_mode": "Enabled", "dev": "input", "mode": "Simple"}, {"counter_modes": ["Enabled", "Disabled"], "glob_dev_id": 1, "modes": ["Simple", "DirectSwitch"], "value": 0, "circuit": "1_04", "debounce": 50, "counter": 0, "counter_mode": "Enabled", "dev": "input", "mode": "Simple"}, {"relay_type": "digital", "glob_dev_id": 1, "pwm_duty": 0, "dev": "relay", "modes": ["Simple", "PWM"], "pwm_freq": 39, "value": 0, "alias": "al_lights_kitchen", "mode": "Simple", "circuit": "1_01", "pending": false}, {"relay_type": "digital", "glob_dev_id": 1, "pwm_duty": 0, "dev": "relay", "modes": ["Simple", "PWM"], "pwm_freq": 39, "value": 0, "alias": "al_lights_bedroom", "mode": "Simple", "circuit": "1_02", "pending": false}, {"pwm_duty": 0, "glob_dev_id": 1, "pwm_freq": 39, "modes": ["Simple", "PWM"], "value": 0, "circuit": "1_03", "pending": false, "relay_type": "digital", "dev": "relay", "mode": "Simple"}, {"pwm_duty": 0, "glob_dev_id": 1, "pwm_freq": 39, "modes": ["Simple", "PWM"], "value": 0, "circuit": "1_04", "pending": false, "relay_type": "digital", "dev": "relay", "mode": "Simple"}, {"glob_dev_id": 1, "unit": "V", "value": 0.010469025995341785, "circuit": "1_01", "range_modes": ["10.0"], "modes": ["Voltage", "Current"], "range": "10.0", "dev": "ai", "mode": "Voltage"}, {"modes": ["Voltage", "Current", "Resistance"], "value": 0.0, "glob_dev_id": 1, "dev": "ao", "circuit": "1_01", "unit": "V", "mode": "Voltage"}, {"value": 0, "circuit": "1_01", "dev": "led", "glob_dev_id": 1}, {"value": 0, "circuit": "1_02", "dev": "led", "glob_dev_id": 1}, {"value": 0, "circuit": "1_03", "dev": "led", "glob_dev_id": 1}, {"value": 0, "circuit": "1_04", "dev": "led", "glob_dev_id": 1}, {"circuit": "1_01", "value": 0, "glob_dev_id": 1, "dev": "wd", "timeout": 5000, "was_wd_reset": 0, "nv_save": 0}, {"glob_dev_id": 1, "last_comm": 0.014560937881469727, "ver2": "2.4", "sn": 1, "circuit": "1", "model": "S103", "dev": "neuron", "board_count": 1}, {"uart_circuit": "None", "dev": "extension", "glob_dev_id": 2, "last_comm": 1.0246500968933105, "circuit": "UART_1_2", "model": "xG18", "uart_port": "/dev/extcomm/0/0"}, {"conf_value": 3262, "glob_dev_id": 1, "sw_address": 0, "parity_modes": ["None", "Odd", "Even"], "stopb_modes": ["One", "Two"], "speed_modes": ["2400bps", "4800bps", "9600bps", "19200bps", "38400bps", "57600bps", "115200bps"], "dev": "uart", "circuit": "1_01", "parity_mode": "None", "stopb_mode": "One", "speed_mode": "19200bps"}, {"name": "temperature", "value": 327.68, "glob_dev_id": 2, "valid": "false", "dev": "unit_register", "circuit": "UART_1_2_8", "unit": "\u00b0C"}, {"name": "temperature", "value": 327.68, "glob_dev_id": 2, "valid": "false", "dev": "unit_register", "circuit": "UART_1_2_4", "unit": "\u00b0C"}, {"name": "temperature", "value": 327.68, "glob_dev_id": 2, "valid": "false", "dev": "unit_register", "circuit": "UART_1_2_5", "unit": "\u00b0C"}, {"name": "temperature", "value": 327.68, "glob_dev_id": 2, "valid": "false", "dev": "unit_register", "circuit": "UART_1_2_6", "unit": "\u00b0C"}, {"name": "temperature", "value": 327.68, "glob_dev_id": 2, "valid": "false", "dev": "unit_register", "circuit": "UART_1_2_7", "unit": "\u00b0C"}, {"name": "temperature", "value": 327.68, "glob_dev_id": 2, "valid": "false", "dev": "unit_register", "circuit": "UART_1_2_1", "unit": "\u00b0C"}, {"name": "temperature", "value": 327.68, "glob_dev_id": 2, "valid": "false", "dev": "unit_register", "circuit": "UART_1_2_2", "unit": "\u00b0C"}, {"name": "temperature", "value": 327.68, "glob_dev_id": 2, "valid": "false", "dev": "unit_register", "circuit": "UART_1_2_3", "unit": "\u00b0C"}, {"period_2": 2, "period_3": 2, "period_1": 2, "period_6": 2, "period_7": 2, "period_4": 2, "period_5": 2, "period_8": 2, "dev": "ext_config", "glob_dev_id": 2, "circuit": "UART_1_2", "address": 15}]}
                      This is my /etc/evok.conf:
                      [MAIN]                                          ; !!! ALL MAIN SECTION OPTIONS ARE MANDATORY !!!
                      config_version = 2.5                            ; Configuration file version, DO NOT CHANGE!
                      use_schema_verification = False                 ; Enabling this will deny any requests that do not match the JSON Schema; NOTE THAT THIS RESULTS IN A SIGNIFICANT INCREASE IN LATENCY AND SHOULD NOT BE USED EXCEPT FOR TESTING
                      log_level = ERROR                               ; Minimum severity of messages to be logged; one of INFO, DEBUG, WARNING, ERROR, CRITICAL
                      log_file = /var/log/evok.log                    ; Log file to use; will be cleared on boot
                      port = 8080                                     ; !!! Internal API port - only change if you are certain you know what you are doing; FOR OUR WEB INTERFACE THE PORT SHOULD BE CHANGED IN "/etc/evok-nginx.conf" INSTEAD !!!
                      webhook_enabled = False                         ; Enables webhook notification - see e.g. https://sendgrid.com/blog/whats-webhook/
                      webhook_address = http://127.0.0.1:80           ; Put your server endpoint address here (e.g. http://123.123.123.123:/wh )
                      webhook_device_mask = ["input","wd"]            ; List of device types to notify on (written as a JSON list) - adding AI will generate a large amount of messages!
                      webhook_complex_events = False                  ; EVOK will send POST requests with the same data as WebSocket, rather than an empty GET request
                      soap_server_enabled = False                     ; Enables the simple SOAP server; use only if you need the functionality
                      soap_server_port = 8081                         ; !!! IF SOAP SERVER IS ENABLED, THIS PORT NEEDS TO BE UNIQUE (i.e. different from the port setting above) !!!
                      force_immediate_state_changes = False           ; Outputs will return the value they are set to, rather than the value that the device is currently aware of
                      websocket_all_filtered = False                  ; 'All' WebSocket requests will be subject to the filtering set by 'filter'
                      [NEURON_1]
                      global_id = 1                                   ; Mandatory, REQUIRED TO BE UNIQUE
                      allow_register_access = False                   ; Optional, False default
                      scan_frequency = 10                             ; Optional, 10 default, scanning frequency in [Hz]
                      scan_enabled = True                             ; Optional, True default
                      ; Below you can find examples for connecting devices over UART; first example is a Neuron extension while the second is a custom third-party device
                      ; Devices sharing a port use the port settings of the first device on that port (baud rate, parity, stop bits)
                      ; !!! Note that device_name has to match a filename in the /etc/hw_definitions directory !!! See /etc/hw_definitions/CUSTOM_MODBUS_DEVICE.yaml for an example
                      [EXTENSION_1]
                      global_id = 2                                   ; Mandatory, REQUIRED TO BE UNIQUE
                      device_name = xG18                              ; Mandatory, must match name of .yaml modbus map file in /etc/hw_definitions
                      modbus_uart_port = /dev/extcomm/0/0             ; Mandatory
                      ;neuron_uart_circuit = 1_01                     ; Optional, allows associating extensions with specific Neuron UART-over-Modbus ports (not possible for non-Modbus UART ports, e.g. /dev/ttyUSB0 or /dev/ttyS0)
                      ;allow_register_access = False                  ; Optional, False default, is mandatory with third-party devices
                      ;address = 1                                    ; Optional, 1 default
                      ;scan_frequency = 10                            ; Optional, 10 default, scanning frequency in [Hz]
                      ;scan_enabled = True                            ; Optional, True default
                      ;baud_rate = 19200                              ; Optional, NEEDS UNIPI IMAGE TO WORK WITH UNIPI SERIAL PORTS! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN
                      ;parity = N                                     ; Optional, NEEDS UNIPI IMAGE TO WORK WITH UNIPI SERIAL PORTS! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN
                      ;stop_bits = 1                                  ; Optional, NEEDS UNIPI IMAGE TO WORK WITH UNIPI SERIAL PORTS! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN
                      ;[EXTENSION_2]
                      ;global_id = 3                                  ; Mandatory, REQUIRED TO BE UNIQUE
                      ;device_name = CUSTOM MODBUS DEVICE             ; Mandatory, must match name of .yaml modbus map file in /etc/hw_definitions
                      ;modbus_uart_port = /dev/extcomm/0/0            ; Mandatory
                      ;allow_register_access = True                   ; Mandatory with third-party devices
                      ;address = 1                                    ; Optional, 15 default
                      ;scan_frequency = 2                             ; Optional, 1 default, scanning frequency in [Hz]
                      [OWBUS_1]
                      owbus = /dev/i2c-1                              ; Mandatory, scanned bus (--i2c=/dev/i2c-1:ALL or localhost:2122 or 'u' for USB dongle)
                      interval = 3                                    ; Mandatory, [s] length of sensor reading
                      scan_interval = 300                             ; Mandatory, [s] How often the scanning is done
                      ; See below for 1Wire extension module configuration
                      ; Example for the 1W-4R/4DI extension module, 1W-8R is almost the same, only with inputs instead of relays
                      ; - Setting the correct reading interval is crucial to achieve ideal performance; the default interval is 15s
                      ;[1WDEVICE_2]
                      ;bus = 1
                      ;address = 29F39A17000000BC
                      ;type = DS2408
                      ;interval = 1
                      ;[1WRELAY_10]
                      ;sensor = 2
                      ;pin = 0
                      ;[1WRELAY_11]
                      ;sensor = 2
                      ;pin = 1
                      ;[1WRELAY_12]
                      ;sensor = 2
                      ;pin = 2
                      ;[1WRELAY_13]
                      ;sensor = 2
                      ;pin = 3
                      ;[1WINPUT_20]
                      ;sensor = 2
                      ;pin = 4
                      ;[1WINPUT_21]
                      ;sensor = 2
                      ;pin = 5
                      ;[1WINPUT_22]
                      ;sensor = 2
                      ;pin = 6
                      ;[1WINPUT_23]
                      ;sensor = 2
                      ;pin = 7
                      Please, verify that the configuration is the same. If it still doesn't work, can you please stop the evok and run it manually? It will show more information about the error.
                      systemctl stop evok
                      /opt/evok/bin/python /opt/evok/lib/python2.7/site-packages/evok/evok.py
                        Stoeffel
                        Hello Martin
                        I checked again the evok.conf
                        I have exactly the same settings as you.
                        Here the output:
                        user@sps:~ $ sudo /opt/evok/bin/python /opt/evok/lib/python2.7/site-packages/evok/evok.py
                        [I 210721 21:36:07 config:73] eprom: UniPi Neuron L503 version: 1.0 serial: 0x62
                        [I 210721 21:36:07 evok:1894] Starting using config file /etc/evok.conf
                        /opt/evok/lib/python2.7/site-packages/evok/config.py:96: YAMLLoadWarning: calling yaml.load() without Loader=... is deprecated, as the default Loader is unsafe. Please read https://msg.pyyaml.org/load for full details.
                          self.definitions += [yaml.load(yfile)]
                        [I 210721 21:36:07 config:97] YAML Definition loaded: xS10.yaml, type: 3, definition count 0
                        [I 210721 21:36:08 config:97] YAML Definition loaded: xS30.yaml, type: 3, definition count 1
                        [I 210721 21:36:08 config:97] YAML Definition loaded: IAQ.yaml, type: 3, definition count 2
                        /opt/evok/lib/python2.7/site-packages/evok/config.py:103: YAMLLoadWarning: calling yaml.load() without Loader=... is deprecated, as the default Loader is unsafe. Please read https://msg.pyyaml.org/load for full details.
                          self.neuron_definition = yaml.load(yfile)
                        [I 210721 21:36:08 config:104] YAML Definition loaded: /etc/hw_definitions/BuiltIn/L503.yaml, type: UniPiBuiltIn
                        [I 210721 21:36:08 config:97] YAML Definition loaded: xS40.yaml, type: 3, definition count 3
                        [I 210721 21:36:08 config:97] YAML Definition loaded: xG18.yaml, type: 3, definition count 4
                        [I 210721 21:36:08 config:97] YAML Definition loaded: xS51.yaml, type: 3, definition count 5
                        [I 210721 21:36:08 config:97] YAML Definition loaded: xS50.yaml, type: 3, definition count 6
                        [I 210721 21:36:08 config:97] YAML Definition loaded: CUSTOM_MODBUS_DEVICE.yaml, type: 3, definition count 7
                        [I 210721 21:36:08 config:97] YAML Definition loaded: xS11.yaml, type: 3, definition count 8
                        [I 210721 21:36:08 config:97] YAML Definition loaded: evok-alias.yaml, type: 2, definition count 0
                        [I 210721 21:36:08 evok:1964] HTTP server listening on port: 8080
                        [I 210721 21:36:09 modbusclient_tornado:128] SPI client started
                        [I 210721 21:36:09 modbusclient_rs485:347] UART client started
                        [I 210721 21:36:09 neuron:334] Reading the UART board on Modbus address 2
                        [I 210721 21:36:09 owclient:445] Entering OWW loop with PID 2074
                        [I 210721 21:36:09 neuron:334] Reading the UART board on Modbus address 3
                        [I 210721 21:36:09 neuron:334] Reading the UART board on Modbus address 4
                        [I 210721 21:36:09 neuron:334] Reading the UART board on Modbus address 1
                        [I 210721 21:36:09 neuron:215] Reading SPI boards
                        [C 210721 21:36:09 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 285076EB09000092
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 2830A9D309000034
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 283278D5090000C0
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 28CA66EB09000090
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 281EA6EA09000025
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 2801BF790B0000F3
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 2891EBEA090000EE
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 28097AD30900005F
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 28492EEB090000F4
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 28D92ED409000097
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 2885FFD3090000D1
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 2895EBD40900006F
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 289D6AD509000047
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 28BD9ED309000041
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 289391D40900000D
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 284B90D309000023
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 2877B5EB090000CD
                        [D 210721 21:36:11 owclient:335] New sensor DS18B20 - 280FB2EB090000A5
                        [C 210721 21:36:18 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [C 210721 21:36:19 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [C 210721 21:36:21 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [E 210721 21:36:21 modbusclient_rs485:259]   Unrequested message: <modbusclient_rs485.AsyncErrorResponse object at 0x75f5b510>
                        [D 210721 21:36:21 neuron:97] device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:36:21 sync:383] cleanup recv buffer before send:
                        [C 210721 21:36:22 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:36:22 sync:383] cleanup recv buffer before send: 0x31
                        [C 210721 21:36:33 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:36:33 sync:383] cleanup recv buffer before send: 0x0
                        [C 210721 21:36:43 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [C 210721 21:36:45 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:36:45 sync:383] cleanup recv buffer before send:
                        [C 210721 21:36:46 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [I 210721 21:36:48 web:2064] 101 GET /ws (127.0.0.1) 6.56ms
                        [D 210721 21:36:48 evok:162] New WebSocket client connected
                        [C 210721 21:36:48 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:36:48 sync:383] cleanup recv buffer before send: 0x0
                        [C 210721 21:36:50 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [C 210721 21:36:51 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:36:51 sync:383] cleanup recv buffer before send: 0x0
                        [C 210721 21:36:53 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:36:53 sync:383] cleanup recv buffer before send: 0x0
                        [W 210721 21:36:53 sync:383] cleanup recv buffer before send: 0x80
                        [C 210721 21:36:54 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:36:54 sync:383] cleanup recv buffer before send: 0x0
                        [C 210721 21:37:05 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:37:05 sync:383] cleanup recv buffer before send:
                        [C 210721 21:37:06 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:37:06 sync:383] cleanup recv buffer before send: 0x2
                        [C 210721 21:37:14 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:37:14 sync:383] cleanup recv buffer before send: 0x2
                        [C 210721 21:37:22 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [C 210721 21:37:23 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:37:23 sync:383] cleanup recv buffer before send:
                        [C 210721 21:37:35 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:37:35 sync:383] cleanup recv buffer before send:
                        [C 210721 21:37:37 modbusclient_rs485:232] SerialException: device reports readiness to read but returned no data (device disconnected or multiple access on port?)
                        [W 210721 21:37:37 sync:383] cleanup recv buffer before send: 0x2
                              File "/opt/evok/local/lib/python2.7/site-packages/tornado/ioloop.py", line 605, in _run_callback
                                ret = callback()
                              File "/opt/evok/local/lib/python2.7/site-packages/tornado/stack_context.py", line 277, in null_wrapper
                                return fn(*args, **kwargs)
                              File "/opt/evok/lib/python2.7/site-packages/evok/modbusclient_rs485.py", line 162, in _sendAsyncRequest
                                self.client._send(self.frame)
                              File "/opt/evok/lib/python2.7/site-packages/evok/modbusclient_rs485.py", line 263, in _send
                                super(AsyncModbusSerialClient, self)._send(request)
                              File "/opt/evok/local/lib/python2.7/site-packages/pymodbus/client/sync.py", line 381, in _send
                                result = self.socket.read(waitingbytes)
                              File "/opt/evok/local/lib/python2.7/site-packages/serial/serialposix.py", line 596, in read
                                'device reports readiness to read but returned no data '
                        [E 210721 21:39:38 web:1591] Uncaught exception GET /rest/all (127.0.0.1)
                            HTTPServerRequest(protocol='http', host='192.168.1.70:80', method='GET', uri='/rest/all', version='HTTP/1.0', remote_ip='127.0.0.1', headers={'Sec-Gpc': '1', 'Accept-Language': 'de-CH', 'Accept-Encoding': 'gzip, deflate', 'Host': '192.168.1.70:80', 'Accept': 'text/html,application/xhtml+xml,application/xml;q=0.9,image/webp,*/*;q=0.8', 'User-Agent': 'Mozilla/5.0 (X11; Ubuntu; Linux x86_64; rv:90.0) Gecko/20100101 Firefox/90.0', 'Connection': 'close', 'Upgrade-Insecure-Requests': '1'})
                              File "/opt/evok/local/lib/python2.7/site-packages/tornado/web.py", line 1510, in _execute
                                result = method(*self.path_args, **self.path_kwargs)
                              File "/opt/evok/lib/python2.7/site-packages/evok/evok.py", line 1591, in get
                                result += map(lambda dev: dev.full(), Devices.by_int(UNIT_REGISTER))
                              File "/opt/evok/lib/python2.7/site-packages/evok/evok.py", line 1591, in <lambda>
                              File "/opt/evok/lib/python2.7/site-packages/evok/neuron.py", line 1655, in full
                                'value': (self.regvalue()),
                              File "/opt/evok/lib/python2.7/site-packages/evok/neuron.py", line 1593, in <lambda>
                                self.regvalue = lambda: (self.arm.neuron.modbus_cache_map.get_register(1, self.valreg, unit=self.arm.modbus_address, is_input=_is_iput)[0] * self.factor) + self.offset
                              File "/opt/evok/lib/python2.7/site-packages/evok/neuron.py", line 55, in get_register
                            Exception: No cached value of register 8 on unit 1 - read error
                        [E 210721 21:39:38 web:2064] 500 GET /rest/all (127.0.0.1) 44.95ms
                        [E 210721 21:39:42 web:1591] Uncaught exception GET /rest/all (::1)
                            HTTPServerRequest(protocol='http', host='192.168.1.70:80', method='GET', uri='/rest/all', version='HTTP/1.0', remote_ip='::1', headers={'Sec-Gpc': '1', 'Accept-Language': 'de-CH', 'Accept-Encoding': 'gzip, deflate', 'Host': '192.168.1.70:80', 'Accept': 'text/html,application/xhtml+xml,application/xml;q=0.9,image/webp,*/*;q=0.8', 'User-Agent': 'Mozilla/5.0 (X11; Ubuntu; Linux x86_64; rv:90.0) Gecko/20100101 Firefox/90.0', 'Connection': 'close', 'Upgrade-Insecure-Requests': '1'})
                        [E 210721 21:39:42 web:2064] 500 GET /rest/all (::1) 15.39ms
                        [E 210721 21:39:50 web:1591] Uncaught exception GET /json/all (127.0.0.1)
                            HTTPServerRequest(protocol='http', host='192.168.1.70:80', method='GET', uri='/json/all', version='HTTP/1.0', remote_ip='127.0.0.1', headers={'Sec-Gpc': '1', 'Accept-Language': 'de-CH', 'Accept-Encoding': 'gzip, deflate', 'Host': '192.168.1.70:80', 'Accept': 'text/html,application/xhtml+xml,application/xml;q=0.9,image/webp,*/*;q=0.8', 'User-Agent': 'Mozilla/5.0 (X11; Ubuntu; Linux x86_64; rv:90.0) Gecko/20100101 Firefox/90.0', 'Connection': 'close', 'Upgrade-Insecure-Requests': '1'})
                              File "/opt/evok/local/lib/python2.7/site-packages/tornado/web.py", line 1512, in _execute
                                result = yield result
                              File "/opt/evok/local/lib/python2.7/site-packages/tornado/gen.py", line 1055, in run
                                value = future.result()
                              File "/opt/evok/local/lib/python2.7/site-packages/tornado/concurrent.py", line 238, in result
                              File "/opt/evok/local/lib/python2.7/site-packages/tornado/gen.py", line 307, in wrapper
                                yielded = next(result)
                              File "/opt/evok/local/lib/python2.7/site-packages/tornado_json/schema.py", line 160, in _wrapper
                                output = rh_method(self, *args, **kwargs)
                              File "/opt/evok/lib/python2.7/site-packages/evok/evok.py", line 1540, in get
                              File "/opt/evok/lib/python2.7/site-packages/evok/evok.py", line 1540, in <lambda>
                        [E 210721 21:39:50 web:2064] 500 GET /json/all (127.0.0.1) 23.83ms
                          martin_triska
                          Hello @Stoeffel ,
                          it seems that you access the serial (RS485) line from multiple applications which confuses Evok. Can you try to disable other processes potentially working with HW and leave running Evok only?
                          • Y
                            yish
                            My L403 just arrived yesterday and I’m trying to connect the xG18 and having the same issues with Stefan.
                            I was able to connect in node-red over modbus RTU directly.
                            However when I try to access through Evok (different SD card with the same base OS image: https://kb.unipi.technology/_media/files:software:os-images:neuron-node-red_image-20210426.2.zip), I get the exact same error message as Stefan.
                            unipi@L403-sn141:/etc$ sudo /opt/evok/bin/python /opt/evok/lib/python2.7/site-packages/evok/evok.py
                            [I 210723 07:07:45 config:73] eprom: UniPi Neuron L403 version: 0.1 serial: 0x8d
                            [I 210723 07:07:45 evok:1894] Starting using config file /etc/evok.conf
                            [I 210723 07:07:45 config:97] YAML Definition loaded: xS10.yaml, type: 3, definition count 0
                            [I 210723 07:07:45 config:97] YAML Definition loaded: xS51.yaml, type: 3, definition count 1
                            [I 210723 07:07:45 config:97] YAML Definition loaded: IAQ.yaml, type: 3, definition count 2
                            [I 210723 07:07:45 config:97] YAML Definition loaded: xG18.yaml, type: 3, definition count 3
                            [I 210723 07:07:45 config:97] YAML Definition loaded: xS30.yaml, type: 3, definition count 4
                            [I 210723 07:07:45 config:97] YAML Definition loaded: CUSTOM_MODBUS_DEVICE.yaml, type: 3, definition count 5
                            [I 210723 07:07:46 config:97] YAML Definition loaded: xS40.yaml, type: 3, definition count 6
                            [I 210723 07:07:46 config:97] YAML Definition loaded: xS50.yaml, type: 3, definition count 7
                            [I 210723 07:07:46 config:97] YAML Definition loaded: xS11.yaml, type: 3, definition count 8
                            [I 210723 07:07:46 config:104] YAML Definition loaded: /etc/hw_definitions/BuiltIn/L403.yaml, type: UniPiBuiltIn
                            [I 210723 07:07:46 config:97] YAML Definition loaded: evok-alias.yaml, type: 2, definition count 0
                            [I 210723 07:07:46 evok:1964] HTTP server listening on port: 8080
                            [I 210723 07:07:46 modbusclient_tornado:128] SPI client started
                            [I 210723 07:07:46 modbusclient_rs485:347] UART client started
                            [I 210723 07:07:46 neuron:334] Reading the UART board on Modbus address 1
                            [I 210723 07:07:46 neuron:215] Reading SPI boards
                            [I 210723 07:07:46 owclient:445] Entering OWW loop with PID 1414
                            [I 210723 07:07:47 config:390] Alias loaded: <neuron.Relay object at 0x76244cf0> al_lights_kitchen
                            [I 210723 07:07:47 config:390] Alias loaded: <neuron.Relay object at 0x762653d0> al_lights_bedroom
                            [I 210723 07:07:48 web:2064] 101 GET /ws (127.0.0.1) 5.50ms
                            [D 210723 07:07:48 evok:162] New WebSocket client connected
                            [I 210723 07:07:52 config:390] Alias loaded: <neuron.Relay object at 0x76244cf0> al_lights_kitchen
                            [I 210723 07:07:52 config:390] Alias loaded: <neuron.Relay object at 0x762653d0> al_lights_bedroom
                            [E 210723 07:08:02 web:1591] Uncaught exception GET /json/all (::1)
                                HTTPServerRequest(protocol='http', host='l403-sn141.local:80', method='GET', uri='/json/all', version='HTTP/1.0', remote_ip='::1', headers={'Accept-Language': 'en-us', 'Accept-Encoding': 'gzip, deflate', 'Host': 'l403-sn141.local:80', 'Accept': 'text/html,application/xhtml+xml,application/xml;q=0.9,*/*;q=0.8', 'User-Agent': 'Mozilla/5.0 (Macintosh; Intel Mac OS X 10_15_7) AppleWebKit/605.1.15 (KHTML, like Gecko) Version/13.1.3 Safari/605.1.15', 'Connection': 'close', 'Upgrade-Insecure-Requests': '1'})
                                  File "/opt/evok/lib/python2.7/site-packages/evok/neuron.py", line 1654, in full
                                  File "/opt/evok/lib/python2.7/site-packages/evok/neuron.py", line 1592, in <lambda>
                            [E 210723 07:08:02 web:2064] 500 GET /json/all (::1) 28.64ms
                            Did an apt update and install to the latest evok version (2.4.10) to no avail.
                              Martin Kudláček @yish
                              Hello @yish,
                              the image doesn't have the latest evok. Please, proceed with apt update && apt upgrade, then reboot the PLC and try again.
                              Have a nice weekend,
                              • Y
                                yish
                                @Martin-Kudláček said in After installation of a xG18 extention I get a Server Error 500 for the Rest Json:
                                Updated, Rebooted and same error:
                                root@L403-sn141:/home/unipi# systemctl stop evok
                                root@L403-sn141:/home/unipi# /opt/evok/bin/python /opt/evok/lib/python2.7/site-packages/evok/evok.py
                                [I 210723 14:58:18 config:73] eprom: UniPi Neuron L403 version: 0.1 serial: 0x8d
                                [I 210723 14:58:18 evok:1894] Starting using config file /etc/evok.conf
                                [I 210723 14:58:18 config:97] YAML Definition loaded: xS10.yaml, type: 3, definition count 0
                                [I 210723 14:58:18 config:97] YAML Definition loaded: xS51.yaml, type: 3, definition count 1
                                [I 210723 14:58:19 config:97] YAML Definition loaded: IAQ.yaml, type: 3, definition count 2
                                [I 210723 14:58:19 config:97] YAML Definition loaded: xG18.yaml, type: 3, definition count 3
                                [I 210723 14:58:19 config:97] YAML Definition loaded: xS30.yaml, type: 3, definition count 4
                                [I 210723 14:58:19 config:97] YAML Definition loaded: CUSTOM_MODBUS_DEVICE.yaml, type: 3, definition count 5
                                [I 210723 14:58:19 config:97] YAML Definition loaded: xS40.yaml, type: 3, definition count 6
                                [I 210723 14:58:19 config:97] YAML Definition loaded: xS50.yaml, type: 3, definition count 7
                                [I 210723 14:58:19 config:97] YAML Definition loaded: xS11.yaml, type: 3, definition count 8
                                [I 210723 14:58:20 config:104] YAML Definition loaded: /etc/hw_definitions/BuiltIn/L403.yaml, type: UniPiBuiltIn
                                [I 210723 14:58:20 config:97] YAML Definition loaded: evok-alias.yaml, type: 2, definition count 0
                                [I 210723 14:58:20 evok:1964] HTTP server listening on port: 8080
                                [I 210723 14:58:20 modbusclient_tornado:128] SPI client started
                                [I 210723 14:58:20 modbusclient_rs485:347] UART client started
                                [I 210723 14:58:20 neuron:334] Reading the UART board on Modbus address 1
                                [I 210723 14:58:20 neuron:215] Reading SPI boards
                                [I 210723 14:58:20 owclient:445] Entering OWW loop with PID 1412
                                [I 210723 14:58:20 config:390] Alias loaded: <neuron.Relay object at 0x761f6db0> al_lights_kitchen
                                [I 210723 14:58:20 config:390] Alias loaded: <neuron.Relay object at 0x76217510> al_lights_bedroom
                                [I 210723 14:58:20 web:2064] 101 GET /ws (::1) 6.23ms
                                [D 210723 14:58:20 evok:162] New WebSocket client connected
                                [I 210723 14:58:20 web:2064] 200 GET /rest/all (::1) 15.25ms
                                [I 210723 14:58:21 web:2064] 101 GET /ws (127.0.0.1) 3.41ms
                                [D 210723 14:58:21 evok:162] New WebSocket client connected
                                [I 210723 14:58:26 config:390] Alias loaded: <neuron.Relay object at 0x761f6db0> al_lights_kitchen
                                [I 210723 14:58:26 config:390] Alias loaded: <neuron.Relay object at 0x76217510> al_lights_bedroom
                                [E 210723 14:58:26 web:1591] Uncaught exception GET /json/all (::1)
                                [E 210723 14:58:26 web:2064] 500 GET /json/all (::1) 26.74ms
                                [D 210723 14:58:31 evok:259] Skipping WS message: {u'cmd': u'all'} (No cached value of register 8 on unit 1 - read error)
                                [E 210723 14:58:33 web:1591] Uncaught exception GET /rest/all (::1)
                                    HTTPServerRequest(protocol='http', host='l403-sn141.local:80', method='GET', uri='/rest/all', version='HTTP/1.0', remote_ip='::1', headers={'Accept-Language': 'en-us', 'Accept-Encoding': 'gzip, deflate', 'Host': 'l403-sn141.local:80', 'Accept': 'text/html,application/xhtml+xml,application/xml;q=0.9,*/*;q=0.8', 'User-Agent': 'Mozilla/5.0 (Macintosh; Intel Mac OS X 10_15_7) AppleWebKit/605.1.15 (KHTML, like Gecko) Version/13.1.3 Safari/605.1.15', 'Connection': 'close', 'Upgrade-Insecure-Requests': '1'})
                                [E 210723 14:58:33 web:2064] 500 GET /rest/all (::1) 11.47ms
                                [E 210723 14:58:33 web:2064] 500 GET /rest/all (::1) 11.42ms
                                  Stoeffel
                                  Hello Martin
                                  I hope I have solved the problem now. My Modbus and Json/Rest have been running error-free for 24 hours.
                                  I have done the following:
                                  • Update EVOK to 2.4.10
                                  • Deactivated the Modbus device in FHEM
                                  • The Modbus is now only addressed via the Neuron Device in FHEM.
                                  The access to the Modbus is realised with Fhem on the one hand via the Device Neuron and on the other hand via the Device Modbus. If both are installed, there will probably be conflicts which cause EVOK to crash. In any case, it was possible to get the system running again for a while by restarting EVOK.
                                  After deactivating the Modbus device in Fhem, I no longer had any error messages in EVOK. However, after 2 hours, the Modbus hung up again. Then I updated EVOK to 2.4.10 and rebooted everything. Since then, the system has been running error-free for 24 hours.
                                  I will get back a response to you in a week again.
                                  Kind regards Stefan
                                  • Y
                                    yish
                                    Hi Martin, do you have any suggestions on how to resolve. I tried disabling node-red to see if that worked but no success. Am open to suggestions on what to try.
                                    If I have some extra time I will try a fresh SD card with the setup you verified for Stefan (specified vanilla neuron OS, install evok, and use the same evok.conf) to see if that will work.
                                      Stoeffel
                                      As promised, here is the feedback.
                                      The problem has definitely been solved.
                                      Many thanks for the help
                                      Kind regards
                                      Stefan