RS485/M-Bus converter configuration
-
Hi all, is here anyone with a knowledge to properly setup RS485/M-Bus converter from JC Elektronika?
My testing setup:
- Unipi Patron M527 with Patron Node RED OS installed and libmbus 0.8.0,
- 80 device version of RS485toMBus-XL connected to 1.3 port RS485,
- Electricity meter Inepro PRO380Mb (Addr set to 9, Bdr set to 1200).
mbus-serial-scan tool seems to find the meter:
unipi@M527-snXXX:~$ mbus-serial-scan -d -b 1200 /dev/ttymxc0 Scanning primary addresses: ... 9 [2024-06-09 09:23:07] SEND (005): 10 40 09 49 16 [2024-06-09 09:23:07] RECV (001): E5 Found a M-Bus device at address 9 ...but mbus-serial-request-data tool is not able to read response:
unipi@M527-snXXX:~$ mbus-serial-request-data-multi-reply -d -b 1200 /dev/ttymxc0 9 main: debug: sending init frame [2024-06-09 09:15:20] SEND (005): 10 40 FF 3F 16 [2024-06-09 09:15:21] SEND (005): 10 7B 09 84 16 mbus_sendrecv_request: Failed to receive M-Bus response frame. mbus_frame_print: Dumping M-Bus frame [type 0, -3 bytes]: Failed to generate XML representation of MBUS frames: M-bus data parse error.If I use M-Bus master from ENBRA (USB-MBus) CODMBUS the read tool is ok to read the meter:
unipi@M527-snXXX:~$ mbus-serial-request-data -d -b 1200 /dev/ttyUSB0 9 main: debug: sending init frame [2024-06-09 09:05:30] SEND (005): 10 40 FF 3F 16 [2024-06-09 09:05:30] SEND (005): 10 7B 09 84 16 [2024-06-09 09:05:31] RECV (081): 68 4B 4B 68 08 09 72 08 05 08 21 CD 25 01 02 2D 00 00 00 0C 04 61 77 26 00 8C 10 04 61 77 26 00 8C 20 04 00 00 00 00 1C 04 61 77 26 00 9C 10 04 61 77 26 00 9C 20 04 00 00 00 00 2C 04 00 00 00 00 AC 10 04 00 00 00 00 AC 20 04 00 00 00 00 83 16 mbus_frame_print: Dumping M-Bus frame [type 4, 81 bytes]: 68 4B 4B 68 08 09 72 08 05 08 21 CD 25 01 02 2D 00 00 00 0C 04 61 77 26 00 8C 10 04 61 77 26 00 8C 20 04 00 00 00 00 1C 04 61 77 26 00 9C 10 04 61 77 26 00 9C 20 04 00 00 00 00 2C 04 00 00 00 00 AC 10 04 00 00 00 00 AC 20 04 00 00 00 00 83 16 <MBusData> <SlaveInformation> <Id>21080508</Id> <Manufacturer>INM</Manufacturer> <Version>1</Version> <ProductName></ProductName> <Medium>Electricity</Medium> <AccessNumber>45</AccessNumber> <Status>00</Status> <Signature>0000</Signature> </SlaveInformation> <DataRecord id="0"> <Function>Instantaneous value</Function> <Unit>Energy (10 Wh)</Unit> <Value>267761</Value> <Timestamp>2024-06-09T09:05:31</Timestamp> </DataRecord> ...I would appreciate any idea what I'm doing wrong. Thanks!
-
Hi @t-kavan,
We have already encountered this, unfortunately this meter does not wait for the prescribed time and responds too quickly, so that the RS485 (transmit/receive) state in the controller does not have enough time to change.
The RS485 behaviour was modified in later versions of the debian packages. With the current OS image the PRO380-MB meter are already working.
Best regards,
Antonín Všetula - Unipi technician
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.