      CKB last edited by

      Hi,

      could you please have a look at my configuration? Every time I connect one EMO-R8 to the unipi it creates a fault - so that relays will change to red in debug mode and unipi stops any switching activities.

      I set the one and only EMO-R8 to this parameters within Mervis:
      0_1499446018686_upload-2b639ea2-030e-41fb-9eb6-7ce5adb2ca04

      The jumper on the extension board is configured to
      A0=1 => 33 Dec
      A1=0
      A2=0

      Where's the fault?

      Thanks

      C 1 Reply Last reply Reply Quote 0
      • C
        CKB @CKB last edited by

        No idea?

        T 1 Reply Last reply Reply Quote 0
        • T
          tomas_hora administrators @CKB last edited by

          @CKB Did you power-cycle the EMO-R8 after the address is set? Do you have the possibility to connect to the ssh of UniPi? If yes, user is root and password is unipi

          Then issue the following command while the EMO-R8 is connected and paste the output here, please.

          i2cdetect -y 1
          

          There might also be an issue with the cable but all cables are tested before shipment..

          C 1 Reply Last reply Reply Quote 0
          • C
            CKB @tomas_hora last edited by

            @tomas_hora

            here it is: 0_1499872688381_upload-47522c44-3960-4042-b54e-4e14b56649f4

            T 1 Reply Last reply Reply Quote 0
            • T
              tomas_hora administrators @CKB last edited by

              @CKB Have you tried multiple times if it is always like this? And how does it look when EMO-R8 is disconnected? Do you have the possibility to check the I2C cable or make a new one?

              C 1 Reply Last reply Reply Quote 0
              • C
                CKB @tomas_hora last edited by

                @tomas_hora

                Hi Tomas,

                I found the fault- a Rj12 cable was defect. I connected all my I2C devices stepwise in debug mode and I could see when the relays changed from grey to red background colour. Crazy...I thought that these kind of production faults don't exist nowadays...
                Can you send me a new one?

                Cheers
                Christoph

                T 1 Reply Last reply Reply Quote 0
                • T
                  tomas_hora administrators @CKB last edited by

                  @CKB Please contact us at our email with the link to this topic including your order number and also a picture of the QR code on EMO-R8 which included the bad cable and we will figure it out.

                  1 Reply Last reply Reply Quote 0