      I have been trying to connect PT1000 to Neuron S103 AO or AI without success.

      Resistance to temperature conversion has been chosen, also PT1000 is selected.

      Neuron S10x_AO_1 resulting in PLC value of -246.8609 etc..

      Tried following youtube tutorial with no success. Should I connect the PT1000 to AI or AO? I bet if I connect resistor to ao or ai, it still shows the same.

      Any ideas?

      T 1 Reply Last reply Reply Quote 0
      • T
        tomas_hora administrators @Iogo last edited by

        @Iogo Resistance measurement on S103 is available only on Analog Output (even though it sounds a bit wierd). You have to connect the sensor between AO and AGND. Did you follow the chapetr 2.8.2.1Analog Outputof group 1 (Alternatively Resistance Analog Input–Pt1000)?

        1 Reply Last reply Reply Quote 0
        • I
          Iogo last edited by

          Well, at first, i thought it would do these all connections internally after selection has been done with the AO/AI channel to measure resistance and just put it directly to a variable, which would have been easy.. Then I tried the function block, but as you can see..nothing

          0_1509017111485_aoi module.jpg

          T 1 Reply Last reply Reply Quote 0
          • T
            tomas_hora administrators @Iogo last edited by

            @Iogo It seems that the measured resistance is really too small = 9Ω. Is it really Pt1000? And do you really have it connected?

            1 Reply Last reply Reply Quote 0
            • T
              tomas_hora administrators last edited by

              Btw what are the AO_moed and AO_1 variables? Are they mapped to the HW? It should be like like this. (We might need to update the documentation)
              0_1509024911409_neuron_resistance.png

              1 Reply Last reply Reply Quote 0
              • I
                Iogo last edited by

                They are mapped to hw, although the name does not imply that. Exactly as in your example. Did not get it to work, so I decided to add a modbus device, 4 channel analog output module and take the pt1000 temperatures through another modbus device...seemed easier way to go =)