Modbus RTU - NeuronL503 - Mervis
-
Hi all,
I'm used to working with Codesys and I can't find my way fully around Mervis yet :)
So I am trying to read out some PPM CO2 readings from a Modbus RTU transmitter
-
Datasheet: http://downloads.epluse.com/fileadmin/data/product/ee870/BA_EE870_e.pdf
-
I'm trying to read out the CO2 fast parameter: Address: 29 + 30
It seems I can read out some values, but I have to combine them into a REAL, in Codesys I use UNION to combine both words (and swap them) into a REAL.
What is the easiest way to achieve this within Mervis?

Thank you.
-
-
Hi @OlivierP ,
you can change the byte order via MultiByte Order:
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.