I would like to use my actuators for underfloor heating with unipi
Is it possible to connect 24 Vac on analog on unipi as illustrated.
Then replace N1 with a unipi
[attachment=1:3p3de0wg]Siemens SQX62.jpg[/attachment:3p3de0wg]Connection as shown below
SN>A0G
SP>A0V
Y>A0
[attachment=0:3p3de0wg]Analog_unipi.jpg[/attachment:3p3de0wg] -
I would like to use my actuators for underfloor heating with unipi
Is it possible to connect 24 Vac on analog on unipi as illustrated.
Then replace N1 with a unipi
[attachment=1:3p3de0wg]Siemens SQX62.jpg[/attachment:3p3de0wg]Connection as shown below
SN>A0G
SP>A0V
Y>A0
[attachment=0:3p3de0wg]Analog_unipi.jpg[/attachment:3p3de0wg] -
You definitely do not want to connect 24V AC
But what is a little confusing that the connector has 0-10V DC but does not have a proper GND for it... Or am I missing anything? Because you cannot connect the GND of UniPi to the AC gnd. But if you find where to put gnd for the 0-10V than you can easily connect it according to the second picture
-
GND to 0-10V DC sits on G0 24VAC on Siemens RLE162 regulator
-
The problem is solved