Problem recognition 1w-Wire
-
I see.
But if I have to reformat the schema and let it come back virgin how can I do it? -
Page 26 of the manual
Set the PLC to Commissioning mode –Right click on the PLC icon in Solution Explorer and choose PLC Operation→ Commissioning mode
-
@zorro_66
thank you -
Goodbye to everyone .. I finally finally managed to recognize the 1-Wire basic temperature sensor of the PLC .. it works properly ..
But now I need a help ..
I also bought two sensors of the UNICA Wire Sensor (temperature-humidity and light sensor) all in one.
The problem is how to connect it .. I have two photos to let you know better.
Virtually I connected to terminal 5 i + 5V, to 6 the DATA, 7 empty, 8 GND.
I connected it to the Wire port I tried to make the recognition but with a negative result .. I also attach the screen of how I inserted the device in the Mervis..HO performed the same procedure for the 1-Wire sensor .. -
@TriathletC Please check the pin map of the RJ45: https://www.unipi.technology/hardware_documentation/1-wire-network-46
The wiring seems OK, but you have to wire at also both data lines to the sensor, or you break the topology.
Also, do not strip the end of cables when you make the RJ45 connector. The connector cuts the plastic foil of the cable when you press it with the crimping tool. If you strip the cables before, the cables can touch each other which could cause shortcut....
-
So from what you tell me I have to bring another thread and jump to the DQ. right?
-
@TriathletC Correct
-
@tomas_hora
Thanks Thoma ... you were right I wore everything as you said and it works correctly .. so I need an info .. how do I parameterize the UR%? -
@TriathletC You are welcome... But now I do not understand. Could you describe it better please?
-
@tomas_hora
I do not know how to configure correctly so that I can read the relative uimness on the mervis I attach to the screens. -
@TriathletC Try to use FUPLA block called 'unica_u1wt'.
-
@David SO?
-
Yes, that it should work.