    Could not find temp sensors connected via 1-wire hub

    Scheduled Pinned Locked Moved Mervis
    5 Posts 2 Posters 2.8k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • D
      dgajic
      last edited by

      Hi,

      not sure is this Mervis or HW issue, but I've recently purchased 2 temp sensors and 1-wire 8 port hub from the shop. I can't see temp sensors in Mervis if they are connected via 1-wire 8 port hub, but if I connect them directly to Neuron (m203) 1-wire port they do work (one by one of course).

      I have connected Neuron to hub via patch 5e cable (cable is checked, working), hub is shielded, on the hub itself it's stated port 1 is for IN, so patch cable is on port 1, two temp sensors are on ports 2 and 3.

      I configure Mervis the same way like for single temp sensor:

      • 1-wire channel added
      • build/deploy
      • PLC to commision mode
      • Discover temperature sensors returns empty list/table

      When I repeat the same with one temp sensor directly attached on 1-wire on Neuron, everything works OK.

      I've also tried to add 2 temp sensors and then to assign them, with the same results, via hub it's not working, directly yes.

      Do I need to do something else in Mervis, or any other advice?

      Thanks!

      T 1 Reply Last reply
      Reply Quote 0
      • T
        tomas_hora administrators @dgajic
        last edited by

        @dgajic Do you have the connection of the sensors and the 1wire line from Neuron correctly according to the schematics on the hub?

        1 Reply Last reply
        Reply Quote 0
        • D
          dgajic
          last edited by

          Port 1 on hub is marked as IN and I have patch cable there connected to 1-wire on Neuron.

          Temperature sensors are from the shop, I think they have only 4 pins wired (5-8), and they are connected to ports 2 and 3 of the hub.

          So, 3 ports on the hub used (1-3), first 1-wire to Neuron via patch cable and then 2 temp sensors.

          Is this correct?

          1 Reply Last reply
          Reply Quote 0
          • D
            dgajic
            last edited by

            Solved!

            I had to open 1 wire hub, there was a short circuit between pins 3 and 4 on port 8. After fixing that, everything is working OK.

            T 1 Reply Last reply
            Reply Quote 0
            • T
              tomas_hora administrators @dgajic
              last edited by

              @dgajic Thanks a lot for the info. I am glad you figured it out. Also sorry for the issues!

              1 Reply Last reply
              Reply Quote 0

              Hello! It looks like you're interested in this conversation, but you don't have an account yet.

              Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.