How to Read M103 Modbus Doc?
-
Hi all,
ok, I manged to use the relays through modbus with libmodbus with my C-code. Now I am trying to use the DI/DO/AO/AI interfaces.
I see the Neuron Registers Map but I am only able to understand it partially...
I am aware the function modbus_read_bits() can be usedd to read the DIs. So I open a modbus_tcp connection with the address of DI2.1 for example:
modbus_read_bits(modbus_handle, 108, nb, *dest);*dest is supposed to be uint16_t.
I was able to read the above- finally I have some data in *dest. But how do I have to read the data there? I expected something like "bit 1 tells if the DI is currently ON or OFF and bit2 is the counter while writing bit3 will reset the counter" or stuff like this.
So I am a little bit lost here to interpret the values I got.
Nearly the same is for writing. What values should I put into uint16_t to enable the DI?
And how can I configure the AO?
Thanks a lot for hints!
/KNEBB
-
@knebb said in How to Read M103 Modbus Doc?:
*dest is supposed to be uint16_t.
No, it is an uint8_t array. Every element of the array contains the value of a single digital channel, set to
TRUE(that is, IIRC,1) orFALSE(that is surely0).Here is my untested snippet:
// Reading one channel uint8_t my_digital; modbus_read_bits(bus, 108, 1, &my_digital); if (my_digital) { ... } // Reading multiple channels uint8_t my_digitals[2]; modbus_read_bits(bus, 108, 2, my_digitals); if (my_digitals[0]) { ... } -
@ntd :Thanks a lot four your input, I really appreciate it.
I am just wondering as there seems to be no difference between uint8_t, uint16_t and uint32_t.
See my question here.
When using uint8_t the result is exactly the same. All seem to be 32bit long...So how does modbus deal with this? It writes only the least significant 8 bits? Others are set to zero?
/KNEBB
-
@knebb TL/DR: just use
uint8_t. This is the right thing to do.There is no differences (because of integer promotion) only when you use that variable in an expression. Incidentally, and for different reasons [1], reading a single bit will work with whatever 0-initialized integer you throw at
modbus_read_bits, although conceptually wrong. But I can assure you that, when reading multiple channels, using anything butuint8_twill give you wrong results.[1] Raspberry Pi is little-endian. Setting the first byte of any 0-initialized
uint*variable to a specific value (e.g.,TRUE), makes that very same variable initialized to that value, regardless of its type.Here is an example that hopefully will shed some light:
#include <assert.h> #include <stdint.h> #include <string.h> #define TRUE 12 int main() { // Using an union to be able to set the first byte of everything // with only one instruction (m.byte = ...) union { uint8_t byte; uint16_t word; uint32_t dword; uint64_t qword; } m; // Let's set the first byte of 0 initialized memory memset(&m, 0, sizeof m); m.byte = TRUE; assert(m.byte == TRUE); // Ok assert(m.word == TRUE); // Ok on little-endian machines assert(m.dword == TRUE); // Ok on little-endian machines assert(m.qword == TRUE); // Ok on little-endian machines // Now let's try with random initialized memory memset(&m, 3, sizeof m); m.byte = TRUE; assert(m.byte == TRUE); // Ok assert(m.word == TRUE); // Error! assert(m.dword == TRUE); // Error! assert(m.qword == TRUE); // Error! return 0; } -
Thanks for the explanation; I figured it already out Raspbian is littleEndian.
Just to make sure:
To read i.e. the counter for digital input 2.1 (address 103-104 with DWORD, 32bit in total) I would use:uint8_t counter[4]; modbus_read_bits(bus, 103, 4, counter);Or this one?
uint8_t counter1[2],counter2[2]; modbus_read_bits(bus, 103, 2, counter1); modbus_read_bits(bus, 104, 2, counter2);Would both work?
Sorry for my dumb question, I am really new to modbus...
/KNEBB
-
@knebb said:
Would both work?
None of them will. You should really read a ModBUS introduction... I think the wikipedia page should suffice.
The counter is an input register, not a bit, so:
union { uint16_t word[2]; uint32_t dword; } counter; if (modbus_read_registers(bus, 103, 2, counter.word) != 2) { printf("Error\n"); } else { printf("DI2.1 counter is %u\n", counter.dword); }Not sure which is the less and the most significant word, so if the above gives wrong results just swap
counter.word[0]andcounter.word[1]. -
@ntd
Perfect!Got it finally. I mixed up modbus_read_bits and modbus_read_register. Now working like a charm!
Thanks a lot!
/KNEBB
-
@all
As I was struggling again with this I figured it out now finally (at least I hope so).
My issue was the interpretation of whatever value I got.
So for alle future readings:
In the linked Calc-Sheet above you have notes about the registers (read only registers, not bits!).
So for the M103 you have the "Registers - group 1" and "Registers - group 2". Use these. The coils tables are somehow misleading (at least for me).
Additionally be aware
modbus_read_registers()need to write the data into anuint16_tvariable. With the help of @ntd and his suggestes "union" I was easy to "convert" them into the uint32_t. Unions access the same memory by different variables. See more here.In the code sniplet above
modbus_read_registers()writes the content into the counter.word memory location and the prinft reads them as uint32_t. Easy going now to re-calculate the counter.dword variable to get the values you need.So to read the current settings and values of all relays and digital inputs I use the following code:
uint16_t state; union { uint16_t word[2]; uint32_t dword; } counter; /* Relais */ modbus_read_registers(modbusglob,101,1,&state); printf("Lesen Relay Register: %u\n",state); printf("\n"); /* DigitalIN 1 */ modbus_read_registers(modbusglob,0,1,&state); printf("Lesen DigIn1: %u\n",state); printf("\n"); /* Digital-In 1 Counter */ for (i=8;i<16;i=i+2) { modbus_read_registers(modbusglob,i,2,counter.word); printf("Counter %d DigIn1: %u\n",i,counter.dword); } printf("\n"); /* DigitalIN 2 */ modbus_read_registers(modbusglob,100,1,&state); printf("Lesen DigIn1: %d\n",state); printf("\n"); /* DigitalIN 2 Counter */ for (i=103;i<118;i=i+2) { modbus_read_registers(modbusglob,i,2,counter.word); printf("Counter %d DigIn2: %u\n",i,counter.dword); }This works now perfectly.
/KNEBB
-
Just as an update.
I was struggling with multiple registers which are used i.e. for the AO1.1 port of my Neuron M103.
So for the AO registers 3000 and 3001 are given as "real".
I extended the above
unionas follows:union { uint16_t word[2]; uint32_t dword; float fl; } counter;And I am reading the register like this:
modbus_read_registers(modbusglob, 3000, 2, &counter.word[0]);It reads 2 registers starting at 3000 and writes the result in the word array where it is automatically converted to "float" by the union structure.
Works fine!
/KNEBB
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.