    30645
      Boy Lenssen last edited by
      the run led is blinking slowly, so there is no communication.
      Can you tell me or point me to somewhere where it describes step-by-step what to do to connect the extension module? I have no idea what to do with the dip switches and if I set them, what do I need to do to configure them? I'm quite novice on this. I see 8 DIP switches and have them set to 0 atm.
      I also se an 'on/off' dipswitch next to the rs485 connection on the Neuron. That needs to be put to 'on'?
        TomasKnot @Boy Lenssen last edited by
        @Boy-Lenssen
        Do you see the TX and RX leds blinking? That's the most part important. Ideally if you could mention the status of all four of them.
        The dip switches are used to set speed, parity and address, as per the descriptions on top. They need to be set to 19200, N, and e.g. 1 (you will need to set the address to 1 in the configuration file as well).
        The switch on the Neuron (there is another equivalent switch on the extension marked END) is used to turn on termination resistors. These are used to make the line more resistant to noise, and you can ignore it for now.
          I have no idea how to set the dipswitches to 19200 N and 1. They are just 8 "toggles".
          The TX / RX on both xS40 and Neuron don't do anything. I have all dipswitches to 'off'.
          The run led is blinking every 2 seconds. Power led is on ofcourse :)
          Do I need a minimum version of the EVOK service installed on the system?
            Does the file /dev/extcomm/0/0 exist? Try changing it to /dev/ttyNS0 if it does not.
            If the TX light on the Neuron doesn't turn on it means there is no communication at all.
            I'm not quite clear on what you by having an EVOK service installed.
              Boy Lenssen last edited by Boy Lenssen
              root@raspberrypi:/home/pi# ls /dev/extcomm/
              0 1
              root@raspberrypi:/home/pi# ls /dev/extcomm/0/0
              /dev/extcomm/0/0
              seems to exists.
              With evok service, I mean the latest EVOK software from Github.
              Is it correct to have the RS-485-A connected to the RS-485-A of the xS40 and the B's too?
              Can you point me to the page in the documentation someone should follow when adding an Extension unit?
                @Boy-Lenssen
                It should be connected A-A, B-B, yes, the other way around will not work. The documentation, such as it is, is available from https://evok-6.api-docs.io/1.05/cgct7pncnqf9fper7/introduction, but it's targeted at users with prior experience with serial lines.
                I would use the following settings myself:
                [EXTENSION_1]
                device_name = xS40                                              ; Mandatory
                neuron_uart_circuit = 1_01                             ; Optional, allows associating extensions with specific Neuron UART-over-Modbus ports (not possible for non-Modbus UART ports, e.g. /dev/ttyUSB0 or /dev/ttyS0)
                ;allow_register_access = True                   ; Optional, False default, is mandatory with third-party devices
                address = 1                                                   ; Optional, 15 default
                scan_frequency = 10                                     ; Optional, 1 default
                ;scan_enabled = True                                    ; Optional, True default
                baud_rate = 19200                                              ; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN
                parity = N                                                             ; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN
                stop_bits = 1
                Then connect the line and set the dip switches to the following positions:
                (apologies for the rotation)
                I have verified that these settings work with a fresh EVOK install, with the device in the photo.
                  Boy Lenssen @TomasKnot last edited by Boy Lenssen
                  @TomasKnot Hey, thanks a lot! I got it working now. I think I might have forgotten to remove the semi-colon before [EXTENSION 1] :face_palm:
                  Now the Rx light on the xS40 is now constant on, the run light is still going on / off every 2 seconds. On the neuron, the TX flashes on very swiftly.
                  I don't see the extra in/outputs when I go to my ip address. How can I read / write the ports now? I thought I would get some ports like 4_05 or so...
                  I tried something like this: http://192.168.1.16/rest/relay/UART_1_2 but gives a 500 error
                    TomasKnot @Boy Lenssen last edited by TomasKnot
                    @Boy-Lenssen
                    This looks like an address problem perhaps, or possibly some other communication setting issue. Did you try to set it up as I have above? At least for testing purposes.
                    If you did do so then it may be another issue, possibly with a hardware definition; if you can run the following commands while connected to the Neuron and paste the output here we may find the problem.
                    sudo su
                    systemctl stop evok
                    python /opt/evok.py
                      @TomasKnot
                      Hi! As far as I can see, I set it up exactly the way you said above...
                      This is the output:
                      The /get/all call is my software requesting the status of all in and outputs, you can ignore that.
                      root@raspberrypi:/home/pi# python /opt/evok/evok.py
                      [I 180522 06:56:19 config:63] eprom: UniPi Neuron L203 version: 1.0 serial: 0x51
                      [I 180522 06:56:19 evok:1634] Starting using config file /etc/evok.conf
                      [I 180522 06:56:20 config:75] YAML Definition loaded: L30x.yaml, type: 3, definition count 0
                      [I 180522 06:56:20 config:75] YAML Definition loaded: M20x.yaml, type: 3, definition count 1
                      [I 180522 06:56:20 config:75] YAML Definition loaded: M50x.yaml, type: 3, definition count 2
                      [I 180522 06:56:20 config:75] YAML Definition loaded: xS40.yaml, type: 3, definition count 3
                      [I 180522 06:56:20 config:75] YAML Definition loaded: M30x.yaml, type: 3, definition count 4
                      [I 180522 06:56:20 config:75] YAML Definition loaded: L40x.yaml, type: 3, definition count 5
                      [I 180522 06:56:20 config:75] YAML Definition loaded: S10x.yaml, type: 3, definition count 6
                      [I 180522 06:56:21 config:75] YAML Definition loaded: L51x.yaml, type: 3, definition count 7
                      [I 180522 06:56:21 config:75] YAML Definition loaded: CUSTOM MODBUS DEVICE.yaml, type: 3, definition count 8
                      [I 180522 06:56:21 config:75] YAML Definition loaded: L50x.yaml, type: 3, definition count 9
                      [I 180522 06:56:21 config:75] YAML Definition loaded: xS30.yaml, type: 3, definition count 10
                      [I 180522 06:56:21 config:75] YAML Definition loaded: xS10.yaml, type: 3, definition count 11
                      [I 180522 06:56:21 config:75] YAML Definition loaded: M40x.yaml, type: 3, definition count 12
                      [I 180522 06:56:21 config:75] YAML Definition loaded: M10x.yaml, type: 3, definition count 13
                      [I 180522 06:56:21 config:75] YAML Definition loaded: M60x.yaml, type: 3, definition count 14
                      [I 180522 06:56:22 config:75] YAML Definition loaded: L20x.yaml, type: 3, definition count 15
                      [I 180522 06:56:22 config:75] YAML Definition loaded: xS50.yaml, type: 3, definition count 16
                      [I 180522 06:56:22 config:75] YAML Definition loaded: evok-alias.yaml, type: 2, definition count 0
                      [I 180522 06:56:22 evok:1698] HTTP server listening on port: 8080
                      [I 180522 06:56:22 modbusclient_tornado:122] SPI client started
                      [I 180522 06:56:22 modbusclient_rs485:333] UART client started
                      [I 180522 06:56:22 neuron:268] Reading the UART board on Modbus address 1
                      [D 180522 06:56:22 owclient:377] Entering 1wire loop
                      [I 180522 06:56:22 web:2064] 101 GET /ws (::1) 3.76ms
                      [D 180522 06:56:22 evok:158] New WebSocket client connected
                      [I 180522 06:56:22 neuron:157] Reading SPI boards
                      [I 180522 06:56:22 web:2064] 200 GET /rest/all (::1) 3.10ms
                      [I 180522 06:56:22 config:351] Alias loaded: <neuron.Relay object at 0x75f42690> al_lights_kitchen
                      [I 180522 06:56:22 config:351] Alias loaded: <neuron.Relay object at 0x75f42650> al_lights_bedroom
                      [I 180522 06:56:24 web:2064] 101 GET /ws (::1) 1.79ms
                      [D 180522 06:56:24 evok:158] New WebSocket client connected
                      [I 180522 06:56:24 web:2064] 200 GET /rest/all (::1) 7.07ms
                      [E 180522 06:56:28 neuron:290] No cached value of register 1018 on unit 1 - read error
                            File "/opt/evok/neuron.py", line 283, in readboards
                              yield board.parse_definition(self.hw_dict, 1)
                            File "/usr/local/lib/python2.7/dist-packages/tornado/gen.py", line 1055, in run
                              value = future.result()
                            File "/usr/local/lib/python2.7/dist-packages/tornado/concurrent.py", line 238, in result
                            File "/opt/evok/neuron.py", line 409, in parse_definition
                              regpolarity=m_feature['polar_reg'], legacy_mode=self.legacy_mode)
                            File "/opt/evok/neuron.py", line 1309, in __init__
                              curr_ds = self.arm.neuron.modbus_cache_map.get_register(1, self.regmode, unit=self.arm.modbus_address)[0]
                            File "/opt/evok/neuron.py", line 48, in get_register
                          Exception: No cached value of register 1018 on unit 1 - read error
                      ^C[I 180522 06:56:39 evok:1773] Shutting down
                        It looks like the system can't connect to the device - does the RX light on the Neuron (not the extension) flash at all? It should be roughly simultaneous with the TX light.
                        From the log it looks like there's no valid communication with the extension unfortunately, so something must be wrong with the connection.
                        • U
                          unix last edited by
                          Hi
                          this day after a reboot i have the same error message and the link from S103G to xs50 not working only one short blink from the modbus rx/tx
                          reinstall evok and fresh image not working.
                          root@pimatic:~# /usr/bin/python /opt/evok/evok.py
                          [I 180524 19:27:48 config:63] eprom: UniPi Neuron S103 version: 1.0 serial: 0xd
                          [I 180524 19:27:48 evok:1634] Starting using config file /etc/evok.conf
                          [I 180524 19:27:48 config:75] YAML Definition loaded: M20x.yaml, type: 3, definition count 0
                          [I 180524 19:27:48 config:75] YAML Definition loaded: xS40.yaml, type: 3, definition count 1
                          [I 180524 19:27:48 config:75] YAML Definition loaded: M30x.yaml, type: 3, definition count 2
                          [I 180524 19:27:48 config:75] YAML Definition loaded: L40x.yaml, type: 3, definition count 3
                          [I 180524 19:27:49 config:75] YAML Definition loaded: L50x.yaml, type: 3, definition count 4
                          [I 180524 19:27:49 config:75] YAML Definition loaded: M50x.yaml, type: 3, definition count 5
                          [I 180524 19:27:49 config:75] YAML Definition loaded: M40x.yaml, type: 3, definition count 6
                          [I 180524 19:27:49 config:75] YAML Definition loaded: L30x.yaml, type: 3, definition count 7
                          [I 180524 19:27:49 config:75] YAML Definition loaded: xS50.yaml, type: 3, definition count 8
                          [I 180524 19:27:49 config:75] YAML Definition loaded: CUSTOM MODBUS DEVICE.yaml, type: 3, definition count 9
                          [I 180524 19:27:50 config:75] YAML Definition loaded: M60x.yaml, type: 3, definition count 10
                          [I 180524 19:27:50 config:75] YAML Definition loaded: L20x.yaml, type: 3, definition count 11
                          [I 180524 19:27:50 config:75] YAML Definition loaded: S10x.yaml, type: 3, definition count 12
                          [I 180524 19:27:50 config:75] YAML Definition loaded: xS30.yaml, type: 3, definition count 13
                          [I 180524 19:27:50 config:75] YAML Definition loaded: M10x.yaml, type: 3, definition count 14
                          [I 180524 19:27:51 config:75] YAML Definition loaded: L51x.yaml, type: 3, definition count 15
                          [I 180524 19:27:51 config:75] YAML Definition loaded: xS10.yaml, type: 3, definition count 16
                          [I 180524 19:27:51 config:75] YAML Definition loaded: DALI.yaml, type: 3, definition count 17
                          [I 180524 19:27:51 config:75] YAML Definition loaded: evok-alias.yaml, type: 2, definition count 0
                          [I 180524 19:27:51 evok:1698] HTTP server listening on port: 8080
                          [I 180524 19:27:51 modbusclient_tornado:122] SPI client started
                          [I 180524 19:27:51 modbusclient_rs485:333] UART client started
                          [I 180524 19:27:51 neuron:268] Reading the UART board on Modbus address 15
                          [I 180524 19:27:51 neuron:157] Reading SPI boards
                          [D 180524 19:27:51 owclient:377] Entering 1wire loop
                          [I 180524 19:27:51 neuron:172] No board on SPI 2
                          [E 180524 19:27:51 neuron:290] 'NoneType' object has no attribute 'get_register'
                                File "/opt/evok/neuron.py", line 561, in parse_definition
                                  self.parse_feature(m_feature, board_id)
                                File "/opt/evok/neuron.py", line 546, in parse_feature
                                  self.parse_feature_ao(max_count, m_feature, board_id)
                                File "/opt/evok/neuron.py", line 478, in parse_feature_ao
                                  dev_id=self.dev_id, major_group=m_feature['major_group'], legacy_mode=self.legacy_mode)
                                File "/opt/evok/neuron.py", line 1777, in __init__
                                  self.offset = (uint16_to_int(self.arm.neuron.modbus_cache_map.get_register(1, self.regcal + 1, unit=self.arm.modbus_address)[0]) / 10000.0)
                              AttributeError: 'NoneType' object has no attribute 'get_register'
                          [I 180524 19:27:51 neuron:172] No board on SPI 3
                          [I 180524 19:27:51 config:351] Alias loaded: <neuron.Relay object at 0x7600dc70> al_lights_kitchen
                          [I 180524 19:27:51 config:351] Alias loaded: <neuron.Relay object at 0x7600df50> al_lights_bedroom
                          Regards
                            alydersen last edited by
                            I have this exact same issue as "unix", both with the master branch and 2.0.6. Anyone that came up with a solution?
                              Hi @alydersen!
                              Do you also have the xS50 and S103G models? The error is simply a generic error indicating that no data from the device is available to EVOK in its cache.
                              It can be caused by wrong parity, bitcount or address settings, as well as potentially any other issues which break the communication.
                              By far the most crucial LED indicator is the RX LED light on the master Neuron unit - does it light at all? If not it means that no response has been sent on the bus, which means that there is no data received on the underlying hardware - much less EVOK itself.
                              Please see below, apologies
                                @alydersen
                                It looks like there has been a recent bug in EVOK which caused the hardware definitions to be parsed incorrectly. What I said above does stand, but the error is a software bug on our part.
                                You will need to download the release 2.0.7 in order to fix the problems you are seeing. The source of the error is a missing condition which causes UART hw_definitions to break, though only some of the time.
                                  Thanks @TomasKnot - will try it out
                                    @TomasKnot That did it - thanks again
                                      @tomasknot Sorry for the late response! I had a different project that needed my attention.
                                      The RX light of the extension is constant on.
                                      the TX light of the Neuron flashes. The RX light doesn't do anything.
                                      Hope we can figure this out, as I got told we need to get this working soon, hopefully this week...
                                      This is the config:
                                      global_id = 1							; Mandatory, REQUIRED TO BE UNIQUE
                                      allow_register_access = False 			; Optional, False default
                                      scan_frequency = 10						; Optional, 10 default
                                      ; Below you can find examples for connecting devices over UART; first example is a Neuron extension while the second is a custom third-party device
                                      ; Devices sharing a port use the port settings of the first device on that port (baud rate, parity, stopbits)
                                      ; !!!Note that device_name has to match a filename in the /etc/hw_definitions directory!!! See /etc/hw_definitions/DOMAT MMIO.yaml for an example
                                      [EXTENSION_1]
                                      ;neuron_uart_circuit = 1_01				; Optional, allows associating extensions with specific Neuron UART-over-Modbus ports (not possible for non-Modbus UART ports, e.g. /dev/ttyUSB0 or /dev/ttyS0)
                                      address = 1							; Optional, 1 default
                                      ;scan_frequency = 10 					; Optional, 10 default
                                      stop_bits = 1							; Optional, NEEDS UNIPI IMAGE TO WORK! USE API TO CONFIGURE UART MANUALLY IF USING STANDARD RASPBIAN
                                      This is the config on the xS40:
                                      https://imgur.com/a/Af53afq
                                      What can I do to help troubleshoot further?
                                        @Boy-Lenssen
                                        That definitely looks like a problem with UART settings, as no RX on the Neuron indicates that there is no response from the extension, not even an error response (which is what occurs when e.g. reading wrong registers or issuing invalid commands).
                                        Could you try using the latest version of EVOK? It is possible that some recent changes will help fix the problems you are seeing.
                                          @tomasknot I'm sorry, I'm already running 2.0.7. Forgot to mention.
                                          still getting this:
                                                File "/opt/evok/neuron.py", line 289, in readboards
                                                File "/opt/evok/neuron.py", line 571, in parse_definition
                                                File "/opt/evok/neuron.py", line 547, in parse_feature
                                                  self.parse_feature_di(max_count, m_feature, board_id)
                                                File "/opt/evok/neuron.py", line 413, in parse_feature_di
                                                File "/opt/evok/neuron.py", line 1394, in __init__
                                                File "/opt/evok/neuron.py", line 50, in get_register
                                            Boy Lenssen @Boy Lenssen last edited by Boy Lenssen
                                            @TomasKnot do you have any pointers for me? I really need to get this working for a customer :\
                                            Any way I can supply you with more info to test it?
                                            Maybe you can create an SD card image file of the configuration that works for you so I can try it out?