NodeRed with analog OUTput
-
I have found trouble with nodered "UniPi output" block in connection with Analog Output mode.
I use Analog Output 1.01 with Current configuration, where sending 4-20mA to the valve. But in "UniPi output" block we see the limits:
Details for the Analog output input msg:
Number - in the interval <0;10> returns the input number, <0 returns 0, >10 returns 10.So, when I send a 20mA to fully open a valve, this valve received only 10mA, because your module has limits.
How can I fix that?
-
Hello @beergeek
You are right with problem when using analog output in configuration 0-20mA. When we designed nodes, we only implemented voltage output.
To fast repair you can add function node to output, that recalculate output value from 0-10 to 0-20. So your input value will be 0 to 10, but output value will be 0-20. We will try to repair output node with support for current output it in next week.
Function code to fast implementation:

Try to import funtion and connect it as in picture.
[{"id":"98b4db11.a43aa8","type":"function","z":"dd6bd412.3bde08","name":"0-20mA","func":"if(msg.payload.value) \n{\n msg.payload.value = msg.payload.value*2.00;\n}\nreturn msg;","outputs":1,"noerr":0,"x":1260,"y":220,"wires":[["a7851ed2.a7d6"]]}]Thank you for your notice.
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.