    Need Some sort of Jumpstart
    11 Posts 3 Posters 4.1k Views 1 Watching
    • ntdN
      ntd
      Hi @knebb
      I developed a fistful of programs in plain C on Neuron. I just linked against libmodbus and called the loopback ModBUS server at 127.0.0.1, port 502 (hence no need to enable the EVOK service).
      If you are not familiar I can send you some code to help you getting started.
        martin_triska
        Hello @knebb, as @ntd wrote there is no need to use the Evok (which is, basically a bridge between Modbus server and several web-service interfaces). The simplest option for direct access from a C/C++ application should be the sysfs interface. Of course, a Modbus client connected to the internally running Modbus server can be used also.
        K 1 Reply Last reply
        Reply Quote 1
        • K
          knebb
          @martin_triska @ntd
          Great thanks for the hints. Using libmodbus seems to be the way I will go. Seems to be easy enough to use and is available in C. I already found the Neuron Docs regarding the coils and registers.
          If you could send me your example code sniplets? How to set the relays, read DI or set DO?
          Thanks a lot in advance! first step is done.
          /KNEBB
          ntdN 1 Reply Last reply
          • K
            knebb @martin_triska
            @martin_triska
            I checked for the sysfs, too.
            I did not see any references to the relays? How can I set relays (Neuron M103 has some) through sysfs?
            Thanks again!
            /KNEBB
            • ntdN
              ntd @knebb
              @knebb The relevant function is fieldbus_thread, that basically runs a polling loop every 20 ms. If you do not need threads, you can consider that function as main() and drop all the locking stuff (i.e. a good 50% of code in iteration).
              #include "lappaseven.h"
              #include "fieldbus.h"
              #include <errno.h>
              #include <string.h>
              #define MODBUS_ID       0
              #define AI1_ADDRESS     3
              #define DI1_ADDRESS     0
              #define DI2_ADDRESS     100
              #define DI3_ADDRESS     200
              #define DO1_ADDRESS     1
              #define DO2_ADDRESS     101
              #define DO3_ADDRESS     201
              #define AO1_ADDRESS     2
              #define VREFINT_ADDRESS 5
              #define VREF_ADDRESS    1009
              static IO image = { 0 };
              void
              fieldbus_free(modbus_t *modbus)
                  if (modbus != NULL) {
                      modbus_close(modbus);
                      modbus_free(modbus);
              modbus_t *
              fieldbus_new(void)
                  modbus_t *modbus;
                  gchar *host;
                  int port;
                  host   = g_settings_get_string(gs.settings, "modbus-host");
                  port   = g_settings_get_uint(gs.settings, "modbus-porta");
                  modbus = modbus_new_tcp(host, port);
                  if (modbus == NULL ||
                      modbus_connect(modbus) == -1 ||
                      modbus_set_slave(modbus, MODBUS_ID) == -1)
                      g_warning("Unable to initialize communication on %s:%d: %s",
                                host, port, modbus_strerror(errno));
                      fieldbus_free(modbus);
                      modbus = NULL;
                  g_free(host);
                  return modbus;
              gboolean
              fieldbus_get_ai(modbus_t *modbus)
                  uint16_t vrefint, vref, ai;
                  if (modbus_read_registers(modbus, VREFINT_ADDRESS, 1, &vrefint) == -1 ||
                      modbus_read_registers(modbus, VREF_ADDRESS, 1, &vref) == -1 ||
                      modbus_read_registers(modbus, AI1_ADDRESS, 1, &ai) == -1)
                      g_warning("fieldbus_get_ai error: %s", modbus_strerror(errno));
                      return FALSE;
                  /* Linearization to volts as described by Neuron manual, page 14.
                   * AI1vdev and AI1voffset are set to supposedly 0. */
                  image.AI1 = 3.3 * vref / vrefint * 3 * ai / 4096;
                  return TRUE;
              gboolean
              fieldbus_get_di(modbus_t *modbus)
                  uint16_t word1, word2, word3;
                  int n;
                  if (modbus_read_registers(modbus, DI1_ADDRESS, 1, &word1) == -1 ||
                      modbus_read_registers(modbus, DI2_ADDRESS, 1, &word2) == -1 ||
                      modbus_read_registers(modbus, DI3_ADDRESS, 1, &word3) == -1)
                      g_warning("fieldbus_get_di error: %s", modbus_strerror(errno));
                      return FALSE;
                  for (n = 0; n < G_N_ELEMENTS(image.DI1); ++n) {
                      image.DI1[n] = (word1 & (1 << n)) > 0;
                  for (n = 0; n < G_N_ELEMENTS(image.DI2); ++n) {
                      image.DI2[n] = (word2 & (1 << n)) > 0;
                  for (n = 0; n < G_N_ELEMENTS(image.DI3); ++n) {
                      image.DI3[n] = (word3 & (1 << n)) > 0;
                  return TRUE;
              gboolean
              fieldbus_set_do(modbus_t *modbus)
                  int n;
                  word1 = 0;
                  word2 = 0;
                  word3 = 0;
                  for (n = 0; n < G_N_ELEMENTS(image.DO1); ++n) {
                      word1 |= image.DO1[n] << n;
                  for (n = 0; n < G_N_ELEMENTS(image.DO2); ++n) {
                      word2 |= image.DO2[n] << n;
                  for (n = 0; n < G_N_ELEMENTS(image.DO3); ++n) {
                      word3 |= image.DO3[n] << n;
                  if (modbus_write_register(modbus, DO1_ADDRESS, word1) == -1 ||
                      modbus_write_register(modbus, DO2_ADDRESS, word2) == -1 ||
                      modbus_write_register(modbus, DO3_ADDRESS, word3) == -1)
                      g_warning("fieldbus_set_do error: %s", modbus_strerror(errno));
                      return FALSE;
                  return TRUE;
              gboolean
              fieldbus_set_ao(modbus_t *modbus)
                  /* Analog output must be between 0 .. 5 V, hence the division */
                  if (modbus_write_register(modbus, AO1_ADDRESS, image.AO1 / 2) == -1) {
                      g_warning("fieldbus_set_ao error: %s", modbus_strerror(errno));
                      return FALSE;
                  return TRUE;
              #if THREADING
              static gboolean
              iteration(modbus_t *modbus)
                  static gboolean workaround = FALSE;
                  gboolean AI, DI, AO, DO, quit;
                  AI = fieldbus_get_ai(modbus);
                  DI = fieldbus_get_di(modbus);
                  g_mutex_lock(&gs.fieldbus_lock);
                  AO = gs.hal.AO1 != gs.share.AO1;
                  DO = memcmp(gs.hal.DO1, gs.share.DO1, sizeof(gs.hal.DO1)) != 0 ||
                       memcmp(gs.hal.DO2, gs.share.DO2, sizeof(gs.hal.DO2)) != 0 ||
                       memcmp(gs.hal.DO3, gs.share.DO3, sizeof(gs.hal.DO3)) != 0;
                  if (DI) {
                      memcpy(gs.share.DI1, image.DI1, sizeof(image.DI1));
                      memcpy(gs.share.DI2, image.DI2, sizeof(image.DI2));
                      memcpy(gs.share.DI3, image.DI3, sizeof(image.DI3));
                  if (AI) {
                      gs.share.AI1 = image.AI1;
                  if (DO) {
                      memcpy(image.DO1, gs.share.DO1, sizeof(image.DO1));
                      memcpy(image.DO2, gs.share.DO2, sizeof(image.DO2));
                      memcpy(image.DO3, gs.share.DO3, sizeof(image.DO3));
                  if (AO) {
                      image.AO1 = gs.share.AO1;
                  quit = gs.quit;
                  g_mutex_unlock(&gs.fieldbus_lock);
                  if (DI) {
                      memcpy(gs.hal.DI1, image.DI1, sizeof(image.DI1));
                      memcpy(gs.hal.DI2, image.DI2, sizeof(image.DI2));
                      memcpy(gs.hal.DI3, image.DI3, sizeof(image.DI3));
                  if (DO && fieldbus_set_do(modbus)) {
                      memcpy(gs.hal.DO1, image.DO1, sizeof(image.DO1));
                      memcpy(gs.hal.DO2, image.DO2, sizeof(image.DO2));
                      memcpy(gs.hal.DO3, image.DO3, sizeof(image.DO3));
                  /* XXX Workaround for a unknown fieldbus error that seems to reset the
                   *     analog output: if this happens, force a AO1 refresh cycle */
                  if (! DI || ! AI) {
                      workaround = TRUE;
                  AO = AO || workaround;
                  if (AO && fieldbus_set_ao(modbus)) {
                      g_debug("AO1 set to %d", image.AO1);
                      gs.hal.AO1 = image.AO1;
                      workaround = FALSE;
                  return ! quit;
              gpointer
              fieldbus_thread(gpointer user_data)
                  modbus_t *modbus;
                  gint64 period, scan, now, span, limit;
                  if (gs.dry_run) {
                      return NULL;
                  modbus = fieldbus_new();
                  if (modbus == NULL) {
                      return NULL;
                  period = g_settings_get_uint(gs.settings, "periodo");
                  if (period == 0) {
                      g_warning("Period set to 0: fallback to 20000");
                      period = 20000;
                  scan  = g_get_monotonic_time();
                  limit = period;
                  do {
                      g_main_context_invoke_full(NULL, G_PRIORITY_HIGH,
                                                 cycle_iteration, NULL, NULL);
                      now  = g_get_monotonic_time();
                      span = now - scan;
                      if (span > limit) {
                          limit = span;
                          g_warning("Period exceeded: %.3f ms > %.3f ms" ,
                                    limit / 1000., period / 1000.);
                      scan += period;
                      if (now < scan) {
                          g_usleep(scan - now);
                  } while (iteration(modbus));
                  return NULL;
              #endif
              The IO struct is just an image of the I/O status:
              typedef struct {
                  uint8_t         DI1[4];
                  uint8_t         DI2[16];
                  uint8_t         DI3[16];
                  uint8_t         DO1[4];
                  uint8_t         DO2[14];
                  uint8_t         DO3[14];
                  double          AI1;
                  uint16_t        AO1;
              } IO;
              • K
                knebb @ntd
                @ntd Thanks a lot! I think I got it so far. The adresses of the devices you got from Neuron documentation I assume?
                Only one question left so far. If I want to write the current state of the relay I would use (according to doc):
                //int modbus_write_bit(modbus_t *ctx, int addr, int status);
                errlvl=modbus_write_bit(modbus_handle, 100, status);
                I am unsure about the "status". This means I will enable or disable the bit and therefore switching the relay, right?
                Ok, how about reading the DI 2.1?
                Would I use the following?
                //int modbus_read_bits(modbus_t *ctx, int addr, int nb, uint8_t *dest);
                errlvl=modbus_read_bits(modbus_handle, 108, nb, *dest);
                Here I have no clue for what I would need the nb... does it mean it will read nb bits? To be stored in nb*dest? I would always use the value 1, wouldn't I? If using 2 it would return the value of the second DI 2.2 in the second bit, correct?
                /KNEBB
                • K
                  knebb
                  for reference purposes even though some questions are still unanswered.
                  I was able to set my relays as expected with the following code:
                  #include <modbus/modbus.h>
                  #include <errno.h>
                  #include <stdio.h>
                  #include <stdlib.h>
                  #include <string.h>
                  #include <unistd.h>
                  void main()
                  modbus_t *modbusglob;
                  int errlvl;
                  void fieldbus_free(modbus_t *modbus)
                    return;
                  modbus_t *fieldbus_new(void)
                      int err;
                      modbus_t *modbus;
                      char host[15];
                      int port;
                  // Need to use IP as it does not resolve DNS Names to IPs
                      strcpy(host,"127.0.0.1");
                      port   = 502;
                      if (modbus == NULL )
                           printf("modbus is NULL\n");
                          exit (55);
                       err = modbus_connect(modbus);
                       if (err  == -1)
                          printf("modbus_connect, %s",modbus_strerror(errno));
                          exit (55);
                       err=modbus_set_slave(modbus, 0);
                       if(  err == -1)
                          printf("modbus_set_slave, %s",modbus_strerror(errno));
                          modbus = NULL;
                          exit (55);
                      return modbus;
                  modbusglob=fieldbus_new();
                  printf("ON\n");
                  // Using fixed address of 100 here for first relay (M103), relay 2.2 ist 101 and so on.
                  // Using TRUE as synonym for HIGH or ON
                  errlvl=modbus_write_bit(modbusglob, 100, TRUE);
                  // Just for demo purposes- keep the relay on for 10 seconds
                  sleep(10);
                  printf("OFF\n");
                  errlvl=modbus_write_bit(modbusglob, 100, FALSE);
                  fieldbus_free(modbusglob);
                  • ntdN
                    ntd @knebb
                    @knebb said in Need Some sort of Jumpstart:
                    According to the documentation, status is the new value of the output and can be TRUE (to enable it) or FALSE (to disable it).
                    Yes to all. This mimics the behavior of the underlying protocol: ModBUS has a Read coils function but does not have Read single coil. You can easily provide your own macro for that, if you really want:
                    #define read_bit(bus,addr,dst) modbus_read_bits((bus),(addr),1,(dst))
                    Reply Quote 1
                    • K
                      knebb @ntd
                      @ntd
                      Sorry to bother you. I think I got it finally!
                      Using modbus_read_bits will read nb bits and write (according to the state) 0 or 1 into dst[0]...dst[nb].
                      I had thought when reading 4 bits it will write the first state into the first bit of dst, second into the second and so on.
                      But no, it writes the state as 0 or 1 into each of the uint8_t .
                      I was successfull in reading RO2.8 and DI2.1 together with
                      int nb,i;
                      uint8_t dst[2];
                      nb=2;
                      modbus_read_bits(modbus,107,nb,dst);
                      for (i=0;i<nb;i++)
                        if (dst[i] != 0)
                          printf("Bit %d is %u\n",i,dst[i]);
                        } else {
                      And in case RO2.8 is on an DI2.1 is off I will get:
                      Bit 0 is 1
                      Bit 1 is 0
                      Similar this would apply to modbus_read_register();
                      Holy sh**, I think I really got it now!
                      Thanks for your patience!
                      /KNEBB
                      • ntdN
                        ntd @knebb
                        Or, using semantic constants, as FALSE and TRUE.
                        Directly using bits would be really slow and error prone (and a nightmare for language bindings).