      I have some real values to send via modbus from Mervis.
      Since REAL take 4 bytes, REAL should take two registers.
      How can I combine the two registers values to make one real value in C program ?

      regards.

      1 Reply Last reply Reply Quote 0
      • G
        Giamba last edited by

        I find it!

        Modbus data order: 1234.
        Example:
        In C program header:

        typedef unsigned long DWORD;
        typedef unsigned short WORD;
        union u_DWORD_TO_FLOAT{
            DWORD i;
            float f;
        };
        

        and in the code:

        union u_DWORD_TO_FLOAT AI01;
        ...
        AI01.i = (mb_mapping->tab_registers[20] << 16) + mb_mapping->tab_registers[21];
        float value = AI01.f;
        

        Hope this help someone !