Reading the ModBus bus with the Patron



  • Hi,

    I have tested to read the Kamstrup 803 meter on the Patron M527 via Modbus.

    However, I don't get any results from mbpoll.

    root@M527-sn60:~# mbpoll /dev/extcomm/0/1 -m rtu -P none -d 8 -s 1 -b 19200 -a 44
    mbpoll 1.4-12 - FieldTalk(tm) Modbus(R) Master Simulator
    Copyright © 2015-2019 Pascal JEAN, https://github.com/epsilonrt/mbpoll
    This program comes with ABSOLUTELY NO WARRANTY.
    This is free software, and you are welcome to redistribute it
    under certain conditions; type 'mbpoll -w' for details.
    
    Protocol configuration: Modbus RTU
    Slave configuration...: address = [44]
                            start reference = 1, count = 1
    Communication.........: /dev/extcomm/0/1,      19200-8N1 
                            t/o 1.00 s, poll rate 1000 ms
    Data type.............: 16-bit register, output (holding) register table
    
    -- Polling slave 44... Ctrl-C to stop)
    Read output (holding) register failed: Connection timed out
    -- Polling slave 44... Ctrl-C to stop)
    Read output (holding) register failed: Connection timed out
    -- Polling slave 44... Ctrl-C to stop)
    Read output (holding) register failed: Connection timed out
    

    Same result on mbpoll /dev/extcomm/0/0 -m rtu -P none -d 8 -s 1 -b 19200 -a 44

    Br,
    Vesa


  • administrators

    Hello Vesa,

    Only some Patron ports are available using the deprecated /dev/extcomm/Y/X notation.
    I recommend using the ports from the table in this article: Patron serial port mapping

    To verify communication with all our Modbus devices, I recommend asking the holding register 1003, which is available for all Modbus devices Unipi and whith contains a unique identifier, according to which the device can also be recognized.

    Best regards,
    Antonin



  • Hi,

    How can i ask the holding register 1003 with mbpoll?

    @AVsetula said in Reading the ModBus bus with the Patron:

    To verify communication with all our Modbus devices, I recommend asking the holding register 1003, which is available for all Modbus devices Unipi and whith contains a unique identifier, according to which the device can also be recognized.

    Thank you!

    /Vesa