    • SorakCz
      SorakCz last edited by

      Hi do you have some manual how I can connect more Modbus extensions? I have xS40 and it works fine with my M303. But when I connect another xS40 I cannot connect it via Modbus. There is no connection. I try sett up addresses on pins, setup Mervis, but LED diodes for connection are off.

      T 1 Reply Last reply Reply Quote 0
      • T
        tomas_hora administrators @SorakCz last edited by

        @SorakCz Baudrate and parity have to be same for the whole bus but addresses have to be different.

        If you have address 0 configured via DIP switches, then the Extensions are using SW address (which can be changed via modbus registers). If you use any other addres via DIP switches, then the DIP switch configuration is also used for baudrate and parity.

        So: Decide which baudrate and parity you want to use (eg, start with 9600, N), configure it in Mervis and on both extensions, and select different addresses. Also do not forget to set address of extensions in Mervis.

        1 Reply Last reply Reply Quote 0
        • SorakCz
          SorakCz last edited by

          i think I have all setted. I changed address on the extensions, restart extension, upload program and it dont work.
          0_1521393606390_Screenshot_18_03_2018__18_16.png
          0_1521393614041_Screenshot_18_03_2018__18_16_2.png
          0_1521393621632_Screenshot_18_03_2018__18_17_3.png
          0_1521393981310_IMG_1745.JPG
          0_1521393991299_IMG_4908.JPG
          0_1521393998734_IMG_6377.JPG

          T 1 Reply Last reply Reply Quote 0
          • T
            tomas_hora administrators @SorakCz last edited by

            @SorakCz The extensions are configured to use Even parity but in the IDE, the parity is None. Those have to be the same too. Also, make sure to power cycle the extensions after you make a change in the DIP switch configuration.

            1 Reply Last reply Reply Quote 0
            • SorakCz
              SorakCz last edited by SorakCz

              Parity is pin 8? I will try it. What is better? Parity no or yes?

              Thank You

              T 1 Reply Last reply Reply Quote 0
              • T
                tomas_hora administrators @SorakCz last edited by

                @SorakCz Yes, its pin 8. It depends on the application. Parity helps to detect an error in a word on the line. Its either None(disabled) or Even in this case...

                1 Reply Last reply Reply Quote 0
                • SorakCz
                  SorakCz last edited by

                  Thank you Tomas, it was very helpful. Now it working. I only switch off parity on external modules and communication started :-)

                  1 Reply Last reply Reply Quote 0