Siemens SQX62
-
I would like to use my actuators for underfloor heating with unipi
Is it possible to connect 24 Vac on analog on unipi as illustrated.
Then replace N1 with a unipi
[attachment=1:3p3de0wg]Siemens SQX62.jpg[/attachment:3p3de0wg]Connection as shown below
SN>A0G
SP>A0V
Y>A0
[attachment=0:3p3de0wg]Analog_unipi.jpg[/attachment:3p3de0wg] -
I would like to use my actuators for underfloor heating with unipi
Is it possible to connect 24 Vac on analog on unipi as illustrated.
Then replace N1 with a unipi
[attachment=1:3p3de0wg]Siemens SQX62.jpg[/attachment:3p3de0wg]Connection as shown below
SN>A0G
SP>A0V
Y>A0
[attachment=0:3p3de0wg]Analog_unipi.jpg[/attachment:3p3de0wg] -
You definitely do not want to connect 24V AC

But what is a little confusing that the connector has 0-10V DC but does not have a proper GND for it... Or am I missing anything? Because you cannot connect the GND of UniPi to the AC gnd. But if you find where to put gnd for the 0-10V than you can easily connect it according to the second picture
-
GND to 0-10V DC sits on G0 24VAC on Siemens RLE162 regulator
-
The problem is solved

Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.