Correct timezone offset setting.



  • Hello,

    Despite having UTC offset set to 0 in the PLC properties, and the time being set correctly in UTC:-

    0_1547493755720_Capture1.PNG

    root@L203-sn218:~# date
    Mon 14 Jan 19:23:22 UTC 2019
    
    root@L203-sn218:~# hwclock --localtime
    2019-01-14 19:23:27.912454+0000
    

    The result of "getlocaltime" in mervis is always 1 hour ahead.

    0_1547493683488_Capture.PNG

    Any ideas how to get it to use UTC time properly?

    Thanks.


  • administrators

    Hello @robl,
    the change you have made is a change of the configuration of the PLC which has to be uploaded to take affect:

    0_1547543323443_379d1180-a268-4c89-8a8f-442a5dedfa80-image.png

    Please be aware of the network settings, which by default will change to IP of the PLC to the static 192.168.1.121