ModbusTCP - Neuron type detection
-
Is there any way to detect the type of Neuron device from the ModbusTCP server?
I tried to read register 1001 and 1002, but the values are not correct. For L533 I have the value 0x41 in register 1002 (unit 2 and 3) and this corresponds to 1 × RS485 and 4 × AO and no AI, which is wrong.
For unit 1 I have a value of 0x311 - 1 × RS485, 1 × AO and 3 × AI, which is also wrong.
Thank you! -
Hello @cvrcejir,
this information is not yet available via ModbusTCP.Best regards,
Martin -
This post is deleted! -
@Martin-Kudláček Why are the values in registers 1002 incorrect?
-
That looks like a bug, @cvrcejir, thanks for pointing that out! I was able to replicate it and pushed the issue to the devs for a fix.
Thanks,
Martin