      Hi,

      I have tested to read the Kamstrup 803 meter on the Patron M527 via Modbus.

      However, I don't get any results from mbpoll.

      root@M527-sn60:~# mbpoll /dev/extcomm/0/1 -m rtu -P none -d 8 -s 1 -b 19200 -a 44
      mbpoll 1.4-12 - FieldTalk(tm) Modbus(R) Master Simulator
      Copyright © 2015-2019 Pascal JEAN, https://github.com/epsilonrt/mbpoll
      This program comes with ABSOLUTELY NO WARRANTY.
      This is free software, and you are welcome to redistribute it
      under certain conditions; type 'mbpoll -w' for details.
      
      Protocol configuration: Modbus RTU
      Slave configuration...: address = [44]
                              start reference = 1, count = 1
      Communication.........: /dev/extcomm/0/1,      19200-8N1 
                              t/o 1.00 s, poll rate 1000 ms
      Data type.............: 16-bit register, output (holding) register table
      
      -- Polling slave 44... Ctrl-C to stop)
      Read output (holding) register failed: Connection timed out
      -- Polling slave 44... Ctrl-C to stop)
      Read output (holding) register failed: Connection timed out
      -- Polling slave 44... Ctrl-C to stop)
      Read output (holding) register failed: Connection timed out
      

      Same result on mbpoll /dev/extcomm/0/0 -m rtu -P none -d 8 -s 1 -b 19200 -a 44

      Br,
      Vesa

      1 Reply Last reply Reply Quote 0
      • A
        AVsetula administrators last edited by AVsetula

        Hello Vesa,

        Only some Patron ports are available using the deprecated /dev/extcomm/Y/X notation.
        I recommend using the ports from the table in this article: Patron serial port mapping

        To verify communication with all our Modbus devices, I recommend asking the holding register 1003, which is available for all Modbus devices Unipi and whith contains a unique identifier, according to which the device can also be recognized.

        Best regards,
        Antonin

        Vesa Kauppinen 1 Reply Last reply Reply Quote 0
        • Vesa Kauppinen
          Vesa Kauppinen @AVsetula last edited by

          Hi,

          How can i ask the holding register 1003 with mbpoll?

          @AVsetula said in Reading the ModBus bus with the Patron:

          To verify communication with all our Modbus devices, I recommend asking the holding register 1003, which is available for all Modbus devices Unipi and whith contains a unique identifier, according to which the device can also be recognized.

          Thank you!

          /Vesa

          A 1 Reply Last reply Reply Quote 0
          • A
            AVsetula administrators @Vesa Kauppinen last edited by

            Hi @Vesa-Kauppinen,

            From Unipi Patron I/O boards by:

            • Section 1: mbpoll -m tcp 127.0.0.1 -a 0 -0 -1 -r 1003 -p 502
            • Section 2: mbpoll -m tcp 127.0.0.1 -a 0 -0 -1 -r 1103 -p 502
            • Section 3: mbpoll -m tcp 127.0.0.1 -a 0 -0 -1 -r 1203 -p 502

            And from Unipi Extension using ttyNS0 port:

            • mbpoll -m rtu /dev/ttyNS0 -b 19200 -P none -0 -1 -r 1003 -a 15

            Best regards,
            Antonin

            1 Reply Last reply Reply Quote 0